Skip to content
All safety questions
Asked by a personUnited Statesen-US

Sloping a 10-foot trench: what angle does OSHA require?

Reviewed by Julie Gunn, Head of Services, SALUS Safety

The question, as asked: Digging a 10' Trench. What degree should I slope back shoring?

A person submitted this question to Rosie's free generator. The asker's identity is neither imported nor published.

Rosie's answer

Published by SALUS

When digging a 10-foot trench, the sloping or shoring requirements depend on the soil type and other conditions 5, 6, 7. Here's a breakdown of factors to consider:

  1. Soil Classification: A "competent person" must classify the soil as Stable Rock, Type A, Type B, or Type C [1]. This classification is crucial for determining the appropriate slope [2].
  1. Sloping Options:
  • Option 1 (Allowable Configurations and Slopes): You can slope the excavation at an angle no steeper than 1 1/2 horizontal to one vertical (34 degrees) [3]. This is generally for Type C soil [3].
  • Option 2 (Appendices A and B): Use the guidelines in OSHA's appendices for maximum allowable slopes and configurations [3].
  • Option 3 (Tabulated Data): Follow tabulated data (tables and charts) approved by a registered professional engineer [3]. A copy of this data must be available at the job site [3].
  • Option 4 (Design by a Registered Professional Engineer): Have a registered professional engineer design the sloping and benching system [3]. The design must be in written form and include the slopes and configurations determined to be safe [3].
  1. Maximum Allowable Slopes: The maximum allowable slope depends on the soil type [2]:
  • Type A Soil: Maximum slope of 3/4:1 (horizontal to vertical) [4]
  • Type B Soil: Maximum slope of 1:1 (horizontal to vertical) [5]
  • Type C Soil: Maximum slope of 1 1/2:1 (horizontal to vertical) [3]
  • Stable Rock: Vertical sides are allowed if the rock is stable [6].
  1. Shoring Systems: As an alternative to sloping, you can use a shoring system [6]. This involves installing supports to prevent cave-ins [6].
  1. Competent Person: A "competent person" must inspect the excavation daily for any signs of potential cave-ins or other hazards [7]. They also need to be able to identify existing and predictable hazards in the surroundings [8].
  1. Additional Considerations:
  • Surface Encumbrances: Remove or support any surface encumbrances that could be a hazard [9].
  • Underground Installations: Identify and locate any underground utilities before excavating [9].
  • Water Accumulation: Take precautions to prevent water accumulation in the excavation [10].
  • Adjacent Structures: Ensure the stability of nearby structures [10].

Disclaimer: Regulations can vary and it is important to check with your local authorities for any specific requirements in Maryland.

10 source record(s)

Sources used for this answer

[1] Safety and Health Regulations for Construction (OSHA)

Page 95

Open source document

Source excerpt

## 29 CFR 1926 (OSHA) - (iii) Adequate precaution shall be taken such as providing ventilation, to prevent employee exposure to an atmosphere containing a concentration of a flammable gas in excess of 20 percent of the lower flammable limit of the gas. - (iv) When controls are used that are intended to reduce the level of atmospheric contaminants to acceptable levels, testing shall be conducted as often as necessary to ensure that the atmosphere remains safe. - (2) Emergency rescue equipment. (i) Emergency rescue equipment, such as breathing apparatus, a safety harness and line, or a basket stretcher, shall be readily available where hazardous atmospheric conditions exist or may reasonably be expected to develop during work in an excavation. This equipment shall be attended when in use. - (ii) Employees entering bell-bottom pier holes, or other similar deep and confined footing excavations, shall wear a harness with a life-line securely attached to it. The lifeline shall be separate from any line used to handle materials, and shall be individually attended at all times while the employee wearing the lifeline is in the excavation. - (h) Protection from hazards associated with water accumulation. (1) Employees shall not work in excavations in which there is accumulated water, or in excavations in which water is accumulating, unless adequate precautions have been taken to protect employees against the hazards posed by water accumulation. The precautions necessary to protect employees adequately vary with each situation, but could include special support or shield systems to protect from cave-ins, water removal to control the level of accumulating water, or use of a safety harness and lifeline. - (2) If water is controlled or prevented from accumulating by the use of water removal equipment, the water removal equipment and operations shall be monitored by a competent person to ensure proper operation. - (3) If excavation work interrupts the natural drainage of surface …

[2] Safety and Health Regulations for Construction (OSHA)

Page 91

Open source document

Source excerpt

## 29 CFR 1926 (OSHA) ## Subpart P-Excavations AUTHORITY: Sec. 107, Contract Worker Hours and Safety Standards Act (Construction Safety Act) (40 U.S.C. 333); Secs. 4, 6, 8, Occupational Safety and Hea1th Act of 1970 (29 U.S.C. 653, 655, 657); Secretary of Labor's Order No. 12-71 (36 FR 8754), 8-76 (41 FR [redacted postal code]), or 9-83 (48 FR [redacted postal code]), as applicable, and 29 CFR part 1911. SOURCE: 54 FR [redacted postal code], Oct. 31, 1989, unless otherwise noted. ## §1926.650 Scope, application, and definitions applicable to this subpart. (a) Scope and application. This subpart applies to all open excavations made in the earth's surface. Excavations are defined to include trenches. ## (b) Definitions applicable to this subpart. Accepted engineering practices means those requirements which are compatible with standards of practice required by a registered professional engineer. Aluminum Hydraulic Shoring means a pre-engineered shoring system comprised of aluminum hydraulic cylinders (crossbraces) used in conjunction with vertical rails (uprights) or horizontal rails (walers). Such system is designed, specifically to support the sidewalls of an excavation and prevent cave-ins. Bell-bottom pier hole means a type of shaft or footing excavation, the bottom of which is made larger than the cross section above to form a belled shape. Benching (Benching system) means a method of protecting employees from cave-ins by excavating the sides of an excavation to form one or a series of horizontal levels or steps, usually with vertical or near-vertical surfaces between levels. Cave-in means the separation of a mass of soil or rock material from the side of an excavation, or the loss of soil from under a trench shield or support system, and its sudden movement into the excavation, either by falling or sliding, in sufficient quantity so that it could entrap, bury, or otherwise injure and immobilize a person. Competent person means one who is capable of…

[3] Safety and Health Regulations for Construction (OSHA)

Page 105

Open source document

Source excerpt

## 29 CFR 1926 (OSHA) appendix apply when the design of sloping and benching protective systems is to be performed in accordance with the requirements set forth in §1926.652(b)(2). ## (b) Definitions. Actual slope means the slope to which an excavation face is excavated. Distress means that the soil is in a condition where a cave-in is imminent or is likely to occur. Distress is evidenced by such phenomena as the development of fissures in the face of or adjacent to an open excavation; the subsidence of the edge of an excavation; the slumping of material from the face or the bulging or heaving of material from the bottom of an excavation; the spalling of material from the face of an excavation; and ravelling, i.e., small amounts of material such as pebbles or little clumps of material suddenly separating from the face of an excavation and trickling or rolling down into the excavation. Maximum allowable slope means the steepest incline of an excavation face that is acceptable for the most favorable site conditions as protection against cave-ins, and is expressed as the ratio of horizontal distance to vertical rise (H:V). Short term exposure means a period of time less than or equal to 24 hours that an excavation is open. - (c) Requirements -(1) Soil classification. Soil and rock deposits shall be classified in accordance with appendix A to subpart P of part 1926. - (2) Maximum allowable slope. The maximum allowable slope for a soil or rock deposit shall be determined from Table B-1 of this appendix. - (3) Actual slope. (i) The actual slope shall not be steeper than the maximum allowable slope. - (ii) The actual slope shall be less steep than the maximum allowable slope, when there are signs of distress. If that situation occurs, the slope shall be cut back to an actual slope which is at least Ú 1 2 horizontal to one vertical ( Ú H:1V) less steep than the maximum allowable slope. 1 2 - (iii) When surcharge loads from stored material or equipment, operating e…

[4] Safety and Health Regulations for Construction (OSHA)

Page 106

Open source document

Source excerpt

Figure B-1 ## Slope Configurations (All slopes stated below are in the horizontal to vertical ratio) B-1.1 Excavations made in Type A soil. - 1. All simple slope excavation 20 feet or less in depth shall have a maximum allowable slope of Ú 3 4 :1. <!-- image --> SIMPLE SLOPE-GENERAL Exception: Simple slope excavations which are open 24 hours or less (short term) and which are 12 feet or less in depth shall have a maximum allowable slope of Ú :1. 1 2

[5] Safety and Health Regulations for Construction (OSHA)

Page 92

Open source document

Source excerpt

## 29 CFR 1926 (OSHA) Failure means the breakage, displacement, or permanent deformation of a structural member or connection so as to reduce its structural integrity and its supportive capabilities. Hazardous atmosphere means an atmosphere which by reason of being explosive, flammable, poisonous, corrosive, oxidizing, irritating, oxygen deficient, toxic, or otherwise harmful, may cause death, illness, or injury. Kickout means the accidental release or failure of a cross brace. Protective system means a method of protecting employees from cave-ins, from material that could fall or roll from an excavation face or into an excavation, or from the collapse of adjacent structures. Protective systems include support systems, sloping and benching systems, shield systems, and other systems that provide the necessary protection. Ramp means an inclined walking or working surface that is used to gain access to one point from another, and is constructed from earth or from structural materials such as steel or wood. Registered Professional Engineer means a person who is registered as a professional engineer in the state where the work is to be performed. However, a professional engineer, registered in any state is deemed to be a 'registered professional engineer' within the meaning of this standard when approving designs for 'manufactured protective systems' or 'tabulated data' to be used in interstate commerce. Sheeting means the members of a shoring system that retain the earth in position and in turn are supported by other members of the shoring system. Shield (Shield system) means a structure that is able to withstand the forces imposed on it by a cavein and thereby protect employees within the structure. Shields can be permanent structures or can be designed to be portable and moved along as work progresses. Additionally, shields can be either premanufactured or job-built in accordance with §1926.652 (c)(3) or (c)(4). Shields used in trenches are usually referred to…

[6] Safety and Health Regulations for Construction (OSHA)

Page 108

Open source document

Source excerpt

UNSUPPORTED VERTICALLY SIDED LOWER PORTION-MAXIMUM 12 FEET IN DEPTH <!-- image --> All excavations 20 feet or less in depth which have vertically sided lower portions that are supported or shielded shall have a maximum allowable slope of Ú :1. The support or shield system must extend at 3 4 least 18 inches above the top of the vertical side. SUPPORTED OR SHIELDED VERTICALLY SIDED LOWER PORTION <!-- image --> - 4. All other simple slope, compound slope, and vertically sided lower portion excavations shall be in accordance with the other options permitted under §1926.652(b). - 1. All simple slope excavations 20 feet or less in depth shall have a maximum allowable slope of 1:1. - 2. All benched excavations 20 feet or less in depth shall have a maximum allowable slope of 1:1 and maximum bench dimensions as follows: SIMPLE SLOPE <!-- image -->

[7] Safety and Health Regulations for Construction (OSHA)

Page 93

Open source document

Source excerpt

## 29 CFR 1926 (OSHA) Support system means a structure such as underpinning, bracing, or shoring, which provides support to an adjacent structure, underground installation, or the sides of an excavation. Tabulated data means tables and charts approved by a registered professional engineer and used to design and construct a protective system. Trench (Trench excavation) means a narrow excavation (in relation to its length) made below the surface of the ground. In general, the depth is greater than the width, but the width of a trench (measured at the bottom) is not greater than 15 feet (4.6 m). If forms or other structures are installed or constructed in an excavation so as to reduce the dimension measured from the forms or structure to the side of the excavation to 15 feet (4.6 m) or less (measured at the bottom of the excavation), the excavation is also considered to be a trench. Trench box. See 'Shield.' ## Trench shield. See 'Shield.' Uprights means the vertical members of a trench shoring system placed in contact with the earth and usually positioned so that individual members do not contact each other. Uprights placed so that individual members are closely spaced, in contact with or interconnected to each other, are often called 'sheeting.' Wales means horizontal members of a shoring system placed parallel to the excavation face whose sides bear against the vertical members of the shoring system or earth. ## §1926.651 Specific excavation requirements. - (a) Surface encumbrances. All surface encumbrances that are located so as to create a hazard to employees shall be removed or supported, as necessary, to safeguard employees. - (b) Underground installations. (1) The estimated location of utility installations, such as sewer, telephone, fuel, electric, water lines, or any other underground installations that reasonably may be expected to be encountered during excavation work, shall be determined prior to opening an excavation. - (2) Utility companies or…

[8] Safety and Health Regulations for Construction (OSHA)

Page 97

Open source document

Source excerpt

## 29 CFR 1926 (OSHA) - (2) Protective systems shall have the capacity to resist without failure all loads that are intended or could reasonably be expected to be applied or transmitted to the system. - (b) Design of sloping and benching systems. The slopes and configurations of sloping and benching systems shall be selected and constructed by the employer or his designee and shall be in accordance with the requirements of paragraph (b)(1); or, in the alternative, paragraph (b)(2); or, in the alternative, paragraph (b)(3), or, in the alternative, paragraph (b)(4), as follows: - (1) Option (1)-Allowable configurations and slopes. (i) Excavations shall be sloped at an angle not steeper than one and one-half horizontal to one vertical (34 degrees measured from the horizontal), unless the employer uses one of the other options listed below. - (ii) Slopes specified in paragraph (b)(1)(i) of this section, shall be excavated to form configurations that are in accordance with the slopes shown for Type C soil in appendix B to this subpart. - (2) Option (2)-Determination of slopes and configurations using Appendices A and B. Maximum allowable slopes, and allowable configurations for sloping and benching systems, shall be determined in accordance with the conditions and requirements set forth in appendices A and B to this subpart. - (3) Option (3)-Designs using other tabulated data. (i) Designs of sloping or benching systems shall be selected from and be in accordance with tabulated data, such as tables and charts. - (ii) The tabulated data shall be in written form and shall include all of the following: - (A) Identification of the parameters that affect the selection of a sloping or benching system drawn from such data; - (B) Identification of the limits of use of the data, to include the magnitude and configuration of slopes determined to be safe; - (C) Explanatory information as may be necessary to aid the user in making a correct selection of a protective system from the …

[9] Safety and Health Regulations for Construction (OSHA)

Page 102

Open source document

Source excerpt

## 29 CFR 1926 (OSHA) - (iv) The soil is part of a sloped, layered system where the layers dip into the excavation on a slope of four horizontal to one vertical (4H:1V) or greater; or - (v) The material is subject to other factors that would require it to be classified as a less stable material. ## Type B means: - (i) Cohesive soil with an unconfined compressive strength greater than 0.5 tsf (48 kPa) but less than 1.5 tsf (144 kPa); or - (ii) Granular cohesionless soils including: angular gravel (similar to crushed rock), silt, silt loam, sandy loam and, in some cases, silty clay loam and sandy clay loam. - (iii) Previously disturbed soils except those which would otherwise be classed as Type C soil. - (iv) Soil that meets the unconfined compressive strength or cementation requirements for Type A, but is fissured or subject to vibration; or - (v) Dry rock that is not stable; or - (vi) Material that is part of a sloped, layered system where the layers dip into the excavation on a slope less steep than four horizontal to one vertical (4H:1V), but only if the material would otherwise be classified as Type B. - Type C means: - (i) Cohesive soil with an unconfined compressive strength of 0.5 tsf (48 kPa) or less; or - (ii) Granular soils including gravel, sand, and loamy sand; or - (iii) Submerged soil or soil from which water is freely seeping; or - (iv) Submerged rock that is not stable, or - (v) Material in a sloped, layered system where the layers dip into the excavation or a slope of four horizontal to one vertical (4H:1V) or steeper. Unconfined compressive strength means the load per unit area at which a soil will fail in compression. It can be determined by laboratory testing, or estimated in the field using a pocket penetrometer, by thumb penetration tests, and other methods. Wet soil means soil that contains significantly more moisture than moist soil, but in such a range of values that cohesive material will slump or begin to flow when vibrated. Granular m…

[10] Safety and Health Regulations for Construction (OSHA)

Page 96

Open source document

Source excerpt

- (iv) A registered professional engineer has approved the determination that such excavation work will not pose a hazard to employees. - (3) Sidewalks, pavements, and appurtenant structure shall not be undermined unless a support system or another method of protection is provided to protect employees from the possible collapse of such structures. - (j) Protection of employees from loose rock or soil. (1) Adequate protection shall be provided to protect employees from loose rock or soil that could pose a hazard by falling or rolling from an excavation face. Such protection shall consist of scaling to remove loose material; installation of protective barricades at intervals as necessary on the face to stop and contain falling material; or other means that provide equivalent protection. - (2) Employees shall be protected from excavated or other materials or equipment that could pose a hazard by falling or rolling into excavations. Protection shall be provided by placing and keeping such materials or equipment at least 2 feet (.61 m) from the edge of excavations, or by the use of retaining devices that are sufficient to prevent materials or equipment from falling or rolling into excavations, or by a combination of both if necessary. - (k) Inspections. (1) Daily inspections of excavations, the adjacent areas, and protective systems shall be made by a competent person for evidence of a situation that could result in possible cave-ins, indications of failure of protective systems, hazardous atmospheres, or other hazardous conditions. An inspection shall be conducted by the competent person prior to the start of work and as needed throughout the shift. Inspections shall also be made after every rainstorm or other hazard increasing occurrence. These inspections are only required when employee exposure can be reasonably anticipated. - (2) Where the competent person finds evidence of a situation that could result in a possible cave-in, indications of failure of protective sys…

Related Q&A

Keep exploring.

Human questionGeneral

rail construction

Rail Construction and Maintenance Safety ======================================== Document Number: \[SWP-NUMBER] Revision Date: \[DATE] Next Review Date: \[NEXT REVIEW DATE] Department: \[DEPARTMENT NAME] 1\. Scope This safe work procedure (SWP) outlines the safety requirements for all rail construction and maintenance

Read the thread
Human questionUS

excavation procedures

Excavation Safety: Shoring, Sloping, and Trenching ================================================== This document outlines safe work practices and hazard controls for excavation procedures, focusing on shoring, sloping, and trenching safety. It is essential to understand and implement these practices to prevent

Read the thread
Human questionUS

Excavation

Toolbox Talk: Excavation Safety *Date:** [DATE] *Duration:** [DURATION] minutes *Presenter:** [PRESENTER NAME] *Location:** [LOCATION] Objective The objective of this toolbox talk is to educate participants on the hazards associated with excavation work and the necessary safety measures to prevent accidents and

Read the thread
Human questionGeneral

Excavation and trenching

Toolbox Talk: Excavation and Trenching Safety *Date:** [DATE] *Duration:** [DURATION] minutes *Presenter:** [PRESENTER NAME] *Location:** [LOCATION] Objective The objective of this toolbox talk is to educate participants on the safety practices and regulations related to excavation and trenching. By the end of this

Read the thread
Discussion thread

Add your experience.

Community answers can add practical context. They are moderated, but they are not reviewed by Francis Langlois or presented as SALUS safety guidance.

New contributions are closed. Previously approved contributions remain visible.

Community answers(0)

No community answers have been approved yet.

Comments on Rosie's answer(0)

No comments have been approved yet.

Ready to put operational safety to work?

Join 400K users across 150K sites already on SALUS.