For cofferdams and confined space entry in construction and excavation work, the safest approach is to treat any cofferdam, excavation, shaft, vault, manhole, tank, sewer, or similar enclosed area as a potential permit-required confined space until a hazard assessment shows otherwise. Key hazards include oxygen deficiency or enrichment, flammable or explosive atmospheres, toxic gases and vapors, engulfment by water, soil, sludge, or flowing materials, and physical hazards such as mechanical equipment, electrical energy, heat, noise, entrapment, and restricted egress. In cofferdams specifically, also evaluate flooding, seepage, instability, adjacent utility releases, vehicle exhaust, welding fumes, and changing atmospheric conditions caused by pumps, coatings, cutting, or hot work. [5] [15] [13]

Atmospheric testing must be completed before entry and repeated as needed during the job. Test from top to bottom because gases stratify, and monitor at least oxygen, combustibility/LFL, and expected toxic contaminants such as hydrogen sulfide or carbon monoxide. Testing should be performed by a trained, competent person using a direct-reading gas monitor that is calibrated and function-checked. Record the results, keep them at the job site, and make them available to affected workers. If conditions can change, if hot work is performed, or if the work itself may affect air quality, continuous monitoring is the preferred practice. [5] [4] [10]

Acceptable entry conditions for atmosphere should include oxygen between 19\.5% and 23\.5%, flammable gas below 10% of the lower explosive limit, and toxic contaminants below applicable exposure limits. If testing shows unsafe conditions, do not enter until hazards are eliminated or controlled under a permit system with appropriate respiratory protection and rescue capability. Workers must leave immediately if monitor alarms activate or conditions deteriorate. [1] [7] [8]

Ventilation is a control measure, not a substitute for hazard evaluation. Purge, drain, flush, or pump out water, sediment, sludge, or contaminants before entry where necessary. Use mechanical ventilation with 100% outside air where applicable, open additional access points when feasible to improve circulation, and retest after a suitable ventilation period. In cofferdams and excavations, ventilation should also address diesel exhaust, welding fumes, solvent vapors, and stagnant low-lying air. If ventilation alone cannot maintain safe conditions, entry should proceed only under permit-required procedures with additional controls such as supplied-air respiratory protection. [1] [2] [6]

A permit-required confined space program is required when the space has actual or potential atmospheric hazards, engulfment hazards, or other serious safety hazards. All spaces should be treated as permit-required until pre-entry procedures demonstrate otherwise. The permit should identify the space, purpose of entry, authorized entrants, attendant, supervisor, emergency contacts, hazards, isolation steps, atmospheric test results, PPE, communication method, rescue arrangements, and permit duration. A new permit or re-evaluation is needed if work is interrupted or conditions change. [2] [14] [2]

  • Isolate all hazardous energy before entry: lockout/tagout equipment, de-energize circuits, blank or cap lines, and isolate pumps, piping, sewers, and other sources that could introduce material or energy into the space.
  • Survey the surrounding area for drifting vapors, sewer gases, adjacent process releases, vehicle exhaust, water intrusion, and excavation-related hazards.
  • Provide at least one attendant outside the space whenever permit entry is required, maintain constant communication, and prevent unauthorized entry.
  • Use appropriate PPE based on the hazards: hard hat, gloves, eye protection, protective clothing, hearing protection, fall protection, respiratory protection, and intrinsically safe or explosion-proof lighting and tools where needed.
  • Post the permit at the entry point and secure the area around the opening or excavation.

[5] [8] [1] Rescue planning is critical because many confined-space fatalities occur during impulsive rescue attempts. At least one attendant should remain outside to summon help and monitor entrants. The attendant must not enter for rescue until additional help arrives and only if trained, equipped, and authorized. Non-entry rescue is preferred whenever feasible, using a full-body harness, lifeline, and mechanical retrieval device such as a tripod or block and tackle. Rescue personnel should be trained in first aid and CPR, and the rescue plan should be specific to the space, hazards, access limitations, and retrieval method. [1] [1] [9]

Worker training must cover confined-space hazard recognition, permit procedures, atmospheric testing, monitor use and alarm response, ventilation, isolation/lockout, communication, attendant duties, PPE, rescue procedures, and emergency response. Only trained and authorized employees should test, supervise, attend, or enter permit spaces. Training should be refreshed whenever duties change, equipment changes, or deficiencies are observed. For cofferdam and excavation work, training should also address water hazards, engulfment, fall hazards, access/egress, mobile equipment, and changing site conditions. [2] [3] [9]

For emergency response, establish a written plan before entry. The plan should identify who to call, how entrants and attendants communicate, how alarms are triggered, what rescue equipment is staged, whether rescue is non-entry or entry, and how EMS/fire rescue will access the site. Stop work and evacuate immediately if there is an alarm, loss of ventilation, flooding, engulfment risk, fire, collapse, medical emergency, or any unplanned change in conditions. In construction and excavation operations, coordinate the confined-space plan with excavation protection, dewatering, traffic control, utility control, and site emergency procedures. [14] [14] [3]

Relevant OSHA requirements include 29 CFR 1910\.146 for permit-required confined spaces in general industry, which is commonly used as the baseline for hazard evaluation, permits, testing, attendants, and rescue. For construction activities, employers should also apply OSHA's confined spaces in construction rule, along with excavation requirements in 29 CFR 1926 Subpart P and cofferdam requirements in 29 CFR 1926 Subpart S where applicable. In practice, cofferdams used in construction often involve both excavation and confined-space hazards, so employers should integrate both sets of controls rather than treating them separately. [5] [9] [9]

  • Classify the space before entry and assume permit-required status until proven otherwise.
  • Complete a site-specific hazard assessment for atmospheric, engulfment, electrical, mechanical, thermal, and access hazards.
  • Isolate energy and material sources; lock out, blank, block, drain, purge, and dewater as needed.
  • Test the atmosphere before entry, after ventilation, and continuously or periodically based on risk.
  • Ventilate with outside air and stop entry if safe conditions cannot be maintained.
  • Use an entry permit, attendant, communication system, and trained authorized entrants.
  • Stage rescue equipment before entry and prohibit unplanned entrant-to-entrant rescue.
  • Maintain safe access/egress, fall protection around openings, housekeeping, lighting, and traffic control.
  • For excavation and cofferdam work, inspect for water intrusion, soil movement, structural instability, and adjacent operations that could affect the space.
  • Suspend work during storms, flooding, pump failure, monitor alarms, or any change that invalidates the permit.

[2] [11] [12]

15 source record(s)

Sources used for this answer

[1] Confined Space - Atmospheric Testing

Page 1

Open source document

Source excerpt

CCOHS CCHST Canadian Centre for Occupational Health and Safety Centre canadien d'hygiène et de sécurité au travail Confined Space # Confined Space - Atmospheric Testing ## On this page What must the employer do when atmospheric testing is needed for a confined space? What are the atmosphere testing requirements for confined spaces? Where can I find more information? ## What must the employer do when atmospheric testing is needed for a confined space? The employer must make sure that a hazard assessment is performed before workers enter a confined space. Part of this assessment involves testing the atmosphere. Atmosphere testing is required before entry, during entry, and continuously throughout entry depending on the hazards and risks present. Atmospheric testing is typically required to determine the presence of: - Toxic gases - various chemical or biological substances - Flammable or explosive gases - Oxygen - too much (enrichment) or too little (deficiency) The employer must designate a qualified or competent person to perform the tests. These tests must be done using equipment that is appropriate and calibrated according to the manufacturer's instructions. The results of the tests must be recorded and retained. Be aware that atmospheric testing is only one component of a confined space entry_program that can help can keep workers safe when entering confined spaces. What are the atmosphere testing requirements for confined spaces? Confined Space - Atmospheric Testing CCOHS

[2] OSH Enforcement Procedures | CFR 184 - Confined Spaces in Construction

Page 149

Open source document

Source excerpt

# Federal Register / Vol. 80, No. 85/Monday, May 4, 2015/Rules and Regulations (cont.) ## Description of Accident: (cont.) Federal Register / Vol. 80, No. 85/Monday, May 4, 2015/Rules and Regulations [redacted postal code] Year Industry SIC Type of confined space Number of reported fatalities Activity No. 10 Employee #1 entered a sewer lift station to check for leaks in the line. Employee #1 was overcome by hydrogen sulfide gas. A second em- ployee entered the station to retrieve Employee #1, and also was overcome by the gas. Both employees died from overexposure to hydrogen sulfide gas. Provisions That Could Potentially Have Prevented the Fatality: Evaluation and Classification Information Exchange Permit Program Ventilation and Hazard Isolation Early Warning System and Atmospheric Testing or Monitoring Provisions Rescue Capacity (Attempted rescue resulted in a fatality) Training <table><tr><th>Year</th><th>Industry SIC</th><th>Type of confined space</th><th>Number of reported fatalities</th><th>Activity No. 11</th></tr><tr><td>2009</td><td>1623</td><td>manhole</td><td>1</td><td>[redacted identifier]</td></tr></table> ## Description of Accident: Employee #3 fell into a manhole and suffered a head injury and was life-flighted to the hospital. Employee #2 became unconscious in a man- hole and was rescued and life-flighted to the hospital. Employee #1 entered the manhole to attempt rescue of employee #2 and became uncon- scious and died before he could be rescued. ## Provisions That Could Potentially Have Prevented the Fatality: Evaluation and Classification Ventilation and Hazard Isolation Early Warning System and Atmospheric Testing or Monitoring Provisions Rescue Capacity (Attempted rescue resulted in a fatality) Training <table><tr><th>Year</th><th>Industry SIC</th><th>Type of confined space</th><th>Number of reported fatalities</th><th>Activity No. 12</th></tr><tr><td>2009</td><td>1791</td><td>tank</td><td>1</td><td>[redacted identifier]</td><…

[3] The Oregon OSHA Confined Space Rule Applicable to General Industry and Construction - Workbook

Page 79

Open source document

Source excerpt

# SAMPLE CONFINED SPACE ENTRY PERMIT (cont.) ## Pre-entry requirements (cont.) Purge or flush or drain: [ ] Yes [ ] No Ventilation (natural or mechanical): [ ] Yes [ ] No Secure area: [ ] Yes [ ] No Safe lighting: [ ] Yes [ ] No Non-sparking tools: [ ] Yes [ ] No Communication method: [ ] Yes [ ] No Contractor employees involved: [ ] Yes [ ] No Continuous air monitoring used: [ ] Yes [ ] No Personal protective equipment: [ ] Hardhat [ ] Gloves [ ] Safety glasses [ ] Respirator, type: <empty> [ ] Other PPE: <empty> [ ] Other PPE: <empty> Periodic air monitoring used: [ ] Yes [ ] No <table><tr><th colspan="2">Space-monitoring results</th><th>Test 1</th><th>Test 2</th><th>Test 3</th><th>Test 4</th></tr><tr><td>Substance monitored</td><td>Permissible entry levels</td><td>Time: Initial:</td><td>Time: Initial:</td><td>Time: Initial:</td><td>Time: Initial:</td></tr><tr><td>Percent oxygen</td><td>19.5% to 23.5%</td><td></td><td></td><td></td><td></td></tr><tr><td>Combustible gas</td><td>Less than 10% LEL</td><td></td><td></td><td></td><td></td></tr><tr><td>Other toxic gas</td><td></td><td></td><td></td><td></td><td></td></tr><tr><td>Other toxic gas</td><td></td><td></td><td></td><td></td><td></td></tr><tr><td>Other toxic gas</td><td></td><td></td><td></td><td></td><td></td></tr></table> ## Names of trained, authorized individuals Entry supervisor: ■ Entry attendant: Authorized entrants: ■ Authorized entrants: ## Emergency contact information Emergency responder: Contact person: Time: Phone number: This permit has been terminated for the following reason: Work completed Canceled Time: Note: Supervisor's signature Time: Date: Return this completed permit to Review, then file for one year.

[4] Confined Space - Program

Page 3

Open source document

Source excerpt

# Confined Space - Program (cont.) ## What is an Entry Permit System? (cont.) - The scope of the work that is to be done in the confined space. - Possible hazards that may be encountered inside and outside the space. - Possible hazards that may develop during the work activity. - The date and time of entry into the confined space and the anticipated time of exit. - The details of any atmospheric testing done of the confined space - when, where, results, and date monitoring equipment was last calibrated. Ideally, calibration (including bump test) would be done just before each use. If this is not possible, follow the equipment manufacturer's guidelines for the frequency of calibration. - Hazard control measures, including the use of mechanical ventilation, work procedures, personal protective equipment needed and any other precautions that must be followed by every worker who is going to enter the confined space. - Means of communication between the persons working in the confined space and the attendant. - Emergency plan, and the protective equipment and emergency equipment to be used by any person who takes part in a rescue or responds to other emergency situations in the confined space - A signature of a worker who did the confined space air testing. The signature on the permit would indicate that adequate precautions are being taken to control the anticipated hazards. - Authorization signature by the supervisor certifying that the space has been properly evaluated, prepared, and it is safe for entry and work. The entry permit should be posted at the confined space and remain so until the work is completed. The employer should keep a copy of the completed permit on file. ## What should happen when work is being done in a confined space? Use warning signs to prevent unauthorized entry to the confined space. Anyone working in a confined space must be constantly alert for any changing conditions within the confined space. In the event of an alarm fr…

[5] Confined Space Guide for General Industry

Page 59

Open source document

Source excerpt

# ATTACHMENT C # Confined Space Entry Permit Sample (Enhanced Title 8 Version) Permit valid for 8 hours only. All copies of permit will remain at job site until job is completed. Date: Time: Site location and description: Purpose of entry: NATURE OF CONFINED SPACE HAZARD Oxygen deficiency (less than 19.5%) Flammable gases/vapors above 10% of lower explosive limit (LEL) Mechanical hazards Oxygen over 23.5% Toxic gases or vapors greater than permissible exposure limit (PEL) Electrical shock Materials harmful to skin Electrical lockout Engulfment Valve out/isolation Other(s) BOLD DENOTES MINIMUM REQUIREMENTS TO BE COMPLETED AND REVIEWED PRIOR TO ENTRY PREPARATION COMPLETED DATE TIME Lock out/de-energize/try-out Line(s) broken/capped/blanked Secure area (post and flag) Breathing apparatus Resuscitator/inhalator Cleaned, drained, washed, & purged Ventilation for fresh air Emergency response team available Employees informed of specific hazards Procedures reviewed with each employee_ Atmospheric test in compliance Hot work permit attached (if required) Continuous monitoring required Other(s) REQUIREMENTS COMPLETED DATE TIME Full body harness w/ "D" ring Emergency escape retrieval equip. Lifelines Lighting (explosion-proof) Protective clothing (PPE) Respiratory equipment Specify Communication equipment Specify Rescue equipment Specify Rescue Service Phone# <table><tr><th>CONTINUOUS MONITORING</th><th>PERMISSIBLE</th><th>RECORD MONITORING RESULTS/TIME</th></tr><tr><td>TEST(S) TO BE TAKEN</td><td>ENTRY LEVEL</td><td></td></tr><tr><td>Percent of Oxygen</td><td>19.5% to 23.5%</td><td></td></tr><tr><td>Lower flammable limit</td><td>Under 10%</td><td></td></tr><tr><td>Carbon Monoxide</td><td>25 ppm</td><td></td></tr><tr><td>Aromatic Hydrocarbon</td><td>1 ppm - 5 ppm</td><td></td></tr><tr><td>Hydrogen Cyanide</td><td>4.7 ppm (S)</td><td></td></tr><tr><td>Hydrogen Sulphide</td><td>10 ppm* 15 ppm**</td><td></td></tr><tr><td>Sulphur Dioxide</td><td>2 ppm* 5 ppm**</td>…

[6] Confined Space Entry

Page 1

Open source document

Source excerpt

WORK SAFE KENTUCKY Free safety resources provided by KEMI HOME SAFETY RESOURCES SAFETY TRAINING SAFETY BLOG ABOUT KEMI CONTACT US O # Confined Space Entry ## Print a Sign-In Sheet | Spanish Version Coming Soon ## What is a Confined Space? The Occupational Safety and Health Administration (OSHA) permit- required confined space standard defines a confined space as a space that is large enough for an employee to enter, has restricted means of entry or exit, and is not designed for continuous employee occupancy. A permit-required confined space (permit space) is a confined space that presents or has the potential for hazards related to atmospheric conditions (toxic, flammable, asphyxiating), engulfment, conflagration, or any other recognized serious hazard. Regulations governing entry into confined spaces are specified by OSHA. You can find these regulations at 29 CFR 1910.146. Examples of confined spaces include ship compartments, missile fuel tanks, vats, silos, sewers, tunnels, and vaults. ## Hazards Confined Space Hazards Dangerous vapors and gases can accumulate in confined spaces. Fires, explosions, and physical hazards can also injure or kill an unprotected worker. Physical Hazards Physical hazards may result from mechanical equipment or moving parts, like agitators, blenders, and stirrers. Other physical hazards include heat and sound. Temperatures can build up quickly in a permit space and cause exhaustion or dizziness. Sounds may reverberate and make it hard to hear important directions or warnings. ## Oxygen Deficiency The primary hazard associated with confined spaces is oxygen deficiency. Oxygen may be reduced in a space either by displacement or consumption. Oxygen is displaced by other gases such as argon, nitrogen, r methane. Consumption may be caused by chemical reactions such as rusting, rotting, fermentation, or burning of flammable substances. ## Combustibility Fire and explosion are serious dangers in permit spaces because fumes and…

[7] The Oregon OSHA Confined Space Rule Applicable to General Industry and Construction - Workbook

Page 93

Open source document

Source excerpt

# Entry permit Permit date: 1/21/14 Work shift: 1st [x] 2nd [ ] 3rd [ ] Expires: 1/21/14 Time started: 7:00 am Permit space to be entered (name and location of space): Water Tank #1 Purpose of entry: Remove rust inside tank, paint inside with epoxy paint ## Names of trained, authorized individuals " Entry supervisor: Nick Fellows ■ Entry attendant: Margaret Carter " Authorized entrants: Jim Buchanan - Authorized entrants: Jay Kirby ## Emergency contact information Emergency responder: In-house Contact person: Steve Rogers Phone number: Time: ## Pre-entry requirements <table><tr><th>Requirements</th><th>Yes</th><th>No</th><th>N/A</th><th>Requirements</th><th>Yes</th><th>No</th><th>N/A</th></tr><tr><td>Lockout tagout/de-energize</td><td></td><td></td><td></td><td>Hot work permit</td><td></td><td></td><td></td></tr><tr><td>Pipes(s) broken or capped or blanked</td><td></td><td></td><td></td><td>Fall arrest harness/lifeline/tripod</td><td></td><td></td><td></td></tr><tr><td>Purge or flush or drain</td><td></td><td></td><td></td><td>Personal protective equipment</td><td></td><td></td><td></td></tr><tr><td>Ventilation (natural or mechanical)</td><td></td><td></td><td></td><td>Hardhat</td><td></td><td></td><td></td></tr><tr><td>Secure area</td><td></td><td></td><td></td><td>Gloves</td><td></td><td></td><td></td></tr><tr><td>Safe lighting</td><td>□□□</td><td></td><td></td><td>Safety glasses</td><td></td><td></td><td></td></tr><tr><td>Non-sparking tools</td><td></td><td></td><td></td><td>Respirator, type</td><td></td><td></td><td></td></tr><tr><td>Communication method</td><td>□□□</td><td></td><td></td><td>Other PPE:</td><td></td><td></td><td></td></tr><tr><td>Contractor employees involved</td><td></td><td></td><td></td><td>Other PPE:</td><td></td><td></td><td></td></tr></table> <table><tr><th colspan="2">Space-monitoring results</th><th>Test 1</th><th>Test 2</th><th>Test 3</th><th>Test 4</th></tr><tr><td>Monitor at least every four hours</td><td>Permissible…

[8] Occupational Safety and Health Standards (OSHA 29 CFR 1910) - 1910.146 App C - Examples of Permit-required Confined Space Programs

Page 2

Open source document

Source excerpt

# Occupational Safety and Health Administration (cont.) ## Appendix C to § 1910.146- - Examples of Permit-required Confined Space Programs (cont.) copy of operating and rescue procedures as required by these procedures shall be at the work site for the duration of the job. The Confined Space Pre-Entry Check List must be completed by the LEAD WORKER before entry into a confined space. This list verifies completion of items listed below. This check list shall be kept at the job site for duration of the job. If circumstances dictate an interruption in the work, the permit space must be re-evaluated and a new check list must be completed. Control of atmospheric and engulfment hazards. Pumps and Lines. All pumps and lines which may reasonably cause contaminants to flow into the space shall be disconnected, blinded and locked out, or effectively isolated by other means to prevent development of dangerous air contamination or engulfment. Not all laterals to sewers or storm drains require blocking. However, where experience or knowledge of industrial use indicates there is a reasonable potential for contamination of air or engulfment into an occupied sewer, then all affected laterals shall be blocked. If blocking and/or isolation requires entry into the space the provisions for entry into a permit- required confined space must be implemented. Surveillance. The surrounding area shall be surveyed to avoid hazards such as drifting vapors from the tanks, piping, or sewers. Testing. The atmosphere within the space will be tested to determine whether dangerous air contamination and/or oxygen deficiency exists. Detector tubes, alarm only gas monitors and explosion meters are examples of monitoring equipment that may be used to test permit space atmospheres. Testing shall be performed by the LEAD WORKER who has successfully completed the Gas Detector training for the monitor he will use. The minimum parameters to be monitored are oxygen deficiency, LFL, and hydrogen sulfide co…

[9] Confined Space Entry Permit

Page 2

Open source document

Source excerpt

# Entry permit (continued) <table><tr><th>Possible atmospheric hazards</th><th>Yes</th><th>No</th><th>N/A</th></tr><tr><td>Lack of oxygen</td><td></td><td></td><td></td></tr><tr><td>Combustible gases</td><td></td><td></td><td></td></tr><tr><td>Combustible vapors</td><td></td><td></td><td></td></tr><tr><td>Combustible dusts</td><td></td><td></td><td></td></tr><tr><td>Toxic gases/vapors</td><td></td><td></td><td></td></tr><tr><td>Possible non-atmospheric hazards</td><td>Yes</td><td>No</td><td>N/A</td></tr><tr><td>Noise</td><td></td><td></td><td></td></tr><tr><td>Chemical contact</td><td></td><td></td><td></td></tr><tr><td>Electrical hazard</td><td></td><td></td><td></td></tr><tr><td>Mechanical exposure</td><td></td><td></td><td></td></tr><tr><td>Temperature extreme</td><td></td><td>୮</td><td></td></tr><tr><td>Engulfment</td><td></td><td></td><td></td></tr><tr><td>Entrapment</td><td></td><td></td><td></td></tr><tr><td>Other non-atmospheric hazard</td><td></td><td></td><td></td></tr></table> <table><tr><th colspan="2">Space-monitoring results</th><th>Test 1</th><th>Test 2</th><th>Test 3</th><th>Test 4</th></tr><tr><td rowspan="2">Monitor at least every four hours</td><td rowspan="2">Permissible entry levels</td><td>Time:</td><td>Time:</td><td>Time:</td><td>Time:</td></tr><tr><td>Initial:</td><td>Initial:</td><td>Initial:</td><td>Initial:</td></tr><tr><td>Percent oxygen</td><td>19.5% to 23.5%</td><td></td><td></td><td></td><td></td></tr><tr><td>Combustible gas</td><td>Less than 10% LEL</td><td></td><td></td><td></td><td></td></tr><tr><td>Other toxic gas</td><td></td><td></td><td></td><td></td><td></td></tr><tr><td>Other toxic gas</td><td></td><td></td><td></td><td></td><td></td></tr><tr><td>Other toxic gas</td><td></td><td></td><td></td><td></td><td></td></tr></table> This permit has been terminated for the following reason: Work completed Canceled Time: Note: Supervisor's signature Time: Date: Return this completed permit to Review, then file for one year…

[10] Occupational Safety and Health Standards (OSHA 29 CFR 1910) - 1910.146 App C - Examples of Permit-required Confined Space Programs

Page 3

Open source document

Source excerpt

# Occupational Safety and Health Administration (cont.) ## B. Entry Permit Required - Permits. Confined Space Entry Permit. All spaces shall be considered permit-required confined spaces until the pre-entry procedures demonstrate otherwise. Any employee required or permitted to pre-check or enter a permit-required confined space shall have successfully completed, as a minimum, the training as required by the following sections of these procedures. A written copy of operating and rescue procedures as required by these procedures shall be at the work site for the duration of the job. The Confined Space Entry Permit must be completed before approval can be given to enter a permit-required confined space. This permit verifies completion of items listed below. This permit shall be kept at the job site for the duration of the job. If circumstances cause an interruption in the work or a change in the alarm conditions for which entry was approved, a new Confined Space Entry Permit must be completed. - Control of atmospheric and engulfment hazards. - Surveillance. The surrounding area shall be surveyed to avoid hazards such as drifting vapors from tanks, piping or sewers. - Testing. The confined space atmosphere shall be tested to determine whether dangerous air contamination and/or oxygen deficiency exists. A direct reading gas monitor shall be used. Testing shall be performed by the SUPERVISOR who has successfully completed the gas detector training for the monitor he will use. The minimum parameters to be monitored are oxygen deficiency, LFL and hydrogen sulfide concentration. A written record of the pre- entry test results shall be made and kept at the work site for the duration of the job. Affected employees shall be able to review the testing results. The most hazardous conditions shall govern when work is being performed in two adjoining, connected spaces. - Space Ventilation. Mechanical ventilation systems, where applicable, shall be set at 100% outside air. Wh…

[11] Cal/OSHA Regulations | Chapter 4 | Subchapter 7: General Industry Safety Orders | §5157. Permit-Required Confined Spaces, Appendix C - Examples of Permit-required Confined Space Programs

Page 1

Open source document

Source excerpt

This information is provided free of charge by the Department of Industrial Relations from its web site at www.dir.ca.gov. These regulations are for the convenience of the user and no representation or warranty is made that the information is current or accurate. See full disclaimer at https://www.dir.ca.gov/od_pub/disclaimer.html. Subchapter 7. General Industry Safety Orders Group 16. Control of Hazardous Substances Article 108. Confined Spaces Return to index New query # §5157. Permit-Required Confined Spaces, Appendix C - Examples of Permit-required Confined Space Programs. Example 1. Workplace. Sewer entry. Potential hazards. The employees could be exposed to the following: Engulfment. Presence of toxic gases. Equal to or more than 10 ppm hydrogen sulfide as measured as an 8-hour time weighted average. If the presence of other toxic contaminants is suspected, specific monitoring programs will be developed. Presence of explosive flammable gases. Equal to or greater than 10% of the lower flammable limit (LFL). Oxygen Deficiency. A concentration of oxygen in the atmosphere equal to or less than 19.5% by volume. ## A. ENTRY WITHOUT PERMIT/ATTENDANT Certification. Confined spaces may be entered without the need for a written permit or attendant provided that the space can be maintained in a safe condition for entry by mechanical ventilation alone as provided in Section 5157(c)(5). All spaces shall be considered permit-required confined spaces until the pre-entry procedures demonstrate otherwise. Any employee required or permitted to pre-check or enter an enclosed/confined space shall have successfully completed, as a minimum, the training as required by the following sections of these procedures. A written copy of operating and rescue procedures as required by these procedures shall be at the work site for the duration of the job. The Confined Space Pre-Entry Check List must be completed by the LEAD WORKER before entry into a confined space. This list ver…

[12] Confined Space Entry

Page 2

Open source document

Source excerpt

# Confined Space Entry (cont.) ## Safety Blog (cont.) After you are sure that the oxygen level is adequate and there is nothing combustible in the space, test for toxicity. Notify your supervisor if pretests find hazards that you cannot adequately protect against. Follow-up testing may be periodic or continuous, depending on specific conditions. Because the work being done within a permit space may also change air quality, continuous testing may be needed to ensure worker safety. ## Purge and Ventilate the Space Some confined spaces may contain water, sediment, hazardous atmosphere, or other unwanted substances. These substances generally must be purged, that is, pumped out or otherwise removed, before entry. Use ventilating equipment where possible. Ventilation should maintain an oxygen level between 19.5 percent and 23.5 percent and keep toxic gases and vapors within accepted levels prescribed by OSHA. Where the entrance is large enough, portable self-contained breathing devices should be used unless the atmosphere is ventilated or has been determined to have no potential atmospheric hazards. If the entrance to a potentially hazardous atmosphere is too small, an air line mask should be used with supplied air. If there is any danger of disconnecting the air line, a 5 to 15-minute escape respirator containing breathing air should be carried. You might also need eye and hearing protection and protective clothing. ## Rescue Procedures At least one person should remain outside to summon help or offer assistance. If the employer designates this attendant to perform rescue procedures in addition to monitoring the safety of the confined space entrant, he or she should be equipped with the necessary PPE and rescue equipment and trained in first aid and cardiopulmonary resuscitation (CPR). He or she should maintain constant communication with those inside the space either visually, by radio, or by field telephone. If a situation arises that requires emergency entry,…

[13] The Oregon OSHA Confined Space Rule Applicable to General Industry and Construction - Workbook

Page 52

Open source document

Source excerpt

# DIVISION 2, GENERAL INDUSTRY (cont.) ## [redacted phone] Confined Spaces (cont.) Potential hazards - All reasonably anticipated conditions within the space and outside the space that can adversely affect conditions within the space. Rescue - Retrieving employees who are unable to remove themselves from a permit space. Rescue can be entry or non-entry, and can be conducted by the employer's employees or a third-party. Rescue service - The onsite or offsite personnel who the employer designates to engage in non-entry and/or entry rescue of employees from a permit space. Retrieval system – The equipment, including mechanical retrieval devices, used for non-entry rescue of authorized entrants from a permit space. Serious physical harm – An impairment in which a body part is made functionally useless or is substantially reduced in efficiency. Such impairment may include loss of consciousness or disorientation, and may be permanent or temporary, or chronic or acute. Injuries involving such impairment would usually require treatment by a physician or other licensed health-care professional while an illness resulting in serious physical harm could shorten life or substantially reduce physical or mental efficiency by impairing a normal bodily function or body part. Simulated Permit-Required Confined Space - Is a confined space or a mock-up of a confined space that has similar entrance openings, and is similar in size, configuration, and accessibility to the permit space the authorized entrants enter. A simulated space does not need to contain any physical or atmospheric hazards. Testing - The process of identifying and evaluating the atmospheric hazards that entrants may be exposed to in a permit-required confined space. Testing includes specifying the initial tests that are to be performed in the permit space. (See also “monitor or monitoring") Note: Testing enables employers both to devise and implement adequate control measures for the protection of authorized …

[14] Confined Space Entry Permit

Page 1

Open source document

Source excerpt

# Confined space entry permit Permit date: <empty> Work shift: [ ] 1st [ ] 2nd [ ] 3rd Expires: <empty> Time started: <empty> Permit space to be entered (name and location of space): <empty> Purpose of entry: <empty> ## Names of trained, authorized individuals Emergency contact information Entry supervisor: Emergency responder: Entry attendant: Contact person: Authorized entrants: Phone number: Authorized entrants: Time: ## Pre-entry checklist Do not enter this permit space until the following "needs action" conditions are corrected: <table><tr><th>OK</th><th>Needs action</th><th></th></tr><tr><td></td><td></td><td>Before entering the permit space, the supervisor or designee must notify the rescue team. IDLH conditions require at least one rescue team member located outside the space.</td></tr><tr><td></td><td></td><td>A minimum of two employees must be assigned to work involving permit space entry. One employee must remain outside the permit space at all times</td></tr><tr><td></td><td></td><td>The surrounding area must be surveyed to show that it is free of hazards such as drifting vapors from tanks, piping, sewers, or vehicle exhaust.</td></tr><tr><td></td><td></td><td>Those responsible for operation of the gas monitor have been trained.</td></tr><tr><td></td><td></td><td>Gas monitor calibration tests and functional test (fresh air calibration) have been performed this shift on the gas monitor. If so, by whom?</td></tr><tr><td></td><td></td><td>The atmosphere will be continuously monitored while the space is occupied, if required by entry procedure.</td></tr></table> <table><tr><th colspan="8">Pre-entry requirements</th></tr><tr><td>Requirements</td><td>Yes</td><td>No</td><td>N/A</td><td>Requirements</td><td>Yes</td><td>No</td><td>N/A</td></tr><tr><td>Lockout-tagout/de-energize</td><td></td><td></td><td></td><td>Hot work permit</td><td></td><td></td><td></td></tr><tr><td>Pipes(s) broken or capped or blanked</td><td></td><td></td><td></td><td>Fall …

[15] Cal/OSHA Regulations | Chapter 4 | Subchapter 7: General Industry Safety Orders | §5157. Permit-Required Confined Spaces, Appendix C - Examples of Permit-required Confined Space Programs

Page 2

Open source document

Source excerpt

# §5157. Permit-Required Confined Spaces, Appendix C - Examples of Permit-required Confined Space Programs. (cont.) ## A. ENTRY WITHOUT PERMIT/ATTENDANT (cont.) dangerous air contamination or engulfment. Not all laterals to sewers or storm drains require blocking. However, where experience or knowledge of industrial use indicates there is a reasonable potential for contamination of air or engulfment into a occupied sewer, then all affected laterals shall be blocked. If blocking and/or isolation requires entry into the space the provisions for entry into a permit-required confined space must be implemented. Surveillance. The surrounding area shall be surveyed to avoid hazards such as drifting vapors from the tanks, piping, or sewers. Testing. The atmosphere within the space will be tested to determine whether dangerous air contamination and/or oxygen deficiency exists. Detector tubes, alarm only type gas monitors and explosion meters are examples of equipment that may be used to test permit space atmospheres. Testing shall be performed by the LEAD WORKER who has successfully completed the Gas detector training for the monitors he will use. The minimum parameters to be monitored are oxygen deficiency, LFL, and hydrogen sulfide concentration. A written record of the pre-entry test results shall be made and kept at the work site for the duration of the job. The supervisor will certify in writing, based upon the results of the pre-entry testing, that all hazards have been eliminated. Affected employees shall be able to review the testing results. The most hazardous conditions shall govern when work is being performed in two adjoining, connecting spaces. Entry Procedures. If there are no non-atmospheric hazards present and if the pre-entry tests show there is no dangerous air contamination and/or oxygen deficiency within the space and there is no reason to believe that any is likely to develop, entry into and work within may proceed. Continuous testing of the atmosph…

Related Q&A

Keep exploring.

Human questionUS

What should a HSE Manager inspect when visiting a customers site?

Here's a checklist for HSE Managers when visiting a customer site, incorporating elements from OSHA standards relevant to Texas [1]: *HSE Manager Customer Site Inspection Checklist** *Purpose:** To ensure compliance with safety regulations and promote a safe working environment at customer sites. *Instructions:**

Read the thread
Human questionGeneral

rail construction

Rail Construction and Maintenance Safety ======================================== Document Number: \[SWP-NUMBER] Revision Date: \[DATE] Next Review Date: \[NEXT REVIEW DATE] Department: \[DEPARTMENT NAME] 1\. Scope This safe work procedure (SWP) outlines the safety requirements for all rail construction and maintenance

Read the thread
Human questionGeneral

Give me a audit for a construction site

Safety Audit Checklist for Construction Site Hazard Identification and Risk Assessment ====================================================================================== This checklist provides a framework for conducting safety audits on construction sites, focusing on hazard identification and risk assessment. It

Read the thread
Discussion thread

Add your experience.

Community answers can add practical context. They are moderated, but they are not reviewed by Francis Langlois or presented as SALUS safety guidance.

New contributions are closed. Previously approved contributions remain visible.

Community answers(0)

No community answers have been approved yet.

Comments on Rosie's answer(0)

No comments have been approved yet.

Ready to put operational safety to work?

Join 400K users across 150K sites already on SALUS.

No commitment · 30-minute personalized walkthrough