Skip to content
All safety questions
Asked by a personGeneral — US and Canadaen-CA

Working space to block off around battery chargers

Reviewed by Julie Gunn, Head of Services, SALUS Safety

The question, as asked: How much work space need to be blocked off while working on battery chargers

A person submitted this question to Rosie's free generator. The asker's identity is neither imported nor published.

Rosie's answer

Published by SALUS

When working on or near electrical equipment, including battery chargers, it's crucial to establish a safe working space. Here's what you need to consider:

  • General Requirements: Sufficient access and working space must be provided and maintained around all electrical equipment to allow for its safe operation and maintenance 9, 11, 19. This space should be kept clear and not used for storage 9, 11.
  • Minimum Dimensions: The working space should be at least 30 inches (762 mm) wide in front of the electrical equipment 9, 11, 19. Ensure the workspace allows for at least a 90-degree opening of equipment doors or hinged panels 11, 19, 20.
  • Depth of Working Space: The depth of the working space depends on the voltage and conditions around the live parts. Distances should be measured from the live parts if they are exposed, or from the enclosure front or opening if the live parts are enclosed 9, 11, 19.
  • Entrance and Access: At least one entrance to the working space must be provided, with a minimum width of 24 inches (610 mm) and a height of 6 feet 6 inches (1.98 m) 6, 8, 20.
  • Guarding Live Parts: Live parts operating at 50 volts or more must be guarded against accidental contact [1].
  • Overhead Lines: If work is performed near overhead lines, they must be de-energized and grounded, or other protective measures must be in place [2]. Maintain a minimum clearance from energized high voltage electrical conductors [3].
  • Specific Battery Charging Area Requirements: Battery charging installations should be located in designated areas 1, 7. Adequate ventilation should be provided to disperse fumes from gassing batteries [4]. Facilities for flushing and neutralizing spilled electrolyte and for fire protection should be available 1, 7.

Remember to consult relevant safety standards and regulations for detailed requirements and specific situations.

4 source record(s)

Sources used for this answer

[1] Rules for the Administration of the Oregon Safe Employment Act (Construction, Division 3, OSHA Oregon)

Page 451

Open source document

Source excerpt

## GENERAL REQUIREMENTS - (iv) Front working space. Where there are live parts normally exposed on the front of switchboards or motor control centers, the working space in front of such equipment shall not be less than 3 feet (914 mm). - (v) Headroom. The minimum headroom of working spaces about service equipment, switchboards, panelboards, or motor control centers shall be 6 feet 3 inches (1.91 m). ## (2) Guarding of live parts. - (i) Except as required or permitted elsewhere in this subpart, live parts of electric equipment operating at 50 volts or more shall be guarded against accidental contact by cabinets or other forms of enclosures, or by any of the following means: - (A) By location in a room, vault, or similar enclosure that is accessible only to qualified persons. - (B) By partitions or screens so arranged that only qualified persons will have access to the space within reach of the live parts. Any openings in such partitions or screens shall be so sized and located that persons are not likely to come into accidental contact with the live parts or to bring conducting objects into contact with them. - (C) By location on a balcony, gallery, or platform so elevated and arranged as to exclude unqualified persons. - (D) By elevation of 8 feet (2.44 m) or more above the floor or other working surface and so installed as to exclude unqualified persons. - (ii) In locations where electric equipment would be exposed to physical damage, enclosures or guards shall be so arranged and of such strength as to prevent such damage. - (iii) Entrances to rooms and other guarded locations containing exposed live parts shall be marked with conspicuous warning signs forbidding unqualified persons to enter. ## (j) Over 600 volts, nominal. - (1) General. Conductors and equipment used on circuits exceeding 600 volts, nominal, shall comply with all applicable provisions of paragraphs (a) through (g) of this section and with the following provisions which supplement or modify …

[2] Rules for the Administration of the Oregon Safe Employment Act (General Occupational Safety and Health, Division 2, OSHA Oregon)

Page 1221

Open source document

Source excerpt

Division 2 AO 3-2019 Oregon Administrative Rules Oregon Occupational Safety and Health Division - (3) Shear Point Guards. Shear points on forklift loaders and similar type vehicles shall be guarded as necessary to protect operators from hazardous exposure. - 1910.178 (f) Fuel handling and storage. - (1) The storage and handling of liquid fuels such as gasoline and diesel fuel shall be in accordance with NFPA Flammable and Combustible Liquids Code (NFPA No. 30-1969), which is incorporated by reference as specified in 1910.6. - (2) The storage and handling of liquefied petroleum gas fuel shall be in accordance with NFPA Storage and Handling of Liquefied Petroleum Gases (NFPA No. 58-1969), which is incorporated by reference as specified in 1910.6. - (g) Changing and charging storage batteries. - (1) Battery charging installations shall be located in areas designated for that purpose. - (2) Facilities shall be provided for flushing and neutralizing spilled electrolyte, for fire protection, for protecting charging apparatus from damage by trucks, and for adequate ventilation for dispersal of fumes from gassing batteries. - (3) [Reserved] - (4) A conveyor, overhead hoist, or equivalent material handling equipment shall be provided for handling batteries. - (5) Reinstalled batteries shall be properly positioned and secured in the truck. - (6) A carboy tilter or siphon shall be provided for handling electrolyte. - (7) When charging batteries, acid shall be poured into water; water shall not be poured into acid. - (8) Trucks shall be properly positioned and brake applied before attempting to change or charge batteries. - (9) Care shall be taken to assure that vent caps are functioning. The battery (or compartment) cover(s) shall be open to dissipate heat. - (10) Smoking shall be prohibited in the charging area. - (11) Precautions shall be taken to prevent open flames, sparks, or electric arcs in battery charging areas.

[3] Safety Standards for General Safety and Health Standards (Chaper 296-24 WAC)

Page 481

Open source document

Source excerpt

\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_ NMAB 353-3-1980 Classification of Combustible Dusts in Accordance with the National Electrical Code. [Statutory Authority: RCW 49.17.010, .040, .050, and .060. 12-16-064 (Order 12-11), § 296-24-[redacted postal code], filed 07/31/12, effective 09/01/12.] ## WAC 296-24-960 Working on or near exposed energized parts. - (1) Application . This section applies to work performed on exposed live parts (involving either direct contact or contact by means of tools or materials) or near enough to them for employees to be exposed to any hazard they present. - (2) Work on energized equipment . Only qualified persons must work on electric circuit parts or equipment that have not been deenergized under the procedures of WAC 296-[redacted postal code](2). Such persons must be capable of working safely on energized circuits and must be familiar with the proper use of special precautionary techniques, personal protective equipment, insulating and shielding materials, and insulated tools. ## (3) General requirements - high voltage lines . - (a) Minimum clearance . - (i) You must not perform any work, you must not pile, store, or otherwise handle any material, you must not erect or dismantle any scaffolding, commercial signs, or structures, nor must you operate any tools, machinery or equipment within the specified minimum distances from any energized high voltage electrical conductor capable of energizing the material or equipment; except where the electrical distribution and transmission lines have been deenergized and visibly grounded at point of work, or where insulating barriers not a part of or an attachment to the equipment have been erected, to prevent physical contact with the lines, you must operate equipment proximate to, under, over, by, or near powerlin…

[4] Safety Standards for General Safety and Health Standards (Chaper 296-24 WAC)

Page 482

Open source document

Source excerpt

\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_\_ - (5) Overhead lines . If work is to be performed near overhead lines, you must deenergize and ground the lines, or provide other protective measures before work is started. If the lines are to be deenergized, you must make arrangements with the person or organization that operates or controls the electric circuits involved to deenergize and ground them. If protective measures, such as guarding, isolating, or insulating, these precautions must prevent employees from contacting such lines directly with any part of their body or indirectly through conductive materials, tools, or equipment. - (6) Unqualified persons . When an unqualified person is working in an elevated position, or on the ground, near overhead lines, the location must be such that the person and the longest conductive object he or she may contact cannot come closer to any unguarded, energized overhead line than the following distances: - (a) For voltages to ground 50kV or below--10 ft.; - (b) For voltages to ground over 50kV--10 ft. plus 0.4 inch for every 1 kV over 50 kV. - (7) Qualified persons . When a qualified person is working in the vicinity of overhead lines, whether in an elevated position or on the ground, the person must not approach or take any conductive object without an approved insulating handle closer to exposed energized parts than shown in subsections (3) and (4) of this section unless: - (a) The person is insulated from the energized part (gloves, with sleeves if necessary, rated for the voltage involved are considered to be insulation of the person from the energized part on which work is performed); or - (b) The energized part is insulated both from all other conductive objects at a different potential and from the person; or - (c) The person is insulated from all co…

Ready to put operational safety to work?

Join 400K users across 150K sites already on SALUS.

No commitment · 30-minute personalized walkthrough