Hazard Identification:
- Falls from Height: This is a primary hazard when working on scaffolds [1]. Workers can fall from the platform level or while accessing/egressing the scaffold. Fall hazards are present when erecting or dismantling scaffolds [1].
- Scaffold Collapse: Overloading, improper construction, or using damaged components can lead to scaffold collapse [2]. Environmental factors like wind or ice can also compromise stability [3].
- Falling Objects: Tools, materials, or debris falling from the scaffold can injure workers below [4].
- Electrocution: Scaffolds near power lines pose a risk of electrocution if contact occurs [2].
- Material Handling: Lifting materials onto the scaffold can create struck-by hazards or cause instability [5].
- Access/Egress: Improper access such as using cross braces can lead to falls [6].
Risk Assessment:
- Likelihood: The likelihood of these hazards occurring depends on factors like worker training, supervision, scaffold inspection frequency, and environmental conditions.
- Severity: The severity of incidents can range from minor injuries to serious injuries or fatalities.
Control Measures:
- Elimination/Substitution: Where possible, eliminate the need for scaffolding by using alternative methods like aerial lifts. If scaffolding is necessary, select the appropriate type for the task [7].
- Engineering Controls:
- Guardrails: Install guardrails on all open sides and ends of scaffolds to prevent falls [5].
- Toeboards: Use toeboards to prevent tools and materials from falling off the scaffold [5].
- Overhead Protection: Provide overhead protection if workers are exposed to falling objects 3, 13.
- Secure Scaffold: Ensure the scaffold is erected on a firm foundation and is plumb and level [8]. Secure it to the building at appropriate intervals to prevent lateral movement [8].
- Administrative Controls:
- Competent Person: A competent person must supervise the erection, dismantling, and alteration of scaffolds [2] and inspect scaffolds before each work shift [2].
- Training: Provide comprehensive training to workers on scaffold safety, including proper use, inspection, and fall protection [5].
- Load Limits: Clearly communicate and enforce the maximum load limits for the scaffold [9].
- Tagging: Implement a scaffold tagging system to indicate its safety status [9].
- Weather Conditions: Prohibit work on scaffolds during storms or high winds [5].
- Housekeeping: Maintain good housekeeping practices to prevent slip, trip, and fall hazards [3].
- Personal Protective Equipment (PPE):
- Fall Protection: Provide and ensure the use of personal fall arrest systems (PFAS) when working at heights [1]. Ensure proper anchorage points are used [7].
- Head Protection: Workers should wear hard hats to protect against falling objects.
- Foot Protection: Wear appropriate footwear with slip-resistant soles.
Monitoring and Review:
- Regularly inspect scaffolds for damage or defects [2].
- Review safety procedures and training programs periodically.
- Investigate incidents and near misses to identify areas for improvement.
Specific Recommendations:
- Ensure scaffolds are designed to support at least four times the intended load [8].
- Provide safe access to the scaffold, such as ladders or scaffold stairs [4].
- Never use cross braces as a means of access [6].
- Maintain a safe distance from power lines, or ensure they are de-energized [6].
- Use tag lines when hoisting materials to prevent uncontrolled swinging [3].
- Do not allow debris to accumulate on scaffold platforms [3].
- Ensure platforms are fully planked or decked with minimal gaps [10].
- Workers must visually inspect the scaffold before each use [8].
- Keep drawings and supplementary information regarding the scaffold at the worksite [11].
This risk assessment provides a framework for managing scaffold-related hazards. It should be adapted to the specific conditions of each worksite and task.
Sources used for this answer
[1] Occupational Health and Safety Regulations, 2020 (Sask. Reg. 10/2020)
Page 103
Open source documentSource excerpt
## OCCUPATIONAL HEALTH AND SAFETY, 2020 - (3) While a scaffold mentioned in subsection (1) is being constructed, erected, used, maintained or dismantled, an employer, contractor or owner shall keep at the worksite all drawings and supplementary information regarding the scaffold, including: - (a) the dimensions, specifications, type and grade of all components of the scaffold; and - (b) the maximum load and the maximum working load that the scaffold is designed or manufactured to support. - (4) An employer, contractor or owner shall make readily available to the workers a copy of the drawings and supplementary information mentioned in subsection (3). 31 Dec 2020 c S-15.1 Reg 10 s12-10. ## Half-horse scaffolds - 12-11 (1) An employer or contractor shall ensure that the legs of a half-horse scaffold are not spliced, are less than 3 metres high and have an angle of repose and an angle of splay that are 15 from the vertical. ° - (2) An employer or contractor shall ensure that a ladder is used to provide access to and exit from a half-horse scaffold. 31 Dec 2020 c S-15.1 Reg 10 s12-11. ## Bracket scaffolds 12-12 An employer or contractor shall ensure that the brackets of a bracket scaffold are securely attached to prevent the brackets from dislodging and are not more than 3 metres apart. 31 Dec 2020 c S-15.1 Reg 10 s12-12. ## Ladderjack scaffolds - 12-13 An employer or contractor shall ensure that: - (a) brackets and ladders used for a ladderjack scaffold are: - (i) designed and constructed to support the anticipated load safely; and - (ii) used according to the manufacturer's specifications and recommendations; and - (b) ladders used for a ladderjack scaffold are not more than 3 metres apart. 31 Dec 2020 c S-15.1 Reg 10 s12-13. ## Single-pole scaffolds - 12-14 An employer or contractor shall ensure that: - (a) a single-pole scaffold is adequately supported in 2 directions by a system of diagonal braces that are: - (i) not more th…
[2] Rules for the Administration of the Oregon Safe Employment Act (Construction, Division 3, OSHA Oregon)
Page 522
Open source documentSource excerpt
## GENERAL REQUIREMENTS ## §1926.451 General Requirements. This section does not apply to aerial lifts, the criteria for which are set out exclusively in §1926.453. ## (a) Capacity. - (1) Except as provided in paragraphs (a)(2), (a)(3), (a)(4), (a)(5) and (g) of this section, each scaffold and scaffold component shall be capable of supporting, without failure, its own weight and at least 4 times the maximum intended load applied or transmitted to it. - (2) Direct connections to roofs and floors, and counterweights used to balance adjustable suspension scaffolds, shall be capable of resisting at least 4 times the tipping moment imposed by the scaffold operating at the rated load of the hoist, or 1.5 (minimum) times the tipping moment imposed by the scaffold operating at the stall load of the hoist, whichever is greater. - (3) Each suspension rope, including connecting hardware, used on non-adjustable suspension scaffolds shall be capable of supporting, without failure, at least 6 times the maximum intended load applied or transmitted to that rope. - (4) Each suspension rope, including connecting hardware, used on adjustable suspension scaffolds shall be capable of supporting, without failure, at least 6 times the maximum intended load applied or transmitted to that rope with the scaffold operating at either the rated load of the hoist, or 2 (minimum) times the stall load of the hoist, whichever is greater. - (5) The stall load of any scaffold hoist shall not exceed 3 times its rated load. - (6) Scaffolds shall be designed by a qualified person and shall be constructed and loaded in accordance with that design. Non-mandatory Appendix A to this subpart contains examples of criteria that will enable an employer to comply with paragraph (a) of this section. ## (b) Scaffold platform construction. - (1) Each platform on all working levels of scaffolds shall be fully planked or decked between the front uprights and the guardrail supports as follows: - (i) Each plat…
[3] General Regulation (N.B. Reg. 91-191)
Page 136
Open source documentSource excerpt
- (c) is designed and constructed to support at least four times the load that may be imposed on it, - (d) if 3 m or more in height, has a guardrail that meets the requirements of section 97, - (e) is erected plumb and level, - (f) has vertical supports resting upon a firm founda -tion or sills, - (g) is adequately secured at vertical intervals not ex -ceeding three times the least lateral dimension of the scaffold, measured at the base, to prevent lateral movement, - (h) if sawn lumber planks are used as a platform, has a platform that is at least 500 mm wide, and - (i) if using manufactured scaffold planks, has a plat -form that is at least 450 mm wide. - 131 (2) Paragraph (1)( d ) does not apply to a mobile rolling scaffold. - 131 (3) Subject to subsection (4), an employer shall en -sure that the spacing of vertical supports and bearers of a scaffold does not exceed 3 m on centres. - 131 (4) Where a scaffold is to be used for bricklaying, masonry or other heavy work, an employer shall ensure that the spacing of vertical supports and bearers of a scaffold does not exceed 2.1 m on centres. 2001-33; 2010-159; 2024-38 ## Scaffolds - employee requirements 2024-38 - 131.1 An employee who uses a scaffold shall - (a) visually inspect the scaffold before each use, and - c) est conçu et construit de façon à soutenir une charge quatre fois plus lourde que la charge qui peut lui être appliquée, - d) s'il a une hauteur d'au moins 3 m, est muni d'un garde-corps qui satisfait aux exigences que pré -voit l'article 97, - e) est installé droit et à niveau, - f) est muni de supports verticaux reposant sur une fondation solide ou sur des semelles, - g) est assujetti de manière convenable à des inter -valles verticaux qui ne dépassent par trois fois la moindre des dimensions latérales de l'échafaudage, mesuré à partir de la base, pour prévenir les mouve -ments latéraux, - h) est muni d'une plate-fo…
[4] Occupational Health and Safety Code
Page 186
Open source documentSource excerpt
325 (3) An employer must ensure that a scaffold used to carry the equivalent of an evenly distributed load of more than 367 kilograms per square metre is - (a) designed and certified by a professional engineer, and - (b) constructed, maintained and used in accordance with the certified specifications. - 325 (4) Subsection (3) applies to a type of scaffold that is not otherwise specifically referred to in this Code. 325 (5) An employer must ensure that all workers on a scaffold are informed of the maximum load that the scaffold is permitted to carry. ## Tagging requirements 326 (1) An employer must ensure that a scaffold is colour coded using tags at each point of entry indicating its status and condition as follows: - (a) a green tag with 'Safe for Use', or similar wording, to indicate it is safe for use; - (b) a yellow tag with 'Caution: Potential or Unusual Hazard', or similar wording, to indicate the presence of a potential or unusual hazard; - (c) a red tag with 'Unsafe for Use', or similar wording, to indicate it is not safe to use. 326 (2) An employer must ensure that a bracket scaffold, double-pole scaffold, needle-beam scaffold, outrigger scaffold, single-pole scaffold, suspended scaffold or swingstage scaffold erected but not immediately put into service, or not used for more than 21 consecutive calendar days, has a red tag at each point of entry until it is inspected and tagged by a competent worker for use. - 326 (3) An employer must ensure that a bracket scaffold, double-pole scaffold, needle-beam scaffold, outrigger scaffold, single-pole scaffold, suspended scaffold or swingstage scaffold is inspected and tagged by a competent worker before it is used for the first time and at intervals of not more than 21 calendar days while workers work from the scaffold or materials are stored on it. 326 (4) A tag attached to a scaffold under this section expires 21 calendar days after the date of the inspection it records. - 326 (5) A tag required by this s…
[5] Rules for the Administration of the Oregon Safe Employment Act (Construction, Division 3, OSHA Oregon)
Page 532
Open source documentSource excerpt
## GENERAL REQUIREMENTS - (iii) When erecting or dismantling tubular welded frame scaffolds, (end) frames, with horizontal members that are parallel, level and are not more than 22 inches apart vertically may be used as climbing devices for access, provided they are erected in a manner that creates a usable ladder and provides good hand hold and foot space. - (iv) Cross braces on tubular welded frame scaffolds shall not be used as a means of access or egress. ## (f) Use. - (1) Scaffolds and scaffold components shall not be loaded in excess of their maximum intended loads or rated capacities, whichever is less. - (2) The use of shore or lean-to scaffolds is prohibited. - (3) Scaffolds and scaffold components shall be inspected for visible defects by a competent person before each work shift, and after any occurrence which could affect a scaffold's structural integrity. - (4) Any part of a scaffold damaged or weakened such that its strength is less than that required by paragraph (a) of this section shall be immediately repaired or replaced, braced to meet those provisions, or removed from service until repaired. - (5) Scaffolds shall not be moved horizontally while employees are on them, unless they have been designed by a registered professional engineer specifically for such movement or, for mobile scaffolds, where the provisions of §1926.452(w) are followed. - (6) The clearance between scaffolds and power lines shall be as follows: Scaffolds shall not be erected, used, dismantled, altered, or moved such that they or any conductive material handled on them might come closer to exposed and energized power lines than as follows: ## Insulated Lines Exception to paragraph (f)(6): Scaffolds and materials may be closer to power lines than specified above where such clearance is necessary for performance of work, and only after the utility company, or electrical system operator, has been notified of the need to work closer and the utility company, or electrical syst…
[6] General Regulation (N.B. Reg. 91-191)
Page 138
Open source documentSource excerpt
- (c) is secured to prevent movement in any direction that may endanger an employee, and - (d) has a slip-resistant surface. 2024-38 ## Scaffolds - miscellaneous requirements 133 (1) An employer shall ensure that - (a) lean-to scaffolds on wall brackets are not used, - (b) the inner supports of the supporting members on a single pole scaffold are of adequate construction and securely fastened to a wall, - (c) a safe means of access is provided to all working levels of a scaffold, and - (d) no person uses cross-bracing or diagonal bracing on a scaffold for climbing. ## Protection of employee working below scaffold 133 (2) Where an employee is working on a scaffold above another employee, the employee working above shall ensure that the employee below is protected from the hazard of objects falling from the higher level by overhead protection or by such means as tying off tools and other unsecured objects on the higher level. ## Working on a scaffold 134 An employee who works on a scaffold and an em -ployer shall each ensure that - (a) only materials for current use are kept on the scaffold, - (b) the scaffold is not moved with employees or un -secured tools, materials or equipment on the scaffold, and - (c) a diagonal supporting brace is removed at the working face level only for access and only if precau -tions are taken to ensure that the strength of the scaf -fold is not weakened and the brace is replaced after the work is completed. - c) sont fixés de façon à les empêcher de se déplacer en tout sens de manière à présenter un danger pour les salariés; - d) sont munis d'une surface antidérapante. 2024-38 ## Échafaudages - exigences d'ordre général 133 (1) L'employeur doit s'assurer que - a) les échafaudages étayés sur des consoles murales ne sont pas utilisés, - b) les supports intérieurs des éléments de soutien des échafaudages à écoperche unique sont de cons -truction convenable et …
[7] General Regulation (N.B. Reg. 91-191)
Page 135
Open source documentSource excerpt
- (b) CAN/CSA-B354.2-01 (R2013), Self-Propelled Elevating Work Platforms or a standard offering equivalent or better protection; and - (c) Repealed: 2024-38 - (d) CAN/CSA-B354.4-02 (R2013), Self-propelled boom-supported elevating work platforms or a stand -ard offering equivalent or better protection. - 130 (2) If an employee is required to work from an ele -vating work platform described in paragraph (1)(b), the employer shall provide and the employee shall continu -ally use a travel restraint system or fall-arresting system attached to an anchor point on the elevating work plat -form. - 130 (3) Despite subsection (2), an employee is not re -quired to continually use a travel restraint system or fallarresting system when an elevating work platform - (a) is on a firm and flat surface, - (b) has all the manufacturer's guardrails and chains in place, and - (c) is not moving horizontally or vertically. 2010-159; 2020-35; 2024-38 ## General Provisions Applicable to Scaffolds 2001-33 ## Scaffolds - specifications - 131 (1) An employer and a contractor shall each ensure that a scaffold - (a) is capable of sustaining a minimum uniformly distributed load of 1.4 kPa, - (b) is at no time subjected to a load that exceeds the equivalent of one-quarter of the load for which it is designed, - ou une norme qui assure une protection équivalente ou supérieure; - b) la norme CAN/CSA-B354.2-01 (C2013), intitu -lée Plates-formes de travail élévatrices automotrices , ou une norme qui assure une protection équivalente ou supérieure; - c) Abrogé : 2024-38 - d) la norme CAN/CSA-B354.4-02 (C2013), intitu -lée Plates-formes de travail élévatrices automotrices à bras articulé , ou une norme qui assure une protec -tion équivalente ou supérieure. - 130 (2) Lorsqu'un salarié est tenu de travailler sur une plate-forme de travail montante visée à l'alinéa (1)b), l'employeur fournit et le salarié utilise à tous moments un système de limita…
[8] Safety and Health Regulations for Construction (OSHA)
Page 74
Open source documentSource excerpt
devices for access, provided they are erected in a manner that creates a usable ladder and provides good hand hold and foot space. - (iv) Cross braces on tubular welded frame scaffolds shall not be used as a means of access or egress. - (f) Use. (1) Scaffolds and scaffold components shall not be loaded in excess of their maximum intended loads or rated capacities, whichever is less. - (2) The use of shore or lean-to scaffolds is prohibited. - (3) Scaffolds and scaffold components shall be inspected for visible defects by a competent person before each work shift, and after any occurrence which could affect a scaffold's structural integrity. - (4) Any part of a scaffold damaged or weakened such that its strength is less than that required by paragraph (a) of this section shall be immediately repaired or replaced, braced to meet those provisions, or removed from service until repaired. - (5) Scaffolds shall not be moved horizontally while employees are on them, unless they have been designed by a registered professional engineer specifically for such movement or, for mobile scaffolds, where the provisions of §1926.452(w) are followed. - (6) The clearance between scaffolds and power lines shall be as follows: Scaffolds shall not be erected, used, dismantled, altered, or moved such that they or any conductive material handled on them might come closer to exposed and energized power lines than as follows: EXCEPTION TO PARAGRAPH (F)(6): Scaffolds and materials may be closer to power lines than specified above where such clearance is necessary for performance of work, and only after the utility company, or electrical system operator, has been notified of the need to work closer and the utility company, or electrical system operator, has deenergized the lines, relocated the lines, or installed protective coverings to prevent accidental contact with the lines. - (7) Scaffolds shall be erected, moved, dismantled, or altered only under the supervision and direction of a com…
[9] Rules for the Administration of the Oregon Safe Employment Act (Construction, Division 3, OSHA Oregon)
Page 533
Open source documentSource excerpt
L ## GENERAL REQUIREMENTS - (7) Scaffolds shall be erected, moved, dismantled, or altered only under the supervision and direction of a competent person qualified in scaffold erection, moving, dismantling or alteration. Such activities shall be performed only by experienced and trained employees selected for such work by the competent person. - (8) Employees shall be prohibited from working on scaffolds covered with snow, ice, or other slippery material except as necessary for removal of such materials. - (9) Where swinging loads are being hoisted onto or near scaffolds such that the loads might contact the scaffold, tag lines or equivalent measures to control the loads shall be used. - (10) Suspension ropes supporting adjustable suspension scaffolds shall be of a diameter large enough to provide sufficient surface area for the functioning of brake and hoist mechanisms. - (11) Suspension ropes shall be shielded from heat-producing processes. When acids or other corrosive substances are used on a scaffold, the ropes shall be shielded, treated to protect against the corrosive substances, or shall be of a material that will not be damaged by the substance being used. - (12) Work on or from scaffolds is prohibited during storms or high winds unless a competent person has determined that it is safe for employees to be on the scaffold and those employees are protected by a personal fall arrest system or wind screens. Wind screens shall not be used unless the scaffold is secured against the anticipated wind forces imposed. - (13) Debris shall not be allowed to accumulate on platforms. - (14) Makeshift devices, such as but not limited to boxes and barrels, shall not be used on top of scaffold platforms to increase the working level height of employees. - (15) Ladders shall not be used on scaffolds to increase the working level height of employees, except on large area scaffolds where employers have satisfied the following criteria: - (i) When the ladder is placed agai…
[10] Spider by Brand Safway: Swing Stage Operator’s Manual
Page 4
Open source documentSource excerpt
## 1926.21 Safety Training and Education - (a) General requirements. The Secretary shall, pursuant to Section 107(f) of the ACT, establish and supervise programs for the education and training of employers and employees in the recognition, avoidance and prevention of unsafe conditions in employments covered by the act. - (b) Employer Responsibility. - 1. The employer should avail himself of the safety and health and training programs the Secretary provides. - 2. The employer shall instruct each employee in the recognition and avoidance of unsafe conditions and the regulations applicable to his work environment to control or eliminate any hazards or other exposure to illness or injury. - 3. Employees required to handle or use poisons, caustics, and other harmful substances shall be instructed regarding the safe handling and use, and be made aware of the potential hazards, personal hygiene, and personal protective measures required. ## 1926.28 Personal protective equipment - (a) The employer is responsible for requiring the wearing of appropriate personal protective equipment in all operations where there is an exposure to hazardous conditions or where this section indicates the need for using such equipment to reduce hazards to employees. - (b) Regulations governing the use, selection, and maintenance of personal protective and lifesaving equipment are described under Subpart E below. ## Subpart E ## Section 1926.104 Safety belts, lifelines, and lanyards - (a) Lifelines, safety belts, and lanyards shall be used only for employee safeguarding. Any lifeline, safety belt, or lanyard actually subjected to in-service loading, as distinguished from static load testing, shall be immediately removed from service and shall not be used again for employee safeguarding. - (b) Lifelines shall be secured above the point of operation to an anchorage or structural member supporting a minimum dead weight of 5,400 lbs. - (c) Lifelines used on rock-scaling operations, or in areas…
[11] Rules for the Administration of the Oregon Safe Employment Act (Construction, Division 3, OSHA Oregon)
Page 534
Open source documentSource excerpt
## GENERAL REQUIREMENTS L - (17) To reduce the possibility of welding current arcing through the suspension wire rope when performing welding from suspended scaffolds, the following precautions shall be taken, as applicable: - (i) An insulated thimble shall be used to attach each suspension wire rope to its hanging support (such as cornice hook or outrigger). Excess suspension wire rope and any additional independent lines from grounding shall be insulated; - (ii) The suspension wire rope shall be covered with insulating material extending at least 4 feet (1.2 m) above the hoist. If there is a tail line below the hoist, it shall be insulated to prevent contact with the platform. The portion of the tail line that hangs free below the scaffold shall be guided or retained, or both, so that it does not become grounded; - (iii) Each hoist shall be covered with insulated protective covers; - (iv) In addition to a work lead attachment required by the welding process, a grounding conductor shall be connected from the scaffold to the structure. The size of this conductor shall be at least the size of the welding process work lead, and this conductor shall not be in series with the welding process or the work piece; - (v) If the scaffold grounding lead is disconnected at any time, the welding machine shall be shut off; and - (vi) An active welding rod or uninsulated welding lead shall not be allowed to contact the scaffold or its suspension system. ## (g) Fall protection. - (1) Each employee on a scaffold more than 10 feet (3.1 m) above a lower level shall be protected from falling to that lower level. Paragraphs (g)(1)(i) through (vii) of this section establish the types of fall protection to be provided to the employees on each type of scaffold. Paragraph (g)(2) of this section addresses fall protection for scaffold erectors and dismantlers. Note to paragraph (g)(1): The fall protection requirements for employees installing suspension scaffold support systems on…