Skip to content
All safety questions
Asked by a personCanadaen-CA

How many washrooms a construction site of 81 workers needs

Reviewed by Julie Gunn, Head of Services, SALUS Safety

The question, as asked: how man washrooms are needed on a construction site of 81 workers?

A person submitted this question to Rosie's free generator. The asker's identity is neither imported nor published.

Rosie's answer

Published by SALUS

For 81 workers, the number of toilets or washrooms mandated varies depending on the specific regulations and standards being followed.

In Alberta, under the Occupational Health and Safety Code, 5 toilets are required for each sex if there are between 76 and 100 workers of that sex. [5]

Nunavut and Northwest Territories require 5 toilets for 76-100 workers, according to their Occupational Health and Safety Regulations. [4]

In Prince Edward Island, the employer shall provide 5 toilet facilities where there are 75 to 100 persons employed when running water is available. [7]

New Brunswick requires five toilets when the number of employees exceeds 74 but does not exceed 100, if the toilets are chemical, self-contained portable or other similar type. [6]

Ontario Construction Projects Regulation 213/91 states that when water flush toilets or non-recirculating chemical flush toilets are provided, 5 toilets are needed for 61 or more workers [3]

British Columbia requires a sufficient number of readily available flush toilets, or chemical toilets if flush toilets are not practical, at a specified construction site where 25 or more workers will be present at any time. [1] [1]

The Safety Code for the Construction Industry in Quebec stipulates that one toilet is provided per group of 30 workers or fewer. If 25 or more workers are to occupy the site at the same time, a flushing toilet must be placed at their disposal [2] [2]

7 source record(s)

Sources used for this answer

[1] Occupational Health and Safety Code (Alberta Regulation 191/2021)

Page 385

Open source document

Source excerpt

# Schedule 6 Dimensions of Scaffold Members (cont.) Schedule 7 OCCUPATIONAL HEALTH AND SAFETY CODE AR 191/2021 # Schedule 7 Toilets at a Work Site [ See section 357(1) ] # Number of toilets required at a work site <table><tr><th>Number of workers of that sex</th><th>Minimum number of toilets for that sex</th></tr><tr><td>1 - 10</td><td>1</td></tr><tr><td>11 - 25</td><td>2</td></tr><tr><td>26 - 50</td><td>3</td></tr><tr><td>51 - 75</td><td>4</td></tr><tr><td>76 - 100</td><td>5</td></tr><tr><td>&gt; 100</td><td>6 plus 1 for each additional 30 workers of the sex in excess of 100</td></tr></table> S7-1

[2] Occupational Health and Safety Regulations (Nu Reg 003-2016)

Page 240

Open source document

Source excerpt

# SCHEDULE K (Subsections 75(2), (3) and (5)) 1. Minimum Number of Toilets Facilities at Work Site <table><tr><th>Number of Workers</th><th>Number of Toilets</th></tr><tr><td>1 to 10</td><td>1</td></tr><tr><td>11 to 25</td><td>2</td></tr><tr><td>26 to 50</td><td>3</td></tr><tr><td>51 to 75</td><td>4</td></tr><tr><td>76 to 100</td><td>5</td></tr><tr><td colspan="2">Add one toilet for each additional unit of 30 workers</td></tr></table> 238

[3] OHS Act General Regulations (PEI Reg. EC180/87)

Page 6

Open source document

Source excerpt

# GENERAL REGULATIONS (cont.) ## PART 2 - TOILET AND WASHING FACILITIES (cont.) PART 2 - TOILET AND WASHING FACILITIES Section 2.5 Occupational Health and Safety Act General Regulations - 2.5 Separate facilities - Where 10 or more persons are employed, the employer shall provide separate washrooms and toilet facilities for each sex with a locking device on the inside. (EC180/87; 126/21) - 2.6 Requirements (1) In every place of employment where running water is available, the employer shall provide (a) toilet facilities in accordance with the following table: <table><tr><th>No. of Persons</th><th>Facilities</th></tr><tr><td>1 to 9</td><td>1</td></tr><tr><td>10 to 24</td><td>2</td></tr><tr><td>25 to 49</td><td>3</td></tr><tr><td>50 to 74</td><td>4</td></tr><tr><td>75 to 100</td><td>5</td></tr><tr><td>Over 100</td><td>(1 for each additional 30 persons)</td></tr></table> (b) a supply of toilet tissue for each toilet at all times and washable covered receptacles for waste; (c) adequate and suitable facilities for personal washing including a supply of clean hot and cold running water, soap, towels or other suitable means of washing and drying. - Idem (2) Where more than two toilets are required for male workers the employer may substitute urinals for up to 2/3 of the required number of toilets. - Shower facilities (3) Where there is a high risk of contamination of workers by the presence of hazardous substances, infectious or offensive materials that are part of the regular work processes at a workplace, an employer shall, where reasonably practicable, supply and maintain adequate changing and showering facilities. - Requirements (4) Where changing and shower facilities referred to in subsection (3) are provided, an employer shall (a) provide separate shower rooms for male and female workers except where there are fewer than six persons employed at a workplace; (b) ensure that where there are fewer than six persons employed at a workplace a sh…

[4] Occupational Health and Safety Regulation (B.C. Reg. 296/97)

Page 402

Open source document

Source excerpt

# OCCUPATIONAL HEALTH AND SAFETY REGULATION (cont.) ## Coordination of multiple employer workplaces (cont.) B.C. Reg. 296/97 WORKERS COMPENSATION ACT OCCUPATIONAL HEALTH AND SAFETY REGULATION Part 20 - Construction, Excavation and Demolition # Washroom Facilities at Construction Sites ## Definitions 20.3.1 In section 20.3.2: "chemical toilet" means a toilet (a) that does not have a bowl, and (b) in which waste falls directly into a tank containing a chemical product that processes the waste; "flush toilet" means a toilet that meets the following specifications: (a) the toilet is connected to a sanitary sewer system or a holding tank; (b) the toilet has a trap or positive seal separating the bowl from the sanitary sewer system or holding tank; (c) waste is flushed from the bowl by means of a flow of clean water or a mixture of clean water and chemicals; "handwashing facility" means a facility by which a person can (a) wash their hands using soap and water, or (b) clean their hands by some other means, if providing water is not practicable; "specified construction site" means a worksite at which (a) a construction project is undertaken, and (b) 25 or more workers will be present at any time during the undertaking of the construction project. [en. B.C. Reg. 260/2024, S. 2.] ## Toilets at specified construction sites - 20.3.2 (1) Subject to subsection (2), the employer must ensure that a sufficient number of flush toilets are readily available for workers at a specified construction site. (2) If it is not practicable to provide flush toilets, the employer must ensure that a sufficient number of chemical toilets or other types of toilets are readily available for workers at the specified construction site. (3) The employer must ensure that each toilet available at a specified construction site (a) is maintained in proper working order, (b) is cleaned and sanitized as frequently as necessary to keep it in a clean and sanitary co…

[5] Construction Projects Regulation (O. Reg. 213/91)

Page 15

Open source document

Source excerpt

# ONTARIO REGULATION 213/91 CONSTRUCTION PROJECTS (cont.) ## HYGIENE (cont.) 1. The facility shall have, i. a toilet with an open-front toilet seat, ii. a toilet paper holder and an adequate supply of toilet paper, and iii. a self-closing door that can be locked from the inside. 2. The facility shall, i. be adequately illuminated by natural or artificial light, ii. be adequately heated, if that is possible, iii. be adequately ventilated, and iv. afford the user privacy and protection from weather and falling objects. 3. If the facility is a single-toilet facility, it shall be completely enclosed. O. Reg. 61/23, S. 3 (1). (1.1) For greater certainty, the requirement that a facility be completely enclosed does not apply to a portable urinal, O. Reg. 61/23, S. 3 (1). (2) Separate toilet facilities shall be provided for male and female workers, unless the facilities are intended to be used by only one worker at a time. O. Reg. 145/00, S. 15. (2.1) Where the minimum number of toilets required at a project under subsection (5) or (7) is five or more, at least one facility at the project shall be for the use of female workers only, where reasonable in the circumstances. O. Reg. 61/23, S. 3 (2). (2.2) If the facility is intended for use by males only or females only, it shall have a sign indicating that. O. Reg. 61/23, S. 3 (2). (2.3) If the facility is intended for use by female workers, there shall be a disposal receptacle for menstrual products. O. Reg. 61/23, S. 3 (2); O. Reg. 190/24, S. 2. (3) Sewered toilet facilities or non-sewered flush toilet facilities shall be provided at a project, subject to subsection (4). O. Reg. 145/00, S. 15. (4) If a project is being carried out in a remote unpopulated area and it is not reasonably possible to provide toilet facilities required under subsection (3), other types of toilet facilities shall be provided. O. Reg. 61/23, S. 3 (3). (5) When water flush toilets or non-recirculating chemical…

[6] Safety Code for the Construction Industry (CQLR c. S-2.1, r.4)

Page 51

Open source document

Source excerpt

# OCCUPATIONAL HEALTH AND SAFETY - CONSTRUCTION - SAFETY CODE the workers are not yet present on site. If there never will be more than 24 workers on site, a chemical toilet may be at their disposal. One toilet is provided per group of 30 workers or fewer. If a flushing toilet is not connected to a waterworks or sewer system in accordance with the Construction Code (chapter B-1.1, r. 2), it must collect the waste in a tank to process the waste chemically and be built in accordance with the standard Sanitation - Nonsewered Waste Disposal Systems - Minimum requirements, ANSI Z4.3-1995 (R. 2005), published by the American National Standards Institute. The obligation to place a toilet at the disposal of workers is met if the workers are authorized to use the sanitary facilities of an establishment located at a distance that complies with section [redacted address] R.R.Q., 1981, c. S-2.1, r. 6, S. 3.1.7; O.C. 329-94, S. 28.and 29; O.C. 428-2015, S. 3. [redacted address]. Toilets must be located at a distance not exceeding 150 m (500 ft.) from the work area and must not be more than 4 storeys higher or lower than the work area. O.C. 428-2015, S. 3. ## [redacted address]. A toilet must be (1) within easy access; (2) free from any obstacle or obstruction that could prevent the toilet from being used; (3) built so that the occupant is sheltered from view and protected from the weather and falling objects; (4) provided with natural or artificial lighting; (5) equipped with a seat and cover; (6) provided with toilet paper; (7) heated to a minimum of 20 °C; and (8) ventilated. The toilet must be maintained in good operating condition and in a clean and sanitary condition and be kept free of vermin, rodents and insects. Any cracked or damaged toilet seat must be replaced immediately. O.C. 428-2015, S. 3. 3.2.8. Sinks: The employer shall provide the workers who handle corrosive or toxic materials with sinks or showers that comply with section 3.2.15 and that e…

[7] General Regulation (N.B. Reg. 91-191)

Page 33

Open source document

Source excerpt

# Loi sur l'hygiène et la sécurité au travail (cont.) ## Toilettes 2024-38 (cont.) O-0.2 Occupational Health and Safety Act 91-191 ployees if the toilet is situated in a room whose entrance door is fitted on the inside with a locking device. - 5(2.1) Despite subsection (1), if the toilets are of a chemical, a self-contained portable or other similar type, an employer shall provide a minimum number of toilets determined according to the maximum number of em- ployees who are normally employed at any one time at the same place of employment as follows: (a) when the number of employees does not exceed nine, one toilet; (b) when the number of employees exceeds nine but does not exceed 24, two toilets; (c) when the number of employees exceeds 24 but does not exceed 49, three toilets; (d) when the number of employees exceeds 49 but does not exceed 74, four toilets; (e) when the number of employees exceeds 74 but does not exceed 100, five toilets; and (f) when the number of employees exceeds 100, five toilets and one toilet for every 30 employees in excess of 100. - 5(3) Repealed: 2024-38 - 5(4) Where more than two toilets are required for male employees, an employer may substitute urinals for up to two-thirds of the required number of toilets. - 5(5) Where running water and sewage facilities are available, toilets shall be of the water flush type and may be of the chemical, self-contained portable or other simi- lar type if no running water is available. - 5(6) As soon as work has started on a project site, the contractor or, if there is no contractor, the owner shall provide toilets in accordance with subsection (1) or (2.1), as the case may be. - 5(7) An employer shall ensure that a washroom is (a) within easy access of an employee's work area, de travail ne dépasse pas neuf et que la porte des toilettes est munie d'un dispositif de verrouillage à l'intérieur. - 5(2.1) Par dérogation au paragraphe (1), si les toilettes sont de type à épuration…

Related Q&A

Keep exploring.

Discussion thread

Add your experience.

Community answers can add practical context. They are moderated, but they are not reviewed by Francis Langlois or presented as SALUS safety guidance.

New contributions are closed. Previously approved contributions remain visible.

Community answers(0)

No community answers have been approved yet.

Comments on Rosie's answer(0)

No comments have been approved yet.

Ready to put operational safety to work?

Join 400K users across 150K sites already on SALUS.

No commitment · 30-minute personalized walkthrough