Skip to content
All safety questions
Asked by a personGeneral — US and Canadaen-CA

Overhead hazard garbage trucks

A person submitted this question to Rosie's free generator. The asker's identity is neither imported nor published.

Rosie's answer

Published by SALUS

Garbage Truck Operation Near Overhead Power Lines =================================================

Date: 2025-07-30

Duration: \[DURATION] minutes

Presenter: \[PRESENTER NAME]

Location: \[LOCATION]

Objective


The objective of this toolbox talk is to provide you with the knowledge and precautions necessary to safely operate garbage trucks around overhead power lines and other overhead hazards, minimizing the risk of electrical contact and ensuring your well-being.

Introduction


Operating garbage trucks near overhead power lines presents significant electrical hazards. This toolbox talk covers the necessary safety precautions to prevent electrical accidents and ensure safe waste management practices.

Key Points


  • Maintain Safe Distance: Always maintain a safe distance from overhead power lines. The minimum approach distance (MAD) is crucial for preventing electrical contact. [9]

[8] [7] [6] [5] [4] [3]

  • Identify Overhead Hazards: Before starting work, identify all overhead hazards, including power lines, communication cables, and other obstructions. Conduct a thorough site assessment to recognize potential risks.
  • Ensure Proper Grounding: Ensure the truck is properly grounded. Grounding helps to dissipate electrical current in case of accidental contact with a power line, reducing the risk of electric shock.
  • Minimum Approach Distance: Never move any part of the machine or load within 10 feet (3m) plus twice the line insulator length of an electric line. [1]

[2]

  • Stay Inside the Cab: Always remain completely inside the cab enclosure while operating the machine. [1]

[2]

Hazard Identification


  • Contact with overhead power lines: Electrocution, severe burns, equipment damage, fire
  • Unstable ground conditions: Truck rollover, tipping, loss of control
  • Swaying electrical lines: Reduced clearance, unexpected contact
  • Operating under the influence: Impaired judgment, slow reaction time, increased risk of accidents [1]

[2]

Control Measures


  • Maintain Minimum Approach Distance (MAD): Always keep a minimum of 10 feet (3 meters) plus additional clearance based on voltage. Refer to the MAD chart.
  • Use a spotter: Assign a trained spotter to monitor clearances and provide warnings when approaching overhead hazards.
  • Grounding: Ensure the truck is properly grounded to dissipate electrical current.
  • Stay inside the cab: Always remain inside the cab enclosure while operating the machine.

Personal Protective Equipment (PPE) Requirements


  • High-Visibility Vest: High-visibility clothing ensures you are seen by other workers and drivers, especially in low-light conditions.
  • Safety Boots (EH Rated): Wear safety boots with electrical hazard protection to minimize the risk of electric shock.
  • Insulated Gloves: Using insulated gloves can provide an additional layer of protection against electrical hazards.

Real-World Example or Case Study


A garbage truck driver made contact with an overhead power line while trying to maneuver in a residential area. The driver was severely injured, and the truck was damaged. This incident highlights the importance of maintaining a safe distance and using a spotter in confined spaces.

Group Discussion


Discuss the following questions:

  1. What are the specific overhead hazards on your route?
  2. What is the correct minimum approach distance for the voltage of the power lines in our area?
  3. What should you do if you see a coworker operating too close to a power line?

Emergency Procedures


  1. Immediately stop work and call for emergency assistance.
  2. Keep personnel away from the truck to prevent further injuries.
  3. Contact the power company to de-energize the power lines.

Summary


Recap of main points:

  • Always maintain the Minimum Approach Distance (MAD) from overhead power lines.
  • Identify and assess all overhead hazards before starting work.
  • Ensure the truck is properly grounded and use appropriate PPE.
  • Know the emergency procedures in case of electrical contact.

Remember: Safety First: Look Up and Live!

Report all hazards, near-misses, and incidents to your supervisor immediately.

Safety powered by SALUS

9 source record(s)

Sources used for this answer

[1] JLG - Boom Lifts : 400SC, 460SJC - Operation (PN 31215018)

Page 20

Open source document

Source excerpt

# SECTION 1 - SAFETY PRECAUTIONS - Maintain distance from electrical lines, apparatus, or any ener- gized (exposed or insulated) parts according to the Minimum Approach Distance (MAD) as shown in Table 1-1. - Allow for machine movement and electrical line swaying. Table 1-1. Minimum Approach Distances (M.A.D.) <table><tr><th>Voltage Range (Phase to Phase)</th><th>MINIMUM APPROACH DISTANCE in Feet (Meters)</th></tr><tr><td>Oto 50KV</td><td>10(3)</td></tr><tr><td>Over 50KV to 200 KV</td><td>15(5)</td></tr><tr><td>Over 200 KV to 350KV</td><td>20(6)</td></tr><tr><td>Over 350 KV to 500KV</td><td>25(8)</td></tr><tr><td>Over 500 KV to 750KV</td><td>35(11)</td></tr><tr><td>Over 750KV to 1000 KV</td><td>45(14)</td></tr><tr><td colspan="2">NOTE: This requirement shall apply except where employer, local or governmental regulations are more stringent.</td></tr></table> Maintain a clearance of at least 10 ft. (3m) between any part of the machine and its occupants, their tools, and their equip- ment from any electrical line or apparatus carrying up to 50,000 volts. One foot additional clearance is required for every additional 30,000 volts or less. 1-6 31215018

[2] Terex Square Shooters Series SS-624 / SS-636 / SS-836 / SS-842 / SS-1048 (manufactured before 5/01/1999) - Operator's Manual (PN 236491)

Page 11

Open source document

Source excerpt

# GENERAL SAFETY # GENERAL SAFETY PROCEDURES ## AVOID ELECTRICAL POWER LINES ! ## DANGER Serious injury or death can result from contact with electrical lines. NEVER move any part of the machine or load within 10 feet (3m) plus twice the line insulator (A) length of an electric line. EXAMPLE: If the line insulator (A) is 6 in. (152 mm), then twice the length is 12 in. (305mm). Therefore, any part of the machine or load should not be within 11 feet (3.4m) of the electric line. ! ## WARNING Always remain completely inside cab enclosure while operating the machine. ! WARNING Never operate this machine under the influence of drugs and /or alcohol. A T DANGER 1-7

[3] JLG - Boom Lifts : 660SJC - Operation (PN 31217175)

Page 20

Open source document

Source excerpt

# SECTION 1 - SAFETY PRECAUTIONS - Maintain distance from electrical lines, apparatus, or any ener- gized (exposed or insulated) parts according to the Minimum Approach Distance (MAD) as shown in Table 1-1. - Allow for machine movement and electrical line swaying. Table 1-1. Minimum Approach Distances (M.A.D.) <table><tr><th>Voltage Range (Phase to Phase)</th><th>MINIMUM APPROACH DISTANCE in Feet (Meters)</th></tr><tr><td>Oto 50KV</td><td>10(3)</td></tr><tr><td>Over 50KV to 200 KV</td><td>15(5)</td></tr><tr><td>Over 200 KV to 350KV</td><td>20(6)</td></tr><tr><td>Over 350 KV to 500KV</td><td>25(8)</td></tr><tr><td>Over 500 KVto 750KV</td><td>35(11)</td></tr><tr><td>Over 750KV to 1000 KV</td><td>45(14)</td></tr><tr><td colspan="2">NOTE: This requirement shall apply except where employer, local or governmental regulations are more stringent.</td></tr></table> Maintain a clearance of at least 10 ft. (3m) between any part of the machine and its occupants, their tools, and their equip- ment from any electrical line or apparatus carrying up to 50,000 volts. One foot additional clearance is required for every additional 30,000 volts or less. 1-6 31217175

[4] JLG - Boom Lifts : 660SJC - Operation (PN 31215036)

Page 20

Open source document

Source excerpt

# SECTION 1 - SAFETY PRECAUTIONS - Maintain distance from electrical lines, apparatus, or any ener- gized (exposed or insulated) parts according to the Minimum Approach Distance (MAD) as shown in Table 1-1. - Allow for machine movement and electrical line swaying. Table 1-1. Minimum Approach Distances (M.A.D.) <table><tr><th>Voltage Range (Phase to Phase)</th><th>MINIMUM APPROACH DISTANCE in Feet (Meters)</th></tr><tr><td>Oto 50KV</td><td>10(3)</td></tr><tr><td>Over 50KV to 200 KV</td><td>15(5)</td></tr><tr><td>Over 200 KV to 350KV</td><td>20(6)</td></tr><tr><td>Over 350 KV to 500KV</td><td>25(8)</td></tr><tr><td>Over 500 KVto 750KV</td><td>35(11)</td></tr><tr><td>Over 750KV to 1000 KV</td><td>45(14)</td></tr><tr><td colspan="2">NOTE: This requirement shall apply except where employer, local or governmental regulations are more stringent.</td></tr></table> Maintain a clearance of at least 10 ft. (3m) between any part of the machine and its occupants, their tools, and their equip- ment from any electrical line or apparatus carrying up to 50,000 volts. One foot additional clearance is required for every additional 30,000 volts or less. 1-6 31215036

[5] Terex Square Shooters Series SS-624 / SS-636 / SS-836 / SS-842 / SS-1048 (manufactured before /01/1998) - Operator's Manual (PN 236490)

Page 13

Open source document

Source excerpt

# GENERAL SAFETY # GENERAL SAFETY PROCEDURES ## AVOID ELECTRICAL POWER LINES ! ## DANGER Serious injury or death can result from contact with electrical lines. NEVER move any part of the machine or load within 10 feet (3m) plus twice the line insulator (A) length of an electric line. EXAMPLE: If the line insulator (A) is 6 in. (152 mm), then twice the length is 12 in. (305mm). Therefore, any part of the machine or load should not be within 11 feet (3.4m) of the electric line. ! ## WARNING Always remain completely inside cab enclosure while operating the machine. A T DANGER ! ## WARNING Never operate this machine under the influence of drugs and /or alcohol. 1-7

[6] JLG - Boom Lifts : 670SJ - Operation (PN 31215883)

Page 20

Open source document

Source excerpt

# SECTION 1 - SAFETY PRECAUTIONS - Maintain distance from electrical lines, apparatus, or any ener- gized (exposed or insulated) parts according to the Minimum Approach Distance (MAD) as shown in Table 1-1. - Allow for machine movement and electrical line swaying. Table 1-1. Minimum Approach Distances (M.A.D.) <table><tr><th>Voltage Range (Phase to Phase)</th><th>MINIMUM APPROACH DISTANCE in Feet (Meters)</th></tr><tr><td>Oto 50KV</td><td>10(3)</td></tr><tr><td>Over 50KV to 200 KV</td><td>15(5)</td></tr><tr><td>Over 200 KV to 350KV</td><td>20(6)</td></tr><tr><td>Over 350 KV to 500KV</td><td>25(8)</td></tr><tr><td>Over 500 KV to 750KV</td><td>35(11)</td></tr><tr><td>Over 750KV to 1000 KV</td><td>45(14)</td></tr><tr><td colspan="2">NOTE: This requirement shall apply except where employer, local or governmental regulations are more stringent.</td></tr></table> Maintain a clearance of at least 10 ft. (3m) between any part of the machine and its occupants, their tools, and their equip- ment from any electrical line or apparatus carrying up to 50,000 volts. One foot additional clearance is required for every additional 30,000 volts or less. 1-6 31215883

[7] JLG - Boom Lifts : 520AJ HC3 - Operation (PN 31217157)

Page 20

Open source document

Source excerpt

# SECTION 1 - SAFETY PRECAUTIONS - Maintain distance from electrical lines, apparatus, or any ener- gized (exposed or insulated) parts according to the Minimum Approach Distance (MAD) as shown in Table 1-1. - Allow for machine movement and electrical line swaying. Table 1-1. Minimum Approach Distances (MAD) <table><tr><th>Voltage Range (Phase to Phase)</th><th>MINIMUM APPROACH DISTANCE in Feet (Meters)</th></tr><tr><td>Oto 50KV</td><td>10(3)</td></tr><tr><td>Over 50KV to 200 KV</td><td>15(5)</td></tr><tr><td>Over 200 KV to 350KV</td><td>20(6)</td></tr><tr><td>Over 350 KV to 500KV</td><td>25(8)</td></tr><tr><td>Over 500 KV to 750KV</td><td>35(11)</td></tr><tr><td>Over750KV to 1000 KV</td><td>45(14)</td></tr><tr><td colspan="2">NOTE: This requirement shall apply except where employer, local or governmental regulations are more stringent.</td></tr></table> Maintain a clearance of at least 10 ft. (3m) between any part of the machine and its occupants, their tools, and their equip- ment from any electrical line or apparatus carrying up to 50,000 volts. One foot additional clearance is required for every additional 30,000 volts or less. 1-6 31217157

[8] JLG - Boom Lifts : 660SJC - Operation (PN 31219003)

Page 20

Open source document

Source excerpt

# SECTION 1 - SAFETY PRECAUTIONS - Maintain distance from electrical lines, apparatus, or any ener- gized (exposed or insulated) parts according to the Minimum Approach Distance (MAD) as shown in Table 1-1. - Allow for machine movement and electrical line swaying. Table 1-1. Minimum Approach Distances (M.A.D.) <table><tr><th>Voltage Range (Phase to Phase)</th><th>MINIMUM APPROACH DISTANCE in Feet (Meters)</th></tr><tr><td>Oto 50KV</td><td>10(3)</td></tr><tr><td>Over 50KV to 200 KV</td><td>15(5)</td></tr><tr><td>Over 200 KV to 350KV</td><td>20(6)</td></tr><tr><td>Over 350 KV to 500KV</td><td>25(8)</td></tr><tr><td>Over 500 KVto 750KV</td><td>35(11)</td></tr><tr><td>Over 750KV to 1000 KV</td><td>45(14)</td></tr><tr><td colspan="2">NOTE: This requirement shall apply except where employer, local or governmental regulations are more stringent.</td></tr></table> Maintain a clearance of at least 10 ft. (3m) between any part of the machine and its occupants, their tools, and their equip- ment from any electrical line or apparatus carrying up to 50,000 volts. One foot additional clearance is required for every additional 30,000 volts or less. 1-6 31219003

[9] JLG - Boom Lifts : 800AJ - Operation (PN 31215045)

Page 20

Open source document

Source excerpt

# SECTION 1 - SAFETY PRECAUTIONS - Maintain distance from electrical lines, apparatus, or any ener- gized (exposed or insulated) parts according to the Minimum Approach Distance (MAD) as shown in Table 1-1. - Allow for machine movement and electrical line swaying. Table 1-1. Minimum Approach Distances (M.A.D.) <table><tr><th>Voltage Range (Phase to Phase)</th><th>MINIMUM APPROACH DISTANCE in Feet (Meters)</th></tr><tr><td>Oto 50KV</td><td>10(3)</td></tr><tr><td>Over 50KV to 200 KV</td><td>15(5)</td></tr><tr><td>Over 200 KV to 350KV</td><td>20(6)</td></tr><tr><td>Over 350 KV to 500KV</td><td>25(8)</td></tr><tr><td>Over 500 KV to 750KV</td><td>35(11)</td></tr><tr><td>Over 750KV to 1000 KV</td><td>45(14)</td></tr><tr><td colspan="2">NOTE: This requirement shall apply except where employer, local or governmental regulations are more stringent.</td></tr></table> Maintain a clearance of at least 10 ft. (3m) between any part of the machine and its occupants, their tools, and their equip- ment from any electrical line or apparatus carrying up to 50,000 volts. One foot additional clearance is required for every additional 30,000 volts or less. 1-6 31215045

Related Q&A

Keep exploring.

Human questionGeneral

Hazards associated with opening an HSI crusher

Safe Work Procedure: Opening an HSI Crusher Document Number: [SWP-NUMBER] Revision Date: [DATE] Next Review Date: [NEXT REVIEW DATE] Department: [DEPARTMENT NAME] 1. Scope This Safe Work Procedure (SWP) outlines the necessary safety precautions and procedures to be followed when opening a Horizontal Shaft Impactor

Read the thread
Human questionGeneral

Welding inside barge hopper tank

Welding Inside Barge Hopper Tanks ================================= *Date:** 2025-09-13 *Duration:** \[DURATION] minutes *Presenter:** \[PRESENTER NAME] *Location:** \[LOCATION] Objective To understand and implement safety procedures for welding operations inside barge hopper tanks, focusing on ventilation, fire

Read the thread
Human questionGeneral

confined space in manholes with excessive temperatures

Confined Space Entry: Manholes with Excessive Heat ================================================== *Date:** 2025-08-22 *Duration:** \[DURATION] minutes *Presenter:** \[PRESENTER NAME] *Location:** \[LOCATION] Objective The objective of this toolbox talk is to ensure all personnel understand and can implement the

Read the thread
Human questionGeneral

Write a safe work procedure for Hot work operations

Hot Work Operations =================== Document Number: \[SWP-NUMBER] Revision Date: \[DATE] Next Review Date: \[NEXT REVIEW DATE] Department: \[DEPARTMENT NAME] 1\. Scope This safe work procedure applies to temporary hot work operations including welding, cutting, grinding, brazing, soldering, and related spark- or

Read the thread
Human questionGeneral

po tank confined space entry procedure

Toolbox Talk: Confined Space Entry Procedure for PO Tanks *Date:** [DATE] *Duration:** [DURATION] minutes *Presenter:** [PRESENTER NAME] *Location:** [LOCATION] Objective To ensure all personnel understand and follow the correct procedures for safe entry into PO tanks, recognizing hazards, implementing control

Read the thread
Discussion thread

Add your experience.

Community answers can add practical context. They are moderated, but they are not SALUS-reviewed safety guidance.

New contributions are temporarily closed while the moderation queue is configured.

Community answers(0)

No community answers have been approved yet.

Comments on Rosie's answer(0)

No comments have been approved yet.

Ready to put operational safety to work?

Join 400K users across 150K sites already on SALUS.

No commitment · 30-minute personalized walkthrough