Do you need to protect a trench that is 2 feet deep?

Reviewed by Julie Gunn, Head of Services, SALUS Safety

The question, as asked: Do I need to protect a trench that is 2 ft deep, 2 ft wide and 40 ft long?

A person submitted this question to Rosie's free generator. The asker's identity is neither imported nor published.

Rosie's answer

Published by SALUS

For a trench that is 2 feet deep, 2 feet wide, and 40 feet long, OSHA regulations generally do not require protective systems such as shoring or trench boxes, as these are typically mandated for trenches deeper than 5 feet. However, it is important to ensure that the trench is safe for workers, even at this depth. Here are some key considerations:

  1. Surface Encumbrances: Ensure that any surface encumbrances that could pose a hazard to employees are removed or supported to safeguard employees [1].
  1. Underground Installations: Before starting excavation, determine the location of any underground utilities to avoid accidental damage [1].
  1. Spoil Piles: Keep excavated materials at least 2 feet away from the edge of the trench to prevent them from falling back in [2].
  1. Access and Egress: Although not required for trenches less than 4 feet deep, consider providing a safe means of entry and exit, such as a ladder, if workers need to enter the trench [3].
  1. Inspection: Conduct daily inspections of the trench and surrounding areas for signs of potential hazards, such as cave-ins or hazardous atmospheres, especially after rain or other events that could affect trench stability [4].

While protective systems are not required for a trench of this depth, maintaining general safety practices is crucial to ensure worker safety.

4 source record(s)

Sources used for this answer

[1] Rules for the Administration of the Oregon Safe Employment Act (Construction, Division 3, OSHA Oregon)

Page 702

Open source document

Source excerpt

<!-- image --> ## SPECIFIC EXCAVATION REQUIREMENTS Oregon Administrative Rules Oregon Occupational Safety and Health Division - (ii) Ramps and runways constructed of two or more structural members shall have the structural members connected together to prevent displacement. - (iii) Structural members used for ramps and runways shall be of uniform thickness. - (iv) Cleats or other appropriate means used to connect runway structural members shall be attached to the bottom of the runway or shall be attached in a manner to prevent tripping. - (v) Structural ramps used in lieu of steps shall be provided with cleats or other surface treatments on the top surface to prevent slipping. - (2) Means of egress from trench excavations. A stairway, ladder, ramp or other safe means of egress shall be located in trench excavations that are 4 feet (1.22 m) or more in depth so as to require no more than 25 feet (7.62 m) of lateral travel for employees. - (d) Exposure to vehicular traffic. Employees exposed to public vehicular traffic shall be provided with, and shall wear, warning vests or other suitable garments marked with or made of reflectorized or high-visibility material. - (e) Exposure to falling loads. No employee shall be permitted underneath loads handled by lifting or digging equipment. Employees shall be required to stand away from any vehicle being loaded or unloaded to avoid being struck by any spillage or falling materials. Operators may remain in the cabs of vehicles being loaded or unloaded when the vehicles are equipped, in accordance with §1926.601(b)(6), to provide adequate protection for the operator during loading and unloading operations. - (f) Warning system for mobile equipment. When mobile equipment is operated adjacent to an excavation, or when such equipment is required to approach the edge of an excavation, and the operator does not have a clear and direct view of the edge of the excavation, a warning system shall be utilized such as barricades, han…

[2] Rules for the Administration of the Oregon Safe Employment Act (Construction, Division 3, OSHA Oregon)

Page 704

Open source document

Source excerpt

<!-- image --> ## SPECIFIC EXCAVATION REQUIREMENTS Oregon Administrative Rules Oregon Occupational Safety and Health Division ## (i) Stability of adjacent structures. - (1) Where the stability of adjoining buildings, walls, or other structures is endangered by excavation operations, support systems such as shoring, bracing, or underpinning shall be provided to ensure the stability of such structures for the protection of employees. - (2) Excavation below the level of the base or footing of any foundation or retaining wall that could be reasonably expected to pose a hazard to employees shall not be permitted except when: - (i) A support system, such as underpinning, is provided to ensure the safety of employees and the stability of the structure; or - (ii) The excavation is in stable rock; or - (iii) A registered professional engineer has approved the determination that the structure is sufficiently removed from the excavation so as to be unaffected by the excavation activity; or - (iv) A registered professional engineer has approved the determination that such excavation work will not pose a hazard to employees. - (3) Sidewalks, pavements, and appurtenant structure shall not be undermined unless a support system or another method of protection is provided to protect employees from the possible collapse of such structures ## (j) Protection of employees from loose rock or soil. - (1) Adequate protection shall be provided to protect employees from loose rock or soil that could pose a hazard by falling or rolling from an excavation face. Such protection shall consist of scaling to remove loose material; installation of protective barricades at intervals as necessary on the face to stop and contain falling material; or other means that provide equivalent protection. - (2) Employees shall be protected from excavated or other materials or equipment that could pose a hazard by falling or rolling into excavations. Protection shall be provided by placing and keeping …

[3] Rules for the Administration of the Oregon Safe Employment Act (Construction, Division 3, OSHA Oregon)

Page 705

Open source document

Source excerpt

Oregon Administrative Rules Oregon Occupational Safety and Health Division ## SPECIFIC EXCAVATION REQUIREMENTS P ## (k) Inspections. - (1) Daily inspections of excavations, the adjacent areas, and protective systems shall be made by a competent person for evidence of a situation that could result in possible cave-ins, indications of failure of protective systems, hazardous atmospheres, or other hazardous conditions. An inspection shall be conducted by the competent person prior to the start of work and as needed throughout the shift. Inspections shall also be made after every rainstorm or other hazard increasing occurrence. These inspections are only required when employee exposure can be reasonably anticipated. - (2) Where the competent person finds evidence of a situation that could result in a possible cave-in, indications of failure of protective systems, hazardous atmospheres, or other hazardous conditions, exposed employees shall be removed from the hazardous area until the necessary precautions have been taken to ensure their safety. - (l) Fall protection. Walkways shall be provided where employees or equipment are required or permitted to cross over excavations. Guardrails which comply with §1926.502(b) shall be provided where walkways are 6 feet (1.8 m) or more above lower levels. Stat. Auth.: ORS 654.025(2) and 656.726(4). Stats. Implemented: ORS 654.001 through 654.295. Hist: APD Admin. Order 8-1990, f. 3/30/90, ef. 9/1/90. OR-OSHA Admin. Order 6-1995, f. 4/18/95, ef. 6/1/95.

[4] Safety and Health Regulations for Construction (OSHA)

Page 93

Open source document

Source excerpt

## 29 CFR 1926 (OSHA) Support system means a structure such as underpinning, bracing, or shoring, which provides support to an adjacent structure, underground installation, or the sides of an excavation. Tabulated data means tables and charts approved by a registered professional engineer and used to design and construct a protective system. Trench (Trench excavation) means a narrow excavation (in relation to its length) made below the surface of the ground. In general, the depth is greater than the width, but the width of a trench (measured at the bottom) is not greater than 15 feet (4.6 m). If forms or other structures are installed or constructed in an excavation so as to reduce the dimension measured from the forms or structure to the side of the excavation to 15 feet (4.6 m) or less (measured at the bottom of the excavation), the excavation is also considered to be a trench. Trench box. See 'Shield.' ## Trench shield. See 'Shield.' Uprights means the vertical members of a trench shoring system placed in contact with the earth and usually positioned so that individual members do not contact each other. Uprights placed so that individual members are closely spaced, in contact with or interconnected to each other, are often called 'sheeting.' Wales means horizontal members of a shoring system placed parallel to the excavation face whose sides bear against the vertical members of the shoring system or earth. ## §1926.651 Specific excavation requirements. - (a) Surface encumbrances. All surface encumbrances that are located so as to create a hazard to employees shall be removed or supported, as necessary, to safeguard employees. - (b) Underground installations. (1) The estimated location of utility installations, such as sewer, telephone, fuel, electric, water lines, or any other underground installations that reasonably may be expected to be encountered during excavation work, shall be determined prior to opening an excavation. - (2) Utility companies or…

Related Q&A

Keep exploring.

Human questionUS

Asbestos

Asbestos Handling and Removal: Health and Safety Regulations ============================================================ This document outlines the key health and safety regulations concerning asbestos handling and removal, drawing from OSHA and Cal/OSHA standards. It addresses scope, permissible exposure limits

Read the thread
Human questionGeneral

Excavation and trenching

Toolbox Talk: Excavation and Trenching Safety *Date:** [DATE] *Duration:** [DURATION] minutes *Presenter:** [PRESENTER NAME] *Location:** [LOCATION] Objective The objective of this toolbox talk is to educate participants on the safety practices and regulations related to excavation and trenching. By the end of this

Read the thread
Human questionUS

Install pipe in excavation

Safe Work Procedure: Install Pipe in Excavation Document Number: [SWP-NUMBER] Revision Date: [DATE] Next Review Date: [NEXT REVIEW DATE] Department: [DEPARTMENT NAME] 1. Scope This procedure covers the safe installation of pipes in excavations, including the identification and management of underground utilities

Read the thread
Human questionUS

high voltage construction work

Safe Work Procedure: High Voltage Construction Work Document Number: [SWP-NUMBER] Revision Date: [DATE] Next Review Date: [NEXT REVIEW DATE] Department: [DEPARTMENT NAME] 1. Scope This Safe Work Procedure (SWP) outlines the necessary safety precautions and procedures to be followed when performing construction work in

Read the thread
Discussion thread

Add your experience.

Community answers can add practical context. They are moderated, but they are not reviewed by Francis Langlois or presented as SALUS safety guidance.

New contributions are closed. Previously approved contributions remain visible.

Community answers(0)

No community answers have been approved yet.

Comments on Rosie's answer(0)

No comments have been approved yet.

Ready to put operational safety to work?

Join 400K users across 150K sites already on SALUS.

No commitment · 30-minute personalized walkthrough