Duct Jack Annual Inspection Checklist =====================================

Date: 2026-01-27

Inspector: \[INSPECTOR NAME]

Location/Area: \[LOCATION/AREA]

Department: \[DEPARTMENT]

Purpose


To ensure duct jacks are in safe operating condition and comply with OSHA 29 CFR 1926 standards. This inspection should be conducted annually by a qualified person.

Instructions for Use


  1. 1\. Visually inspect the duct jack for any signs of damage or wear.
  2. 2\. Perform functional testing to ensure the jack operates correctly and safely.
  3. 3\. Check the hydraulic system (if applicable) for leaks and proper operation.
  4. 4\. Check the screw mechanism (if applicable) for damage and proper operation.
  5. 5\. Record the inspection findings and any corrective actions taken.
  6. 6\. Ensure that the inspection is performed by a qualified person.
  7. 7\. Maintain inspection records for a minimum of 12 months. \[1926\.1412(f)(7\)]

Frequency


This checklist should be completed: Annually

Safety Checklist


General Requirements

These requirements apply to all duct jacks regardless of type or application.

ItemPassFailComments
Rated Capacity Check: The manufacturer's rated capacity is legibly marked on the jack and is not exceeded. \[1926\.305(a)(1\)] If failed: Remove the jack from service if the rated capacity is illegible or if the jack is being used beyond its capacity. Ensure the jack is appropriately labeled or replaced._________________
Positive Stop Check: The jack has a positive stop to prevent overtravel. \[29 CFR 1926\.305(a)(2\)] If failed: Remove the jack from service and repair or replace the stop mechanism._________________
Lubrication Check: The jack is properly lubricated at regular intervals. \[29 CFR 1926\.305(d)(1\)(iii)] If failed: Lubricate the jack according to the manufacturer's recommendations. Establish a lubrication schedule._________________
Inspection Frequency Check: The jack is thoroughly inspected at times which depend upon the service conditions. Inspections are not less frequent than once every 6 months for constant or intermittent use at one locality. \[29 CFR 1926\.305(d)(1\)(iv)(a)] If failed: Adjust the inspection schedule to meet the requirements based on usage.. Document all inspections._________________
Post-lifting security Check: After the load has been raised, it is cribbed, blocked, or otherwise secured at once. \[1926\.305(d)(1\)(i)] If failed: Provide cribbing and blocking materials. Train employees on proper blocking procedures._________________
Freezing Temperatures Check: Hydraulic jacks exposed to freezing temperatures are supplied with an adequate antifreeze liquid. \[1926\.305(d)(1\)(ii)] If failed: Add appropriate antifreeze liquid. Check the antifreeze protection level._________________
Repair Parts Check: Repair or replacement parts are examined for possible defects. \[1926\.305(d)(1\)(v)] If failed: Reject any defective parts. Use only approved replacement parts._________________
Jacks Out of Order Check: Jacks which are out of order are tagged accordingly and not used until repairs are made. \[1926\.305(d)(1\)(vi)] If failed: Tag out the jack and remove it from service until repaired. Ensure repairs are performed by qualified personnel._________________

Visual Inspection

Inspect the jack for any signs of physical damage or wear.

ItemPassFailComments
Cracks Check: No cracks are present in the jack body, base, or lifting mechanism. If failed: Remove the jack from service and repair or replace it._________________
Deformation Check: No deformation is present in the jack body, base, or lifting mechanism. If failed: Remove the jack from service and repair or replace it._________________
Corrosion Check: No excessive corrosion is present on the jack. If failed: Clean and lubricate the jack. If corrosion is severe, remove the jack from service and replace it._________________
Welds Check: All welds are intact and show no signs of cracking or failure. If failed: Remove the jack from service and repair or replace it._________________
Steps, ladders, handrails, guards Check: Originally equipped steps, ladders, handrails, guards are present and in usable/safe condition. \[1926\.1412(f)(2\)(xx)] \[1926\.1412(f)(2\)(xxi)] If failed: Repair or replace any missing or damaged steps, ladders, handrails or guards._________________

Functional Testing

Test the jack to ensure it operates correctly and safely.

ItemPassFailComments
Lifting Check: The jack lifts the rated load smoothly and without excessive effort. If failed: Check the hydraulic fluid level or the screw mechanism for damage. Repair or replace as necessary._________________
Holding Check: The jack holds the load without leaking down or slipping. If failed: Check the seals and valves for leaks. Repair or replace as necessary._________________
Lowering Check: The jack lowers the load smoothly and in a controlled manner. If failed: Check the release valve for proper operation. Repair or replace as necessary._________________
Positive Stop Check: The positive stop prevents overtravel during lifting. If failed: Adjust or repair the positive stop mechanism._________________
Functional Testing Check: Functional testing is conducted to determine that the equipment as configured in the inspection is functioning properly. \[1926\.1412(f)(3\)] If failed: Repair or replace any components that are not functioning properly._________________

Hydraulic System (if applicable)

Inspect the hydraulic system for leaks and proper operation.

ItemPassFailComments
Leaks Check: No hydraulic fluid leaks are present in the cylinder, hoses, or fittings. If failed: Tighten fittings or replace damaged hoses or seals._________________
Fluid Level Check: The hydraulic fluid level is within the recommended range. If failed: Add hydraulic fluid as needed._________________
Cylinder Condition Check: The cylinder is free from damage, such as dents or scoring. If failed: Repair or replace the cylinder._________________
Hoses and Fittings Check: Hoses and fittings are in good condition and properly secured. If failed: Replace damaged or worn hoses and fittings. Ensure proper securement._________________

Screw Mechanism (if applicable)

Inspect the screw mechanism for damage and proper operation.

ItemPassFailComments
Thread Condition Check: The threads are clean and free from damage. If failed: Clean and lubricate the threads. Repair or replace if damaged._________________
Screw Movement Check: The screw moves smoothly without binding or excessive play. If failed: Clean and lubricate the screw mechanism. Repair or replace if binding or excessive play is present._________________
Lubrication Check: The screw mechanism is properly lubricated. If failed: Lubricate the screw mechanism according to the manufacturer's recommendations._________________

General Requirements


ItemPassFailComments
Qualified Inspector Check: Inspection performed by a qualified person who is capable of identifying existing and predictable hazards. \[1926\.1412(f)(1\)] If failed: Ensure the inspector has the necessary training and experience._________________
Removal from Service Check: Where a wire rope is required to be removed from service under this section, either the equipment (as a whole) or the hoist with that wire rope must be tagged-out, in accordance with $ 1926\.1417(f)(1\), until the wire rope is repaired or replaced. \[1926\.1413(a)(4\)(iii)(B)] If failed: Tag out the equipment and remove it from service until the wire rope is repaired or replaced._________________

Failed Item Procedures


  1. If any deficiency is identified, an immediate determination must be made by the qualified person as to whether the deficiency constitutes a safety hazard or, though not yet a safety hazard, needs to be monitored in the monthly inspections. \[1926\.1412(f)(4\)]
  2. If the qualified person determines that a deficiency is a safety hazard, the equipment must be taken out of service until it has been corrected. \[1926\.1412(f)(5\)]
  3. If the qualified person determines that, though not presently a safety hazard, the deficiency needs to be monitored, the employer must ensure that the deficiency is checked in the monthly inspections. \[1926\.1412(f)(6\)]

Documentation Requirements


The following information must be documented and maintained for a minimum of 12 months: \[1926\.1412(f)(7\)]

  • The items checked and the results of the inspection. \[1926\.1412(f)(7\)(i)]
  • The name and signature of the person who conducted the inspection and the date. \[1926\.1412(f)(7\)(ii)]

Checklist Completion


Overall Status: ☐ Pass     ☐ Fail     ☐ Corrective Actions Required

Inspector Signature: Date:

Supervisor Review: Date:

Corrective Actions Completed By: Date:

References and Standards


  • OSHA 29 CFR 1926 Subpart I - Tools - Hand and Power \[1926\.305]
  • OSHA 29 CFR 1926\.1412 - Inspections
  • OSHA 29 CFR 1926\.1413 - Wire rope--inspection

This checklist must be retained for \[RETENTION PERIOD].

Safety powered by SALUS

This answer was preserved from its published ai.salussafety.io page. The legacy export contains no separate citation records for this answer, so SALUS has not invented any.

Related Q&A

Keep exploring.

Human questionGeneral

PPE for Hex chrome in a confined space

Personal Protective Equipment (PPE) for Handling Hexavalent Chromium in Confined Spaces ======================================================================================= Hexavalent chromium (Cr6\+) exposure in confined spaces poses significant health risks, including respiratory irritation, skin sensitization

Read the thread
Human questionGeneral

What’s the safest way to work around 480 V electrical panel boxers?

Safe Work Practices and Procedures for 480V Electrical Panels ============================================================= This document outlines the safe work practices and procedures for working in proximity to or performing maintenance on 480V electrical panels. It includes guidelines for lockout/tagout (LOTO), arc

Read the thread
Human questionGeneral

Write a toolbox talk on construction, hand vibration syndrote

Hand-arm vibration syndrome (HAVS) is caused by vibration transmitted into the hands and arms from hand-held power tools and vibrating equipment. In construction, common sources include jackhammers, hammer drills, impact wrenches, chainsaws, grinders, pneumatic tools, and similar equipment. HAVS damages nerves, blood

Read the thread
Human questionUS

what standard covers fall protection for ironworkers in the CFR’s

Fall protection for ironworkers is covered under 29 CFR 1926 Subpart R, which specifically addresses steel erection [1]. Key aspects include: Fall Distance: Workers on a walking/working surface with an unprotected side or edge more than 15 feet (4.6 m) above a lower level must be protected from fall hazards [2].

Read the thread
Discussion thread

Add your experience.

Community answers can add practical context. They are moderated, but they are not SALUS-reviewed safety guidance.

New contributions are temporarily closed while the moderation queue is configured.

Community answers(0)

No community answers have been approved yet.

Comments on Rosie's answer(0)

No comments have been approved yet.

Ready to put operational safety to work?

Join 400K users across 150K sites already on SALUS.

No commitment · 30-minute personalized walkthrough