How often to check a fire extinguisher

Reviewed by Julie Gunn, Head of Services, SALUS Safety

The question, as asked: How often to check fire extinguisher

A person submitted this question to Rosie's free generator. The asker's identity is neither imported nor published.

Rosie's answer

Published by SALUS

Portable fire extinguishers should be inspected periodically and maintained in accordance with Maintenance and Use of Portable Fire Extinguishers, NFPA No. 10A-1970 [1]. The employer is ultimately responsible for the inspection, maintenance, and testing of portable fire extinguishers 5, 14. This can be done in-house if the employer ensures the persons doing the work have been trained to do so and recognize potential problems 12, 14. Fire fighting equipment should be maintained and inspected at least annually to assure the safe operational condition of the equipment [2]. Portable fire extinguishers and respirators should be inspected at least monthly [2]. Defective equipment should be immediately replaced [3].

3 source record(s)

Sources used for this answer

[1] Rules for the Administration of the Oregon Safe Employment Act (Construction, Division 3, OSHA Oregon)

Page 306

Open source document

Source excerpt

## FIRE PROTECTION - (ii) One 55-gallon open drum of water with two fire pails may be substituted for a fire extinguisher having a 2A rating. - (iii) A 1/2-inch diameter garden-type hose line, not to exceed 100 feet in length and equipped with a nozzle, may be substituted for a 2A-rated fire extinguisher, providing it is capable of discharging a minimum of 5 gallons per minute with a minimum hose stream range of 30 feet horizontally. The garden-type hose lines shall be mounted on conventional racks or reels. The number and location of hose racks or reels shall be such that at least one hose stream can be applied to all points in the area. - (iv) One or more fire extinguishers, rated not less than 2A, shall be provided on each floor. In multistory buildings, at least one fire extinguisher shall be located adjacent to stairway. - (v) Extinguishers and water drums, subject to freezing, shall be protected from freezing. - (vi) A fire extinguisher, rated not less than 10B, shall be provided within 50 feet of wherever more than 5 gallons of flammable or combustible liquids or 5 pounds of flammable gas are being used on the jobsite. This requirement does not apply to the integral fuel tanks of motor vehicles. - (vii) Carbon tetrachloride and other toxic vaporizing liquid fire extinguishers are prohibited. - (viii) Portable fire extinguishers shall be inspected periodically and maintained in accordance with Maintenance and Use of Portable Fire Extinguishers, NFPA No. 10A-1970. - (ix) Fire extinguishers which have been listed or approved by a nationally recognized testing laboratory, shall be used to meet the requirements of this subpart. - (x) Table F-1 may be used as a guide for selecting the appropriate portable fire extinguishers.

[2] Rules for the Administration of the Oregon Safe Employment Act (General Occupational Safety and Health, Division 2, OSHA Oregon)

Page 1067

Open source document

Source excerpt

L Division 2 Oregon Administrative Rules Oregon Occupational Safety and Health Division - (2) The employer shall assure that training and education is conducted frequently enough to assure that each member of the fire brigade is able to perform the member's assigned duties and functions satisfactorily and in a safe manner so as not to endanger fire brigade members or other employees. All fire brigade members shall be provided with training at least annually. In addition, fire brigade members who are expected to perform interior structural fire fighting shall be provided with an education session or training at least quarterly. - (3) The quality of the training and education program for fire brigade members shall be similar to those conducted by such fire training schools as the Maryland Fire and Rescue Institute; Iowa Fire Service Extension; West Virginia Fire Service Extension; Georgia Fire Academy, New York State Department, Fire Prevention and Control; Louisiana State University Firemen Training Program, or Washington State's Fire Service Training Commission for Vocational Education. (For example, for the oil refinery industry, with its unique hazards, the training and education program for those fire brigade members shall be similar to those conducted by Texas A & M University, Lamar University, Reno Fire School, or the Delaware State Fire School.) - (4) The employer shall inform fire brigade members about special hazards such as storage and use of flammable liquids and gases, toxic chemicals, radioactive sources, and water reactive substances, to which they may be exposed during fire and other emergencies. The fire brigade members shall also be advised of any changes that occur in relation to the special hazards. The employer shall develop and make available for inspection by fire brigade members, written procedures that describe the actions to be taken in situations involving the special hazards and shall include these in the training and education…

[3] Rules for the Administration of the Oregon Safe Employment Act (Construction, Division 3, OSHA Oregon)

Page 305

Open source document

Source excerpt

## FIRE PROTECTION ## SUBDIVISION F ## FIRE PROTECTION AND PREVENTION Authority: Section 107 of the Contract Work Hours and Safety Standards Act (40 U.S.C. 3704); Sections 4, 6, and 8 of the Occupational Safety and Health Act of 1970 (29 U.S.C. 653, 655, 657); Secretary of Labor's Order No. 12-71 (36 FR 8754), 8-76 (41 FR [redacted postal code]), 9-83 (48 FR [redacted postal code]),1-90 (55 FR 9033), 6-96 (62 FR 111), 3-2000 (62 FR [redacted postal code]), 5-2002 (67 FR 650008), 5-2007 (72 FR [redacted postal code]), 4-2010 (75 FR [redacted postal code]), or 1-2012 (77 FR 3912), as applicable; and 29 CFR part 1911. ## Β§1926.150 Fire Protection. ## (a) General requirements. - (1) The employer shall be responsible for the development of a fire protection program to be followed throughout all phases of the construction and demolition work, and he shall provide for the firefighting equipment as specified in this subpart. As fire hazards occur, there shall be no delay in providing the necessary equipment. - (2) Access to all available firefighting equipment shall be maintained at all times. - (3) All firefighting equipment, provided by the employer, shall be conspicuously located. - (4) All firefighting equipment shall be periodically inspected and maintained in operating condition. Defective equipment shall be immediately replaced. - (5) As warranted by the project, the employer shall provide a trained and equipped firefighting organization (Fire Brigade) to assure adequate protection to life. ## (b) Water supply. - (1) A temporary or permanent water supply, of sufficient volume, duration, and pressure, required to properly operate the firefighting equipment shall be made available as soon as combustible materials accumulate. - (2) Where underground water mains are to be provided, they shall be installed, completed, and made available for use as soon as practicable. ## (c) Portable firefighting equipment. - (1) Fire extinguishers and small hose lines. …

Related Q&A

Keep exploring.

Human questionCanada

Create a site orientation that meet compliance to BC, Canada

For construction or industrial worksites in British Columbia, site orientation and worker onboarding should be treated as a mandatory, documented, site-specific process under the Workers Compensation Act framework and the Occupational Health and Safety Regulation. At minimum, every young or new worker must receive

Read the thread

Ready to put operational safety to work?

Join 400K users across 150K sites already on SALUS.

No commitment Β· 30-minute personalized walkthrough