Published by SALUSFire Extinguisher Size Recommendations ======================================
Selecting the appropriate size and type of fire extinguisher is crucial for ensuring effective fire suppression and workplace safety. This document outlines the recommended sizes for fire extinguishers based on specific fire hazards and occupancy types, drawing from established safety standards and best practices.
General Requirements
Employers are responsible for providing and maintaining appropriate firefighting equipment, including portable fire extinguishers, suitable for the potential fire hazards in their facilities. There should be no delay in providing necessary equipment as fire hazards occur. Defective equipment must be replaced immediately. [1] [1]
All portable fire extinguishers must bear an approved label from a nationally recognized testing laboratory. [1]
Fire extinguishers should be readily accessible along normal paths of travel in the protected area and their locations clearly indicated, even if visual obstructions are present. [1] [2]
Classification of Fires and Extinguisher Types
Fire extinguishers are selected and distributed based on the classes of anticipated workplace fires. Different classes of fires require different types of extinguishing agents: [7]
- Class A: Fires involving ordinary combustible materials like wood, cloth, paper, rubber, and many plastics. Extinguishers suitable for Class A fires include water, foam, loaded stream, or multipurpose dry chemical.
- Class B: Fires involving flammable liquids, gases, or greases. Suitable extinguishers include Halon 1301, Halon 1211, carbon dioxide, dry chemicals, foam, or loaded stream.
- Class C: Fires involving energized electrical equipment. Extinguishers for Class C fires include Halon 1301, Halon 1211, carbon dioxide, or dry chemical. It is crucial that the extinguishing agent is nonconductive.
- Class D: Fires involving combustible metals such as magnesium, titanium, zirconium, sodium, or potassium. These fires require specific dry powder extinguishing agents approved for use on the particular metal.
- Class K: Fires involving combustible vegetable or animal oils and fats, typically found in commercial kitchens. Class K extinguishers are specifically designed for these types of fires.
[9] [6] [9] [6] [9] [6] [9] [7] Specific Size and Placement Recommendations
Class A Fires:
A fire extinguisher with a rating of not less than 2A should be provided for each 3,000 square feet of protected building area, or major fraction thereof. The travel distance from any point in the protected area to the nearest fire extinguisher should not exceed 75 feet. [8] [8] [1]
In multistory buildings, at least one fire extinguisher rated not less than 2A should be located adjacent to the stairway on each floor. [1] [8] [5]
A 1/2 inch or larger interior diameter garden hose that is not more than 100 feet in length and that is equipped with a nozzle may be substituted for a 2A fire extinguisher if it is capable of reaching all points in the area that would be covered by the replaced extinguisher and is capable of discharging not less than 5 gallons per minute with a horizontal hose stream of not less than 30 feet. The hose line shall be mounted on a rack or reel. Not more than 1/2 of the total number of required fire extinguishers may be replaced by the hose. [1]
Class B Fires:
A fire extinguisher rated not less than 10B should be provided within 50 feet of locations where more than 5 gallons of flammable or combustible liquids or 5 pounds of flammable gas are being used on the job site. This requirement does not apply to the integral fuel tanks of motor vehicles. [3] [5] [8]
Class K Fires:
A Class "K" extinguisher should be maintained within 30 feet of hazards where there is a potential for fires involving combustible vegetable or animal oils and fats. [2] [7]
Specific Locations:
- Outside of, but not more than 10 feet from, a door opening to a room used for the storage of more than 60 gallons of flammable liquids, a portable fire extinguisher that has a rating of not less than 20 BC units shall be located.
- Not less than 25 feet, nor more than 75 feet, from an outside storage area, a portable fire extinguisher that has a rating of not less than 20 BC units shall be located.
- On each tank truck or other vehicle used to transport or dispense flammable liquids, a portable fire extinguisher that has a rating of not less than 20 BC units shall be located.
- Each service or fueling area shall have at least 1 portable fire extinguisher which has not less than a 20 BC unit rating and which is located within 75 feet of each pump, dispenser, underground fill opening, and lubricating or service area.
- Storage locations for liquefied petroleum gas (L.P.G.) shall be provided with at least 1 approved portable fire extinguisher that has a rating of not less than 20 BC.
- Each site of a hazardous process shall be provided with a portable fire extinguisher of an appropriate size and type.
[3] [3] [3] [3] [3] [3] Occupancy Type Considerations
Light Hazard Occupancies:
In light hazard occupancies, where the amount of combustibles or flammable liquids present is such that fires of small size may be expected (e.g., offices, schoolrooms, churches), smaller extinguishers may suffice, provided they meet the area coverage and travel distance requirements. [9]
Ordinary Hazard Occupancies:
In ordinary hazard occupancies, where fires of moderate size may be expected (e.g., mercantile storage and display, auto showrooms, light manufacturing), extinguishers with higher ratings and capacities are necessary to address the increased fire load. [9]
Extra Hazard Occupancies:
In extra hazard occupancies, where fires of severe magnitude may be expected (e.g., woodworking, auto repair, aircraft servicing), extinguishers with the highest ratings and capacities, or fixed fire equipment systems, are essential. [9]
Alternative Fire Suppression Methods
In some cases, standpipe systems or hose stations connected to a sprinkler system can be used instead of Class A portable fire extinguishers, provided that such systems meet specific requirements and employees are trained in their use. Up to 100 feet of 1 1/2-inch hose with a nozzle capable of discharging water at 25 gallons or more per minute may be substituted for a fire extinguisher rated not more than 2A in the designated area, provided that the hose line can reach all points in the area. [7] [4]
Inspection, Maintenance, and Training
Portable fire extinguishers must be visually inspected monthly to ensure they are fully charged and operable. Extinguishers should be maintained in a fully charged and operable condition and kept in their designated places at all times except during use. [10] [7] [10]
A tag should be attached to each extinguisher showing the dates of inspection, recharging or servicing, the name of the servicing agency, and the name of the person who did the service. [10]
Employers must provide training to employees on the use of portable fire extinguishers, including the proper selection, operation, and limitations of extinguishers. Employees should also be informed of evacuation procedures and emergency phone numbers. [1]
Conclusion
Selecting the correct size and type of fire extinguisher, combined with proper placement, inspection, maintenance, and employee training, is essential for maintaining a safe workplace and ensuring effective fire suppression. Compliance with relevant safety standards and regulations is crucial for protecting lives and property.
Safety powered by SALUS
Sources used for this answer
[1] Safety Standards for General Safety and Health Standards (Chapter 296-24 WAC)
Page 252
Open source documentSource excerpt
# PART G-2 FIRE PROTECTION (cont.) Chapter 296-24 WAC General Safety and Health Standards Part G-2 Fire Protection # WAC 296-24-585 Fire protection. [Order 73-5, $ 296-24-585, filed 5/9/73 and Order 73-4, $ 296-24-585, filed 5/7/73.] <table><tr><th>You must meet the requirements</th><th>in this section</th></tr><tr><td>Definitions applicable to fire protection</td><td>WAC 296-24-[redacted postal code]</td></tr><tr><td>Scope, application and definitions applicable</td><td>WAC 296-24-[redacted postal code]</td></tr></table> ## WAC 296-24-[redacted postal code] Definitions applicable to fire protection. Class A fires. Fires in ordinary combustible materials, such as wood, cloth, paper, and rubber. Class B fires. Fires in flammable liquids, gases, and greases. Class C fires. Fires which involve energized electrical equipment where the electrical nonconductivity of the extinguishing media is of importance. (When electrical equipment is deenergized, extinguisher for Class A or B fires may be used safely.) Class D fires. Fires in combustible metals, such as magnesium, titanium, zirconium, sodium, and potassium. Classification of portable fire extinguishers: Portable fire extinguishers are classified for use on certain classes of fires and rated for relative extinguishing effectiveness at a temperature of plus 70°F by nationally recognized testing laboratories. This is based upon the preceding classification of fires and the fire extinguishment potentials as determined by fire tests. Note: The classification and rating system described in this section is that used by Underwriters' Laboratories, Inc. and Underwriters' Laboratories of Canada and is based on extinguishing preplanned fires of determined size and description as follows: (a) Class A rating-Wood and excelsior fires excluding deep-seated conditions. (b) Class B rating-Two-inch depth gasoline fires in square pans. (c) Class C rating-No fire test. Agent must be a nonconductor of electricity. (d) Class…
[2] General Industry Safety and Health Standards (MIOSHA)
Page 3
Open source documentSource excerpt
# GENERAL INDUSTRY STANDARD (cont.) ## R 408.[redacted postal code] Definitions; C to E. (cont.) (2) A placard shall be conspicuously placed near the extinguisher that states that the fire protection system shall be activated before using the fire extinguisher. (3) A class "K" extinguisher shall be maintained within 30 feet, 9.15 meters from the hazards. ## R 408.[redacted postal code] Location. Rule 831. In a location where a visual obstruction cannot be avoided, a sign, color symbol, or other means shall be used to indicate the extinguisher's location. ## R 408.[redacted postal code] Installation. - Rule 833. (1) An extinguisher shall be installed securely on a hanger, in a bracket, or mounted in a cabinet unless it is wheeled type or cart mounted. A means shall be used to indicate the location of an extinguisher mounted in a cabinet or on a shelf. The extinguisher shall be placed so that the operating instructions face outward. (2) An extinguisher having a gross weight of not more than 40 pounds shall be installed so that the top is not more than 5 feet above the floor. An extinguisher having a gross weight of more than 40 pounds, except a wheeled type or cart mounted extinguisher, shall be installed so that the top is not more than 3 1/2 feet above the floor. An extinguisher, except a wheeled type or cart mounted extinguisher, shall be installed so that the bottom is not less than 4 inches from the floor. R 408.[redacted postal code] Rescinded. R 408.[redacted postal code] Rescinded. ## R 408.[redacted postal code] Recharging. Rule 837. An employer maintaining their own extinguisher shall use recharging materials of the class specified on the extinguisher nameplate or recommended by the manufacturer for recharging. R 408. [redacted postal code] Rescinded. 3
[3] Safety and Health Regulations for Construction (OSHA 29 CFR 1926) - 1926.150 - Fire protection
Page 4
Open source documentSource excerpt
# Table F-1 FIRE EXTINGUISHERS DATA <table><tr><th rowspan="3">OF DEPARTMENT</th><th rowspan="2" colspan="4">WATER TYPE</th><th rowspan="2">FOAM</th><th rowspan="2">CARBON DIOXIDE</th><th colspan="4">DBY CHEMICAL</th></tr><tr><td colspan="2">SODIUM OR POTASSIUM BICARBONATE</td><td colspan="2">MULTI-PURPOSE ABC</td></tr><tr><td>STORED PRESSURE</td><td>CARTRIDGE OPERATED</td><td>WATERPUMP PLIMP TAME</td><td>SODA ACID</td><td>FOAM</td><td>CO2</td><td>CARTRIDGE OPERATED</td><td>STOREO PRE SSURE</td><td>STORED PRESSURE</td><td>CARTRIDGE OPERATED</td></tr><tr><td>CLASS A expenses FIRES WOOD. PAPER, TRAIN MAYRIG CLOWING EMBERS -</td><td>YES</td><td>YES</td><td>YES</td><td>YES</td><td>YES</td><td>NO BUT WILL CONTROL SMALL SURFACE FIRES)</td><td>NO BUT WILL CONTROL SMALL SURFACE FIRESH</td><td>NO BUT WILL CONTROL SMALL SURFACE FIRES)</td><td>YES</td><td>YES</td></tr><tr><td>CLASS B FRES B PLANMABLE LICANDS, GAROLINE, ONL PAINTS, GREAM. ETC.</td><td>NO</td><td>NO</td><td>NO</td><td>NO</td><td>YES</td><td>YES</td><td>YES</td><td>YES</td><td>YES</td><td>YES</td></tr><tr><td>CLASS C ELECTION PIRES © ELECTRICAL EQUIPMENT -</td><td>NO</td><td>NO</td><td>NO</td><td>NO</td><td>NO</td><td>YES</td><td>YES</td><td>YES</td><td>YES</td><td>YES</td></tr><tr><td>CLASS D committens FIRES D COMPUSTIBLE METALS</td><td colspan="10">SPECIAL EXTINGUISHING AGENTS APPROVED BY RECOGNIZED TESTING LABORATORIES</td></tr><tr><td>METHOD OF OPERATION</td><td>PULL - i</td><td>TURN UPSIDE DOWN AND BUMP</td><td>PUMP MANDLE</td><td>TURN UPSIDE DOWN</td><td>TURN UPSIDE DOWN</td><td>PULL - SQUEEZE LEVER</td><td>RUPTURE CARTRIDGE- SQUEEZE LEVER</td><td>PULL PIM- SOURCE HANDLE</td><td>PULL PM. SQUARS 28 MANDLE</td><td>RUPTURE CARTRIDGE- SQUEEZE LEVER</td></tr><tr><td>BANGE</td><td>30'- 40'</td><td>30' 40'</td><td>30' 40'</td><td>30' 40'</td><td>30' 40'</td><td>y.s'</td><td>5'-20'</td><td>5'-20'</td><td>5'-20'</td><td>5'-20'</td></tr><tr><td>MAINTENANCE</td><td>CHECK AIR PRESSURE GAUGE MONTHLY</td><td>WEIGH GAS…
[4] Fire Extinguishers - Portable
Page 6
Open source documentSource excerpt
# Fire Extinguishers - Portable (cont.) ## What you should know when using a portable fire extinguisher? (cont.) Use the correct fire extinguisher type to fight the fire. Remember, if you feel that you cannot safely extinguish the fire using the portable extinguisher available and if you have not already done so, pull the fire alarm, evacuate the area, and then call the fire department. When using an extinguisher, use the PASS system - Pull, Aim, Squeeze, Sweep. 1. Pull the pin on the extinguisher. 2. Aim the extinguisher. 3. Squeeze the trigger or top handle. 4. Sweep the fire area with the extinguisher's spray until the fire is completely out. For floor fires, sweep from the edges in. For wall fires, sweep from the bottom up. - Never walk away from a fire, even if you think it is out. The residue may reignite. - Always stand between the escape route and the fire so you can leave safely if the fire grows. - If the fire grows too large, leave the area. Activate the fire alarm to evacuate the area. ## What you should know about selecting, locating, and maintaining portable fire extinguishers? As an employer or contractor, you must: - Use the proper size of the extinguisher. - Install extinguishers according to the height requirements stated in your jurisdiction's Fire Code. - Locate extinguishers so they are readily accessible to employees for immediate use. Make sure that extinguishers are clearly visible, and any location signs are clear. - Mark or label all fire extinguishers clearly with the class of fire it is to be used for. - Make sure that the operating instructions always face outward. - Maintain extinguishers in a fully charged and operable condition. - Keep extinguishers in the designated places at all times (except during use). - Visually inspect portable fire extinguishers monthly. - Use a tag on each extinguisher that shows the dates of inspection, recharging or servicing, the name of the servicing agency, and the name of t…
[5] Construction Safety Orders (CAL/OSHA)
Page 1
Open source documentSource excerpt
This information is provided free of charge by the Department of Industrial Relations from its web site at www.dir.ca.gov. These regulations are for the convenience of the user and no representation or warranty is made that the information is current or accurate. See full disclaimer at https://www.dir.ca.gov/od_pub/disclaimer.html. Subchapter 4. Construction Safety Orders Article 36. Fire Protection and Prevention Return to index New query ## §1922. Portable Fire Fighting Equipment. (a) Fire Extinguishers and Small Hose Lines. (1) A fire extinguisher, rated not less than 2A, shall be provided for each 3,000 square feet of the floor area, or fraction thereof. Where the floor area is less than 3,000 square feet at least one extinguisher shall be provided. Travel distance from any point of the protected area to the nearest fire extinguisher shall not exceed 75 feet. - One 55-gallon open container of water with two fire pails may be substituted for a fire extinguisher having a 2A rating. - A 3/4-inch diameter garden-type hose line, not to exceed 75 feet in length and equipped with an adjustable nozzle, may be substituted for a 2A-rated fire extinguisher, provided it is connected to a reliable water pressure system capable of discharging a minimum, continuous flow of 5 gallons per minute with a minimum hose stream range of 30 feet horizontally. The garden-type hose lines shall be mounted on conventional racks or reels. The number and location of hose racks or reels shall be such that at least one hose stream can be applied to all points in the floor area. - At least one fire extinguisher rated not less than 2A, shall be provided on each floor. In multi-story buildings, at least one fire extinguisher shall be located adjacent to the stairway at each floor level. - EXCEPTION: Single family residential dwellings other than apartments, lodging houses, hotels or dormitories provided that there is at least one fire extinguisher rated not less than 2A, or the equivalen…
[6] Safety Standards for General Safety and Health Standards (Chapter 296-24 WAC)
Page 264
Open source documentSource excerpt
# WAC 296-24-592 Portable fire extinguishers. (cont.) ## WAC 296-24-[redacted postal code] Appendix A-Portable fire extinguishers. (cont.) Chapter 296-24 WAC General Safety and Health Standards Part G-3 Fire Suppression Equipment protection. The selection and distribution of fire extinguishers must reflect the type and class of fire hazards associated with a particular workplace. Extinguishers for protecting Class A hazards may be selected from the following types: Water, foam, loaded stream, or multipurpose dry chemical. Extinguishers for protecting Class B hazards may be selected from the following types: Halon 1301, Halon 1211, carbon dioxide, dry chemicals, foam, or loaded stream. Extinguishers for Class C hazards may be selected from the following types: Halon 1301, Halon 1211, carbon dioxide, or dry chemical. Combustible metal (Class D hazards) fires pose a different type of fire problem in the workplace. Extinguishers using water, gas, or certain dry chemicals cannot extinguish or control this type of fire. Therefore, certain metals have specific dry powder extinguishing agents which can extinguish or control this type of fire. Those agents which have been specifically approved for use on certain metal fires provide the best protection; however, there are also some "universal" type agents which can be used effectively on a variety of combustible metal fires if necessary. The "universal" type agents include: Foundry flux, Lith-X powder, TMB liquid, pyromet powder, TEC powder, dry talc, dry graphite powder, dry sand, dry sodium chloride, dry soda ash, lithium chloride, zirconium silicate, and dry dolomite. - Water is not generally accepted as an effective extinguishing agent for metal fires. When applied to hot burning metal, water will break down into its basic atoms of oxygen and hydrogen. This chemical breakdown contributes to the combustion of the metal. However, water is also a good universal coolant and can be used on some combustible metals, but o…
[7] Construction Safety and Health Standards (MIOSHA)
Page 4
Open source documentSource excerpt
# CONSTRUCTION STANDARD (cont.) ## R 408.[redacted postal code] Employer responsibility. - Rule 1841. (1) An employer shall be responsible for the development of a fire protection program to be followed throughout all phases of the construction and demolition work, and the employer shall provide the firefighting equipment as specified in these rules. As fire hazards occur, there shall be no delay in providing the necessary equipment. (2) The fire protection portion of the program shall include all of the following: (a) Establishing and maintaining a means of egress from all areas of the building occupied by employees to provide free and unobstructed egress from all parts of the building or structure at all times when the building or structure is occupied. A lock or fastening that prevents free escape from the inside of any building shall not be installed, except in mental, penal, or corrective institutions where supervisory personnel is continually on duty and effective provisions are made to remove occupants in case of fire or other emergency. (b) Posting fire rules or, by other means, informing the employees of the evacuation signal, escape routes, and emergency phone numbers. Exits shall be marked by a readily visible sign. Access to exits shall be marked by readily visible signs in all cases where the exit or way to reach the exit is not immediately visible to the occupants. (c) A requirement that means of egress shall be continually maintained free of all obstructions or impediments to full instant use in the case of fire or other emergency. (3) The fire prevention portion of the program shall include both of the following: (a) A housekeeping policy designed to keep a means of egress free from the accumulation of stored materials and debris and to reduce the likelihood of fire. (b) A policy for the storage of combustible and flammable liquids and materials and for the use of proper heating equipment as prescribed in this part. (4) The employer shall p…
[8] Construction Safety and Health Standards (MIOSHA)
Page 5
Open source documentSource excerpt
# FIRE PROTECTION (cont.) (7) In addition to the requirements of this rule, fire extinguishers shall be supplied as follows: (a) Not less than 1 portable fire extinguisher that has a rating of not less than 20 BC units shall be located as follows: (i) Outside of, but not more than 10 feet from, a door opening to a room used for the storage of more than 60 gallons of flammable liquids. (ii) Not less than 25 feet, nor more than 75 feet, from an outside storage area. (iii) On each tank truck or other vehicle used to transport or dispense flammable liquids. (iv) A fire extinguisher, rated not less than 10B, shall be provided within 50 feet of wherever more than 5 gallons of flammable or combustible liquids or pounds of flammable gas are being used on the jobsite. This requirement does not apply to the integral fuel tanks of motor vehicles. 5 (b) Each service or fueling area shall have at least 1 portable fire extinguisher which has not less than a 20 BC unit rating and which is located within 75 feet of each pump, dispenser, underground fill opening, and lubricating or service area. (c) Storage locations for liquefied petroleum gas (L.P.G.) shall be provided with at least 1 approved portable fire extinguisher that has a rating of not less than 20 BC. (d) Each site of a hazardous process shall be provided with a portable fire extinguisher of an appropriate size and type. Other means for safety or control may be provided if approved or required by the process. (8) Table 1 may be used in selecting and providing an extinguisher. (9) Table 1 reads as follows: <table><tr><th colspan="3">TABLE 1</th></tr><tr><td>HAZARD</td><td>DESCRIPTION</td><td>EXTINGUISHER TYPE AND CONTENTS</td></tr><tr><td>Class "A" Fire</td><td>Combustible Material</td><td>Loaded stream, Multipurpose dry chemical, Pressure-operated water, Water pump tanks, Water mist, Halon 1211.</td></tr><tr><td>Class "B" Fire</td><td>Flammable Liquids, Gas, Or Grease</td><td>Carbon dioxide, Dry chemical, F…
[9] General Industry Safety and Health Standards (MIOSHA)
Page 7
Open source documentSource excerpt
# 1910.157 PORTABLE FIRE EXTINGUISHERS ## 1910.157(c) General Requirements. 1910.157(c)(1) The employer shall provide portable fire extinguishers and shall mount, locate and identify them so that they are readily accessible to employees without subjecting the employees to possible injury. ## R 408.[redacted postal code] Location. Rule 831. In a location where a visual obstruction cannot be avoided, a sign, color symbol, or other means shall be used to indicate the extinguisher's location. - 1910.157(c)(2) Only approved portable fire extinguishers shall be used to meet the requirements of this section. 1910.157(c)(3) The employer shall not provide or make available in the workplace portable fire extinguishers using carbon tetrachloride or chlorobromomethane extinguishing agents. - 1910.157(c)(4) The employer shall assure that portable fire extinguishers are maintained in a fully charged and operable condition and kept in their designated places at all times except during use. - 1910.157(c)(5) The employer shall remove from service all soldered or riveted shell self-generating soda acid or self-generating foam or gas cartridge water type portable fire extinguishers which are operated by inverting the extinguisher to rupture the cartridge or to initiate an uncontrollable pressure generating chemical reaction to expel the agent. - 1910.157(d) Selection and distribution. 1910.157(d)(1) Portable fire extinguishers shall be provided for employee use and selected and distributed based on the classes of anticipated workplace fires and on the size and degree of hazard which would affect their use. - 1910.157(d)(2) The employer shall distribute portable fire extinguishers for use by employees on Class A fires so that the travel distance for employees to any extinguisher is 75 feet (22.9 m) or less. - 1910.157(d)(3) The employer may use uniformly spaced standpipe systems or hose stations connected to a sprinkler system installed for emergency use by employees instead…
[10] Safety and Health Regulations for Construction (OSHA 29 CFR 1926) - 1926.150 - Fire protection
Page 3
Open source documentSource excerpt
# Occupational Safety and Health Administration (cont.) ## Water supply. (cont.) The garden-type hose lines shall be mounted on conventional racks or reels. The number and location of hose racks or reels shall be such that at least one hose stream can be applied to all points in the area. - 1926.150(c)(1)(iv) One or more fire extinguishers, rated not less than 2A, shall be provided on each floor. In multistory buildings, at least one fire extinguisher shall be located adjacent to stairway. 1926.150(c)(1)(v) Extinguishers and water drums, subject to freezing, shall be protected from freezing. - 1926.150(c)(1)(vi) A fire extinguisher, rated not less than 10B, shall be provided within 50 feet of wherever more than 5 gallons of flammable or combustible liquids or 5 pounds of flammable gas are being used on the jobsite. This requirement does not apply to the integral fuel tanks of motor vehicles. - 1926.150(c)(1)(vii) Carbon tetrachloride and other toxic vaporizing liquid fire extinguishers are prohibited. - 1926.150(c)(1)(viii) Portable fire extinguishers shall be inspected periodically and maintained in accordance with Maintenance and Use of Portable Fire Extinguishers, NFPA No. 10A-1970. - 1926.150(c)(1)(ix). Fire extinguishers which have been listed or approved by a nationally recognized testing laboratory, shall be used to meet the requirements of this subpart. ## 1926.150(c)(1)(x). Table F-1 may be used as a guide for selecting the appropriate portable fire extinguishers.
Keep exploring.
retirement facility interior renovation whilst occupied
Interior renovation or refurbishment in an occupied retirement facility or aged care residence should be managed as a live-environment construction project with vulnerable occupants, so the core approach is to separate residents from the work, identify all hazards before work starts, control dust, noise, infection
Read the threadWrite a risk assessment for Work at a petroleum storage terminal. Sampling of liquid fuels from storage tanks and road tankers. The task…
Sampling liquid fuels from storage tanks and road tankers at a petroleum terminal is a high-hazard task because it can combine work at height, flammable atmospheres, manual handling, vehicle movement, and potential confined-space conditions. The safe approach is to complete a task-specific risk assessment, use a
Read the threadBuild a 1000 componet JHA
Job Hazard Analysis for 1000-Component Assembly Process ======================================================== *Assessment Date:** \[DATE] *Assessor:** \[ASSESSOR NAME] *Department/Area:** \[DEPARTMENT/AREA] *Review Date:** \[REVIEW DATE] 1\. Assessment Scope This Job Hazard Analysis (JHA) covers the assembly of a
Read the threadOn-site fuel farm diesel and gasoline
Safety Procedures for On-Site Fuel Farms (Diesel and Gasoline) =============================================================== This document outlines the safety procedures for on-site fuel farms storing diesel and gasoline, covering fire prevention, spill control, and hazardous material handling. These procedures are
Read the threadLithium iron phosphate battery safety
Lithium iron phosphate (LFP) batteries are commonly used in various devices and equipment. It's important to follow safety procedures when handling, storing, and disposing of these batteries to prevent hazards. When LFP batteries are not used, stored, installed, disposed of, or charged properly, they can overheat
Read the threadWrite a risk assessment for House refurbishment
For house refurbishment and renovation works, the risk assessment should be task-specific, site-specific, and reviewed as the job changes. Under UK good practice and CDM principles, start by identifying hazards, who may be harmed, existing controls, and additional controls required, then communicate the findings to all
Read the threadAdd your experience.
Community answers can add practical context. They are moderated, but they are not SALUS-reviewed safety guidance.
New contributions are temporarily closed while the moderation queue is configured.
Community answers(0)
No community answers have been approved yet.
Comments on Rosie's answer(0)
No comments have been approved yet.