Write a risk assessment for Work at a petroleum storage terminal. Sampling of liquid fuels from storage tanks and road tankers. The task involves climbing onto the roof of a storage tank, opening the hatch, and collecting a fuel sample. It also includes determining the quantity of fuel stored in the tank. Some of the tanks do not have flat roofs; instead, their roofs are curved in a dome-like shape. The hatch opening is very small, approximately 5 cm in diameter. During sampling, the employee must carry sampling equipment, a rope, and several sample containers. This makes it difficult to maintain stable footing and balance while performing the sampling operation, particularly when working on the curved tank roof.
A person submitted this question to Rosie's free generator. The asker's identity is neither imported nor published.
Rosie's answer
Published by SALUSSampling liquid fuels from storage tanks and road tankers at a petroleum terminal is a high-hazard task because it can combine work at height, flammable atmospheres, manual handling, vehicle movement, and potential confined-space conditions. The safe approach is to complete a task-specific risk assessment, use a permit-to-work system, eliminate or reduce the need to climb where possible, control ignition sources, verify hazardous-area requirements, and ensure workers are trained, supervised, and equipped for both fall protection and emergency rescue. A written fall protection work plan and rescue arrangements should be in place before work starts, and any activity that could become confined-space entry must be separately assessed and controlled under a confined-space permit system. [2] [12] [7]
A practical risk assessment for this work should cover the following task stages: access to tank or tanker, climbing ladders or stairs, movement on fixed-roof or dome-roof surfaces, opening hatches, sampling and gauging, handling and transporting samples, descent, and departure from the area.
- Falls from ladders, stairs, platforms, tanker top walkways, tank roofs, and through openings
- Loss of balance on curved or sloped dome roofs, especially in rain, ice, wind, poor lighting, or while carrying equipment
- Slip and trip hazards from wet/oily surfaces, hoses, sample lines, uneven roof plates, and poor housekeeping
- Exposure to flammable vapours at hatch openings during sampling, gauging, and quantity measurement
- Ignition from static electricity, non-rated electrical equipment, vehicles, phones, torches, metal impact, or smoking materials
- Manual-handling strain from sample thieves, tapes, water-finding paste, bonding leads, and filled sample containers
- Vehicle hazards around road tankers, including movement, reversing, and struck-by risk
- Potential confined-space escalation if any part of the body enters a tank opening beyond normal external sampling/gauging, or if rescue/retrieval from an opening is required
- Weather and environmental hazards such as heat stress, cold stress, lightning, and reduced grip on curved roofs
[2] [10] [15] For storage tanks and road tankers, the preferred control is to avoid climbing and opening hatches whenever reasonably practicable. Use closed or lower-risk systems first, such as fixed sampling points, closed-loop sampling, automatic gauging, remote level measurement, or sampling from grade-level cabinets. If the task cannot be eliminated, use the hierarchy of controls: engineered access platforms and guarded walkways before ladders; fixed guardrails before personal fall arrest; and administrative controls and PPE only as supporting measures. [2]
Safe work procedure for routine sampling and gauging:
- Confirm the task scope, product, tank/tanker identity, sampling point, and whether hatch opening is actually necessary.
- Review the task-specific risk assessment, hazardous-area classification, weather, lighting, and nearby operations such as loading, venting, hot work, or vehicle movement.
- Issue the required permit to work. At minimum this is typically a general/task permit for petroleum operations; add confined-space, hot-work, isolation, or line-breaking permits if conditions require them.
- Verify the tank or tanker is stable and safe to access. For road tankers, immobilize the vehicle, apply brakes/chocks as required by site rules, and control traffic around the work area.
- Inspect access systems before use: stairs, ladders, cages, platforms, handrails, tanker top gantries, and anchor points. Do not use damaged or contaminated access equipment.
- Inspect fall-protection equipment before use and ensure the selected system matches the task: travel restraint is preferred where possible; fall arrest only where a fall cannot be prevented and rescue is assured.
- Use intrinsically safe or otherwise area-approved equipment only. Bond/earth equipment where required by site procedures, and control static-generating clothing or tools.
- Test the atmosphere if required by site rules or if there is any doubt about vapour accumulation, especially near hatch openings, floating roofs, domes, sumps, or partially enclosed areas.
- Ascend maintaining three points of contact and keep hands free by using tool bags, hoists, or shoulder straps rather than carrying loose items while climbing.
- Before stepping onto a roof, confirm the walking surface, route, edge protection, and anchor/tie-off arrangement. Avoid stepping onto curved or wet surfaces unless the route and footing are controlled.
- Position yourself upwind where possible before cracking open a hatch. Open slowly to relieve pressure and avoid standing directly over the opening.
- Keep face and breathing zone away from the hatch. Minimize opening size and opening time. Never lean into the opening or place any part of the body inside unless the job has been reclassified and controlled as confined-space entry.
- Take the sample using non-sparking, compatible, clean equipment. Avoid overfilling containers. Cap and label samples immediately.
- Carry out gauging/quantity measurement using approved tapes, gauges, and procedures that minimize splash, vapour release, and static generation.
- Close and secure the hatch promptly after sampling/gauging. Confirm seals, caps, and locks are reinstated.
- Descend carefully, maintaining three points of contact, and transport samples in suitable carriers or secondary containment to the designated sample handling area.
- Record the sample, any abnormal conditions, gas-test results if taken, and any defects in access, fall protection, or tank condition.
[8] [10] [4] Working on fixed-roof and dome-roof tanks requires special controls because curved surfaces increase the chance of slipping and losing balance, and hatch work often places the worker near an unprotected opening. Use permanent stairs, platforms, and guardrails where installed. Where workers must move beyond guarded areas, a site-specific fall protection plan should define the route, anchor points, tie-off method, exclusion zones, and rescue method. On curved roofs, travel restraint is generally safer than allowing exposure to a fall edge or hatch opening. Workers should not carry bulky items by hand across the roof; use lifting lines or mechanical means. [12] [11] [9]
Fall protection should be selected and used systematically. A personal fall arrest system consists of a body harness, anchorage, and connector; anchors must be suitable for the intended loads and located to minimize swing fall and free fall. Keep lanyards as short as practicable, inspect harnesses, lanyards, connectors, and labels before use, and remove damaged equipment from service. Do not improvise anchor points on vents, pipework, handrails, or weak roof appurtenances. Where tanker top access is needed, use fixed gantries, guarded platforms, or engineered overhead lifeline systems rather than relying on ad hoc tie-off. [11] [13] [14]
The fatality record shows why strict fall controls are necessary. Workers have died after removing harnesses on tank roofs, working near roof openings, or using poorly rigged systems with excessive slack. For sampling and gauging, this means no one should access a tank roof or tanker top without the required fall controls in place, and hatch/opening areas must be treated as fall hazards as well as vapour-release points. [9] [15]
Flammable vapour and ignition control are critical during hatch opening, sampling, and gauging. Petroleum vapours may be released suddenly and can ignite from unsuitable blowers, extension leads, static discharge, or other non-approved equipment. Control measures should include hazardous-area classification of the task location, use of ATEX/DSEAR-compliant equipment in zoned areas, prohibition of smoking and hot work unless separately permitted, control of vehicles and portable electronics, bonding/earthing where required, and stopping work if vapour conditions become abnormal. If forced ventilation is used near petroleum tanks, the equipment must be suitable for flammable atmospheres and arranged so it does not create an ignition hazard. [4] [4] [3]
For ATEX/DSEAR compliance, the employer should classify hazardous places where explosive atmospheres may occur, assess ignition risks from equipment and work activities, select appropriately certified equipment, and implement controls to prevent explosive atmospheres from being ignited. In practice for petroleum sampling, this means treating hatch openings, vents, tanker top compartments, and nearby low points as potentially hazardous zones; using only approved portable gas detectors, torches, radios, and sampling devices; and ensuring permits, signage, and worker instructions reflect the zone controls. Even where local law differs, the underlying requirement is the same: identify explosive atmosphere risk and use equipment and procedures suitable for that risk.
Confined-space considerations are especially important. Routine external sampling from outside a hatch is not automatically confined-space entry, but the risk assessment must prevent the task from drifting into entry conditions. If a worker must break the plane of the opening with the head or torso, descend into the tank, or perform rescue/retrieval involving entry, then a confined-space program, permit, atmospheric testing, isolation, attendant, communications, and rescue capability are required. Tanks can contain oxygen-deficient, toxic, or flammable atmospheres even after draining. [10] [10] [1]
If confined-space controls are triggered, key requirements include hazard assessment, isolation/lockout, purging or ventilation as needed, calibrated gas monitoring, trained entrants and attendants, communications, rescue notification, and suitable retrieval/fall-arrest equipment. The surrounding area should also be checked for drifting vapours and other external hazards before entry. [1] [1] [1]
Manual-handling controls should address the weight and awkwardness of sampling devices, tapes, bonding cables, and filled sample bottles. Use the smallest practical sample volume, lightweight equipment, shoulder bags or holsters that keep hands free, and mechanical lifting aids or tag lines for raising/lowering equipment to roofs. Avoid twisting while standing on ladders or curved roofs, and never climb while carrying open containers. Plan the route so samples can be transferred promptly to a secure container rack or transport case.
PPE for this work should be selected from the risk assessment and site rules.
- Flame-resistant or anti-static clothing suitable for petroleum terminal operations
- Chemical-resistant gloves compatible with the fuel handled
- Safety glasses or goggles; face shield if splash risk is significant
- Hard hat where overhead or access hazards exist
- Slip-resistant safety footwear suitable for oily metal surfaces
- Portable gas detector where required by the risk assessment or permit
- Fall-protection equipment appropriate to the access system: full body harness, suitable lanyard/SRL, rope grab, and approved anchors
- Respiratory protective equipment only where justified by assessment and within a proper respiratory protection program; it is not a substitute for controlling vapours at source
[1] [5] [13] Emergency arrangements must cover both fall rescue and petroleum/fire emergencies. A written rescue plan should identify who rescues, how rescue is initiated, what equipment is on site, communication methods, access routes, first-aid arrangements, and transport to hospital. Relying only on public emergency services is not enough for a suspended worker. If fall arrest is used, the team must be able to recover the worker immediately because suspension trauma can develop within minutes. Rescue planning must also consider that the same vapour, fire, structural, or weather hazards that caused the incident may endanger rescuers. [7] [7] [7]
The rescue plan should be job-specific and reviewed before each shift or whenever conditions change. It should include rescue methods such as self-rescue, ladder rescue, retrieval lines, rope rescue, or use of mobile equipment where appropriate; backup communications; emergency exits and access routes; and procedures to secure the area so rescue is not obstructed. [6] [6] [5]
Regulatory requirements vary by jurisdiction, but petroleum terminal sampling operations are typically governed by occupational safety law, work-at-height rules, hazardous-area/electrical rules, dangerous substances/fire and explosion rules, PPE requirements, and site major-hazard or petroleum licensing requirements. At a minimum, employers should ensure: documented hazard assessment; permit-to-work; worker training and competency; inspection and maintenance of access/fall-protection/gas-testing equipment; emergency response planning; hazardous energy isolation where relevant; and compliance with hazardous-product labeling and sample container requirements. For UK-style regimes, this aligns with HSWA, Management Regulations, Work at Height Regulations, PPE at Work, PUWER, LOLER where lifting is used, DSEAR, and ATEX equipment obligations. For US/Canadian regimes, equivalent OSHA/OHS and fire-code duties apply.
In summary, a defensible safe system for petroleum fuel sampling is: avoid roof access where possible; use engineered access and closed sampling systems; control falls with a written plan and rescue capability; treat hatch opening as both a fall and vapour hazard; use only area-approved equipment; prevent ignition and static; escalate to confined-space controls if entry conditions arise; and train, supervise, and audit the task rigorously. [4] [12] [3]
Sources used for this answer
[1] Occupational Health and Safety Code (Alberta Regulation 191/2021)
Page 407
Open source documentSource excerpt
# OCCUPATIONAL HEALTH AND SAFETY CODE Index <table><tr><th></th><th>documents</th><th>present until replaced or workers have left, 56(5)</th></tr><tr><td></td><td>code of practice, 44, 52(4)-(5)</td><td>records of workers in space, 56(4)</td></tr><tr><td></td><td>emergency response plan, 55</td><td>system for summoning assistance, 56(2)</td></tr><tr><td></td><td>entry permit system, 47, 50, 58</td><td>training, 56(2)</td></tr><tr><td></td><td>evacuation procedures, 53(4)</td><td>traffic hazards, 51</td></tr><tr><td></td><td>hazard assessment, 45, 52(3), 52(6), 58</td><td>training, 46, 53, 56(2)</td></tr><tr><td></td><td>inspection records, 48(3)</td><td>unauthorized entry, 50</td></tr><tr><td></td><td>inspections of equipment, 48(2)-(3), 58</td><td>ventilation, 53</td></tr><tr><td></td><td>retaining records, 58</td><td>water dangers, 49</td></tr><tr><td></td><td>training records, 46</td><td>Connecting components for personal fall-arrest</td></tr><tr><td></td><td>emergency equipment, 45, 46(3), 48(1), 48(2)</td><td>systems (PFAS) (CSA), 835(d)</td></tr><tr><td></td><td>emergency response plan, 2.2, 55, 56(2), 115-116</td><td>connectors</td></tr><tr><td></td><td>entry permit system, 47, 50, 58</td><td>standards for fall arrest system, 143(1)</td></tr><tr><td></td><td>evacuation procedures, 53(4)-(5), 55</td><td>constructed portable ladders See ladders</td></tr><tr><td></td><td>first aid, 46(3)(a)</td><td>construction</td></tr><tr><td></td><td>harmful substances, 49</td><td>first aid, high hazard work, 178, 181(1), Schedule 2,</td></tr><tr><td></td><td>hazard assessment, 45, 49, 52, 56, 58</td><td>Tables 3 and 7</td></tr><tr><td></td><td>hazardous energy, 49</td><td>Construction and Demolition Operations - Personnel</td></tr><tr><td></td><td>hoppers, safeguards, 316</td><td>and Debris Nets (ANSI), 320(1)(a)</td></tr><tr><td></td><td>inerting, 54</td><td>Construction and Test of Electric Cranes and Hoists</td></tr><tr><td></td><td>inspections and tests</td><td>(CSA), β¦
[2] Lockout/Tagout Sample Forms: Evaluation, Procedures, and Permit
Page 9
Open source documentSource excerpt
# Equipment-Specific Hazardous Energy Control Evaluation and Certification (cont.) Enter name of your company here # Safety Permit for Hazardous Energy Control (Lockout/Tagout) Work Operations Date of work activity: <empty> Permit issued to: Authorized employee name: <empty> Title: <empty> Company name (if outside contractor): <empty> Contact number: <empty> Date/Time issued: <empty> Date/Time permit expires: <empty> Work activity: <empty> Machine/equipment description: <empty> Work location: <empty> Personal protective equipment (PPE), as required: (also circle specific types within the parentheses) [ ] Face shield [ ] Ear plugs [ ] Hard hat [ ] Safety glasses [ ] Ear muffs [ ] Hood (chemical, thermal) [ ] Safety goggles [ ] Suit (rubber, thermal, Tyvek) [ ] Safety harness & line [ ] Filtering facepiece/N95 [ ] Respirator (dust, vapor, combination, full-face, half-face) [ ] Gloves (thermal) [ ] Gloves (latex, neoprene, nitrile, PVC, rubber) [ ] Rubber boots [ ] Shoes (steel-toed, electrical safety, slip-resistant) [ ] Additional PPE required: <empty> Energy control devices, as required: (also circle applicable activities within the parentheses) [ ] Disconnect [ ] Blocks [ ] Accident prevention tags [ ] Valves (close, block, blind) [ ] Lock devices (individual, group) [ ] Grounding means [ ] Lines (bleeding, blanking/blinding) [ ] Other: <empty> Other safety considerations, as required: (also circle applicable items within the parentheses) [ ] Confined space (requires additional permit) [ ] Fire hazards (fire extinguisher, area free of combustibles) [ ] Restrict area (barricade, safety tape) [ ] Welding (sparks, shield arcs) [ ] Safe access (ladder, aerial device, scissor lift) [ ] Other: <empty> Approval: Signature: <empty> Print name/title (i.e., Safety Manager, Supervisor): <empty> Date: <empty> [ ] Job complete [ ] Job incomplete Notes: <empty> The authorized worker holds this permit during the work activity and returns it to the approver after woβ¦
[3] Fall Protection - Working at Heights Rescue Plan
Page 4
Open source documentSource excerpt
# Fall Protection - Working at Heights Rescue Plan (cont.) ## What should be included in a working at heights rescue plan? (cont.) Other key considerations include determining how a rescue will be initiated and making sure the appropriate equipment is available and maintained. The ability to respond very quickly and retrieve the worker is essential. Plan for situations where the worker is injured, including procedures for first-aid, medical treatment, and getting the injured worker to the hospital. The quickest route to the hospital should be determined. In locations far from a hospital, additional measures may be needed to make sure a worker can receive appropriate medical attention, as required. Immediately before work begins, another assessment should be done to ensure that the rescue plan is still appropriate and that no additional hazards or factors have been overlooked. Check and follow any legislative requirements regarding rescue at heights in your jurisdiction. ## What personal protective equipment (PPE) do rescuers need to use? The required personal protective equipment will depend on the hazards and risks present and should be specified in the fall rescue plan. Common personal protective equipment includes fall protection equipment, head protection, eye protection, high-visibility apparel, gloves, safety footwear, and other equipment. A first-aid kit and rescue equipment and accessories will also be required. ## How are hazards identified and risks assessed for a rescue at heights? Developing a systematic and comprehensive method for identifying hazards and assessing risk is essential. Risk assessments should be done well in advance and again immediately before and during the work as conditions can change. The team responsible for developing the rescue plan needs to identify all hazards that may cause harm to workers during the work and a potential rescue. Hazards may include: - sources that may damage equipment or infrastructure, such as the prβ¦
[4] An Introduction to Personal Fall Protection Equipment
Page 11
Open source documentSource excerpt
# Full body harnesses (cont.) ## Webbing Look for frayed, cracked, cut, burned, or damaged webbing, and loose or broken stitching. ## D-rings Look for bent, cracked, nicked, or gouged rings. ## Manufacturer's label Inspect the manufacturer's label on the harness. The manufacturer's label on a CSA-approved full body harness will contain the following information: - Manufacturer or vendor identification β’ Size of the harness β’ Date the harness was manufactured β’ Model number Some harnesses are designed to serve more than one purpose. Check the manufacturer's label for the harness's classification. Group A - Fall arresting Group D Controlled descent Group E-Confined entry (raising and lowering) Group L - Ladder climbing Group P - Work positioning Note: A full body harness that meets CSA Standard Z259.10 is acceptable to WorkSafeBC. ## Putting on a full body harness Adjust all hardware and straps so the harness fits snugly, but still lets you move freely. Tuck in all loose straps so they don't snag or cause you to trip. Hook on to the harness D-ring (marked "A") designed to arrest falls. ## Lanyards and anchors A lanyard is a flexible line of webbing or a synthetic or wire rope used to secure a safety belt or full body harness to a lifeline or anchor. ## Using the right lanyard A lanyard that meets the requirements of CSA Z259.1 is acceptable to WorkSafeBC. Keep lanyards as short as possible to reduce the distance you could fall. Try to arrange the lanyard to limit a free fall to no more than 1.2 m (4 ft.) in a fall arrest situation. When using a wire rope lanyard for fall arrest, a personal shock absorber must be incorporated as part of your personal fall protection system in order to keep the arrest force at a safe level. An Introduction to Personal Fall Protection Equipment -6-
[5] Program Directive: Walking-Working Surfaces and Personal Protective Equipment (Fall Protection Systems), Final Rule; and Other Related Provisions
Page 11
Open source documentSource excerpt
# Walking-Working Surfaces and Personal Protective Equipment (Fall Protection Systems), Final Rule; and Other Related Provisions (cont.) ## Subpart D-Walking-Working Surfaces (cont.) [redacted postal code] Federal Register/Vol. 81, No. 223/Friday, November 18, 2016/Rules and Regulations. Low-slope roof means a roof that has a slope less than or equal to a ratio of 4 in 12 (vertical to horizontal). Lower level means a surface or area to which an employee could fall. Such surfaces or areas include, but are not limited to, ground levels, floors, roofs, ramps, runways, excavations, pits, tanks, materials, water, equipment, and similar surfaces and structures, or portions thereof. Manhole steps means steps that are individually attached to, or set into, the wall of a manhole structure. Maximum intended load means the total load (weight and force) of all employees, equipment, vehicles, tools, materials, and other loads the employer reasonably anticipates to be applied to a walking-working surface at any one time. Mobile means manually propelled or moveable. Mobile ladder stand (ladder stand) means a mobile, fixed-height, self- supporting ladder that usually consists of wheels or casters on a rigid base and steps leading to a top step. A mobile ladder stand also may have handrails and is designed for use by one employee at a time. ta Mobile ladder stand platform means a mobile, fixed-height, self-supporting unit having one or more standing platforms that are provided with means of access or egress. Open riser means the gap or space between treads of stairways that do not have upright or inclined members (risers). Opening means a gap or open space in a wall, partition, vertical walking- working surface, or similar surface that is at least 30 inches (76 cm) high and at least 18 inches (46 cm) wide, through which an employee can fall to a lower level. Personal fall arrest system means a system used to arrest an employee in a fall from a walking-working surface. Iβ¦
[6] Fatality Narrative: Foreman Performing Maintenance Work on Fuel Storage Tank Killed in Explosion
Page 1
Open source documentSource excerpt
# Fatality Narrative Foreman Performing Maintenance Work on Fuel Storage Tank Killed in Explosion* Industry: Specialty trade contractor. Occupation: Foreman. Task: Preparing fuel tank for permit required confined space entry. Type of Incident: Explosion. Release Date: March 10, 2008. Case No.: 07WA02101. SHARP Report No.: 71-69-2008. On March 28, 2007, a foreman died when a fuel tank exploded. The 60-year-old victim, a foreman, was an 18-year employee of a specialty trade contractor that installs linings and coatings for storage tanks. The contractor was hired by a bulk petroleum distributor to apply an epoxy coating to the inside of four 15,000 gallon above ground fuel (gasoline) storage tanks. Prior to the incident, two of the 20' x 11' tanks had been drained of fuel and their interiors, vented with a blower, abrasively blasted, cleaned, and coated with a two-part epoxy. A third tank was being prepared for a permit-required confined space entry by five workers, including the victim, a co-worker, a temporary help agency contracted worker, and two oil company employees. A worker placed an electric blower outside the tank near its base by an open hatch in order to ventilate the tank by sucking air out. The vents at the top of the tank were not opened to allow fresh air to circulate through the tank. The blower was not rated for use in areas where flammable gases or vapors may present. The victim approached the tank to move the blower to do air testing to determine whether it was safe for workers to enter the tank. When the victim moved the still operating blower, a flame shot into the tank where flammable vapors were ignited and an explosion occurred. The victim was killed and a co- worker and two oil company employees received extensive burn injuries. An investigation determined that the probable cause of the explosion was 1) the blower and its extension cord were not rated for use in flammable atmospheres and 2) there may have been a static disβ¦
[7] Confined Space Entry Permit
Page 1
Open source documentSource excerpt
# Confined space entry permit Permit date: <empty> Work shift: [ ] 1st [ ] 2nd [ ] 3rd Expires: <empty> Time started: <empty> Permit space to be entered (name and location of space): <empty> Purpose of entry: <empty> ## Names of trained, authorized individuals Emergency contact information Entry supervisor: Emergency responder: Entry attendant: Contact person: Authorized entrants: Phone number: Authorized entrants: Time: ## Pre-entry checklist Do not enter this permit space until the following "needs action" conditions are corrected: <table><tr><th>OK</th><th>Needs action</th><th></th></tr><tr><td></td><td></td><td>Before entering the permit space, the supervisor or designee must notify the rescue team. IDLH conditions require at least one rescue team member located outside the space.</td></tr><tr><td></td><td></td><td>A minimum of two employees must be assigned to work involving permit space entry. One employee must remain outside the permit space at all times</td></tr><tr><td></td><td></td><td>The surrounding area must be surveyed to show that it is free of hazards such as drifting vapors from tanks, piping, sewers, or vehicle exhaust.</td></tr><tr><td></td><td></td><td>Those responsible for operation of the gas monitor have been trained.</td></tr><tr><td></td><td></td><td>Gas monitor calibration tests and functional test (fresh air calibration) have been performed this shift on the gas monitor. If so, by whom?</td></tr><tr><td></td><td></td><td>The atmosphere will be continuously monitored while the space is occupied, if required by entry procedure.</td></tr></table> <table><tr><th colspan="8">Pre-entry requirements</th></tr><tr><td>Requirements</td><td>Yes</td><td>No</td><td>N/A</td><td>Requirements</td><td>Yes</td><td>No</td><td>N/A</td></tr><tr><td>Lockout-tagout/de-energize</td><td></td><td></td><td></td><td>Hot work permit</td><td></td><td></td><td></td></tr><tr><td>Pipes(s) broken or capped or blanked</td><td></td><td></td><td></td><td>Fall β¦
[8] Fall Prevention Training Guide A Lesson Plan for Employers
Page 14
Open source documentSource excerpt
# Third Talk: Roofing Work Safety (cont.) ## How to protect workers from fall hazards: (cont.) β’ Personal Fall Arrest Systems (PFASS), or fall restraints consisting of: a) Anchorage A fixed and secured point of attachment for lifelines, lanyards, or deceleration devices capable of supporting 5,000 lbs. Sound anchorages include: structural members, but not standpipes, vents, other piping systems and electrical conduit. b) Body Harness _ - Straps which may be secured to the body in a manner which will distribute fall arrest forces over the thighs, pelvis, waist, chest and shoulders, with a means to attach to other components of a PFAS. c) Connectors - Devices used to couple/ connect parts of the PFAS and positioning system devices together, e.g. a carabiner or an integral part of the system such as a dee-ring or buckle (sewn into a body harness) or a locking snap-hook. d) Deceleration Device β Any mechanism, such as a rope grab, rip-stitch lanyard, specially-woven lanyard, tearing or deforming lanyards, automatic self- retracting lifelines/lanyards, which serves to dissipate a substantial amount of energy during a fall arrest, or otherwise limit the energy imposed on an employee during fall arrest. ## INSPECTIONS Daily inspections are required prior to use of PFASS for wear damage, deterioration or other component defect and if observed, the PFAS must be immediately removed from service. ## Other forms of fall protection systems include: β’ Guardrail Systems - 1926.502(b), . Safety Net Systems - 1926.502(c), Warning Line Systems β 1926.502(f), β’ Controlled Access Zones - 1926.502(g), Safety Monitor Systems - 1926.502(h), and - Hole Covers 1926.502(i). ## Fall prevention practices Who has seen or heard of a worker who sat on a skylight for a break, a drink or a smoke, and then, the skylight breaks, and the worker falls onto the concrete floor below? Yet we don't even need a skylight, or a floor opening to fall through a roof! We can over-load a roof wiβ¦
[9] FATALITY NARRATIVE: Welder Fell 32 Feet from Storage Tank Roof
Page 1
Open source documentSource excerpt
WASHINGTON State FACE Program Fatality Assessment & Control Evaluation CONSTRUCTION # FATALITY NARRATIVE FACE INCIDENT FACTS ## Welder Fell 32 Feet from Storage Tank Roof REPORT DATE: November 1, 2024 ## SUMMARY REPORT #: 71-260-2024 INCIDENT DATE: April 27, 2023 WORKER: 60 years old ## INDUSTRY: Oil and Gas Pipeline and Related Structures Construction ## OCCUPATION: Construction Welder ## SCENE: Storage tank construction site ## EVENT TYPE: Fall from elevation Hole in roof where welder fell. A 60-year-old welder fell 32 feet while constructing the leading edge of a storage tank roof. His employer was an aboveground storage tank manufacturer. He had over 40 years of job experience. He was with three other workers constructing the leading edge with sheets of metal sheathing. The roof was 76-feet wide by 34.5-feet high, with a 1 in 12 pitch. He was acting as a "spotter" for a crane operator who was hoisting the sheets to cover a 16-foot hole remaining on the roof. After unloading the sheets, he needed to tack Storage tank at incident site. weld one near the center peak of the roof. He stepped from the leading edge to a rafter over part of the hole. He then sat down on the rafter and extended his legs two and a half feet across the hole to another rafter. While sitting on the rafter, he used a pry bar to bend and move the sheet into place for welding. As he pried, he fell backward through the hole between the rafter and leading edge. After landing on the ground, he was badly hurt but still conscious and breathing. Emergency responders arrived and had a critical care helicopter airlift him to the hospital. He died the next day. Following the incident, investigators found: β’ The welder and his co-workers had tied off while riding a boom lift to the roof, but their supervisor allowed them to remove their personal fall arrest system (PFAS) harnesses on the roof. β’ The workers and their supervisor discussed the fall hazards and the general contrβ¦
[10] Fall Protection Work Plan
Page 1
Open source documentSource excerpt
Washington State Department of Labor & Industries Division of Occupational Safety and Health # Fall Protection Work Plan WAC 296-880-[redacted postal code]: You must develop and implement a written fall protection work plan including each area of the work place where the employees are assigned and where fall hazards of 10 feet or more exist and be available on the job site for inspection by the department. Company Name Date Company Name:<empty> Date:<empty> Site Address:<empty> (If additional space is needed, use the back of the sheet.) Identify all fall hazards 10 feet or more above the ground or lower level. Check all that apply. [ ] Open-sided floors [ ] Openings [ ] Leading edge work [ ] Decks/Balconies [ ] Roof [ ] Mobile lift work [ ] Hole [ ] Skylights Methods of fall protection to be used: (LSO = Low Slopes Only. Low Slope = 4 x 12 or less) [ ] Personal fall arrest system [ ] Safety watch system (LSO) [ ] Warning line system (LSO) [ ] Catch platform [ ] Positioning device system [ ] Safety net [ ] Covers [ ] Horizontal life lines [ ] Vertical life lines & rope grab [ ] Personal fall restraint system [ ] Warning line with safety monitor (LSO) Name of safety watch or monitor (if used):<empty> Overhead Hazard Protection Methods [ ] Hard Hats [ ] Toe boards on guardrails [ ] Other:<empty> [ ] Overhead Hazard Signs [ ] Screens on guardrails [ ] Other:<empty> [ ] Debris Nets [ ] Barricade to control access to area Describe procedures for assembly, maintenance, inspection, disassembly of fall protection system to be used.:<empty> Describe procedures for handling, storage, and securing tools, equipment, and materials.:<empty> Describe methods of overhead protection for workers who may be in, or pass through work area.:<empty> Describe method for prompt rescue of employees in the event of a fall.:<empty> Employees who received fall protection training on the above site specific fall protection work plan. Name(s):<empty> Date:<empty> <empty> <empty> <eβ¦
[11] Fall Protection - Working at Heights Rescue Plan
Page 2
Open source documentSource excerpt
# Fall Protection - Working at Heights Rescue Plan (cont.) ## What is a working at heights rescue plan? (cont.) Relying only on calling for local emergency services after an incident as a rescue plan is not appropriate. Workers who fall and become suspended in their fall arrest harness need to be rescued immediately. Suspension trauma (also referred to as orthostatic intolerance) involves blood pooling in the lower body, reducing the amount of oxygen available to the brain and other vital organs. It occurs when a worker hangs in the harness for too long. The harness may create pressure, preventing the blood from circulating, or the worker may be in shock, unconscious, or otherwise not able to move their legs, causing blood to pool in their lower limbs. This trauma can occur in minutes and can cause serious health effects such as damage to the brain, kidneys or other organs. Death may occur in less than 30 minutes. The worker may have sustained an injury from the fall or be unconscious and be unable to rescue themselves or assist the rescuers. A rescue may be needed if a worker experiences a medical emergency while working at heights, such as heat stroke, fainting, and cardiovascular or respiratory distress, and is unable to get down on their own or requires immediate medical assistance. The plan must also consider that the conditions or hazards that caused the fall may also be a risk to other workers, including the rescuers. ## What elements should a rescue plan include? Before a specific task begins, make sure that the plan covers any possible scenarios experienced at the specific worksite. Adjust and modify the rescue plan as needed. A rescue plan should include the following details: - Be written, reviewed and posted before work begins - Identify who will conduct the rescue and their roles and responsibilities - Include procedures for identifying, assessing, and controlling hazards - Outline training requirements for both rescue personnel and workβ¦
[12] FATALITY NARRATIVE: Laborer Falls through Roof Opening
Page 1
Open source documentSource excerpt
FACE/WA Fatality Assessment FATALITY NARRATIVE and Control Evaluation # Laborer Falls through Roof Opening * Industry: General contracting Task: Repairing roof Occupation: Construction laborer Type of Incident: Fall through roof opening Incident Date: October 31, 2011 Release Date: January 25, 2013 SHARP Report No.: 71-117-2013 Case No.: 11WA046 On Oct. 31, 2011, an 18-year-old laborer was fatally injured when he fell through a roof opening. He was an employee of a contractor who was replacing rotten plywood sheathing and joists on a warehouse roof. The victim, a foreman, and another laborer were working on the building's flat roof tearing out 4'x8' plywood sections and nailing new ones in place. The victim was wearing a full-body harness with a lanyard and using two lifelines hooked together with one of the lines looped around a skylight frame, which served as an anchor point. The other two employees were not using fall protection. The two laborers were taking nails out of a sheet of plywood they had removed when their foreman asked them to move out of the way so that he could place a new sheet of plywood over the roof opening they had exposed. They were then to nail the plywood in place. When the victim moved aside, he stepped onto two pieces of rotten plywood that were not nailed down, and the plywood pieces and unattached joist supporting them gave way. An investigation determined that his rope grab was attached near the end of his lifeline which left too much slack in the line allowing him to fall 30 feet to a concrete floor. ## Requirements β’ When employees are exposed to a hazard of falling from a location 10 feet or more in height, the employer must ensure that fall restraint, fall arrest systems or positioning device systems are provided, installed and implemented according to the requirements of WAC 296-155-[redacted postal code]. β’ Employers must develop and implement a fall protection work plan including each area of the work placβ¦
[13] Confined Space Entry
Page 1
Open source documentSource excerpt
WORK SAFE KENTUCKY Free safety resources provided by KEMI HOME SAFETY RESOURCES SAFETY TRAINING SAFETY BLOG ABOUT KEMI CONTACT US O # Confined Space Entry ## Print a Sign-In Sheet | Spanish Version Coming Soon ## What is a Confined Space? The Occupational Safety and Health Administration (OSHA) permit- required confined space standard defines a confined space as a space that is large enough for an employee to enter, has restricted means of entry or exit, and is not designed for continuous employee occupancy. A permit-required confined space (permit space) is a confined space that presents or has the potential for hazards related to atmospheric conditions (toxic, flammable, asphyxiating), engulfment, conflagration, or any other recognized serious hazard. Regulations governing entry into confined spaces are specified by OSHA. You can find these regulations at 29 CFR 1910.146. Examples of confined spaces include ship compartments, missile fuel tanks, vats, silos, sewers, tunnels, and vaults. ## Hazards Confined Space Hazards Dangerous vapors and gases can accumulate in confined spaces. Fires, explosions, and physical hazards can also injure or kill an unprotected worker. Physical Hazards Physical hazards may result from mechanical equipment or moving parts, like agitators, blenders, and stirrers. Other physical hazards include heat and sound. Temperatures can build up quickly in a permit space and cause exhaustion or dizziness. Sounds may reverberate and make it hard to hear important directions or warnings. ## Oxygen Deficiency The primary hazard associated with confined spaces is oxygen deficiency. Oxygen may be reduced in a space either by displacement or consumption. Oxygen is displaced by other gases such as argon, nitrogen, r methane. Consumption may be caused by chemical reactions such as rusting, rotting, fermentation, or burning of flammable substances. ## Combustibility Fire and explosion are serious dangers in permit spaces because fumes andβ¦
[14] Hazard and Risk - Sample Risk Assessment Form
Page 3
Open source documentSource excerpt
# What is a sample risk assessment form? (cont.) ## Sample Risk Assessment Form (cont.) <table><tr><th>Step or task</th><th>Hazard</th><th>Consequences or harm</th><th>Risk</th><th>Priority</th><th>Hazard Controls</th></tr><tr><td>EXAMPLE: Working at heights while on a ladder</td><td>Safety hazard: falling from heights</td><td>Serious injury due to a fall</td><td>High risk</td><td>1</td><td>Follow the hierarchy of controls for working at heights Elimination: when possible, perform work from the ground. Engineering controls: use an elevating work platform when appropriate. Administrative controls:</td></tr><tr><td></td><td></td><td></td><td></td><td></td><td>development of fall protection plans, safe work procedures, emergency response plans for working at heights, and adequate training (including working heights and fall protection training, elevating work platform training, ladder safety, training on safe work procedures and emergency response, etc.). Personal protective equipment: fall arrest system and equipment, head protection, high-visibility. clothing, protective footwear, face and eye protection, emergency response equipment, and other appropriate equipment for the job.</td></tr><tr><td></td><td></td><td></td><td></td><td></td><td></td></tr><tr><td></td><td></td><td></td><td></td><td></td><td></td></tr></table> Hazard and Risk - Sample Risk Assessment Form CCOHS
[15] Fall Protection - Working at Heights Rescue Plan
Page 3
Open source documentSource excerpt
# Fall Protection - Working at Heights Rescue Plan (cont.) ## What elements should a rescue plan include? (cont.) - Include procedures for: - rescue, including rope rescue, ladder rescue, retrieval lines, self-rescue, and location of anchor points - using any powered mobile equipment, mechanical hoisting systems or elevating devices that may be required during the rescue - first-aid and medical care for rescued or injured workers, including transport of the worker to the hospital - Identify the communication system that will be used. Make sure there is a backup system for the main method of communication - Identify all emergency exits and access routes within the worksite, including the roof and work area - Include procedures to clear and secure work areas that are unsafe or may interfere with a rescue - Provide contact information for local emergency medical and fire services, as appropriate (NOTE again: Relying only on calling local emergency services after an incident as a rescue plan is not appropriate.) - Review and update as needed (e.g., on a regular schedule, after changes to the worksite or tasks, and after a rescue or related incident) ## What should be included in a working at heights rescue plan? There are many factors to consider when developing a rescue plan. It is important to begin planning well before any work is done at heights to make sure the rescue plan is appropriate and that the rescue team is thoroughly trained. When developing the plan, involve qualified individuals competent in rescue at heights and those workers doing the work. Make sure the plan is specific for the job and considers the hazards, location, tasks being performed, environmental conditions, how and where a worker could fall and the type of rescue that would be needed, among other factors. Identify the hazards associated with the rescue. This information determines the rescue procedures, what equipment will be required, who will be on the rescue team, and wβ¦
