Cave-in protection for a 15-foot-deep open pit excavation
Reviewed by Julie Gunn, Head of Services, SALUS Safety
The question, as asked: what cave in protection is required in an open pit excavation 15 feet deep and 50 feet long and 50 feet wide. the walls of the open pit excavation are vertical, 90 degrees perpendicular to the working surface
A person submitted this question to Rosie's free generator. The asker's identity is neither imported nor published.
Rosie's answer
Published by SALUSFor an open pit excavation that is 15 feet deep, 50 feet long, and 50 feet wide with vertical 90-degree walls, OSHA Subpart P requires cave-in protection if employees are exposed. This excavation is not a trench under the standard definitions because a trench is a narrow excavation with a bottom width not greater than 15 feet; however, it is still an excavation covered by 29 CFR 1926 Subpart P, and employees must be protected from cave-ins by an appropriate protective system. With vertical 90-degree walls at 15 feet deep, the excavation is not compliant unless it is made entirely in stable rock or protected by a properly designed support/shield system. An unprotected vertical wall at that depth is not acceptable under OSHA excavation rules. [3] [5] [1]
Required protective system options for cave-in protection:
- Sloping: OSHA's default allowable slope option is no steeper than 1\.5H:1V (34 degrees from horizontal). For a 15-foot-deep excavation, that means each wall would need about 22\.5 feet of horizontal run from the bottom edge to the top. In a 50-foot-wide pit, sloping all four sides from a centered 15-foot-deep bottom would generally leave only about a 5-foot-wide bottom if geometry allows, so the existing 90-degree walls would have to be cut back substantially.
- Benching: Benching may be used only if allowed by the soil conditions and Appendix B criteria. Benching is not allowed in Type C soil. Vertical 90-degree walls are not benching; the excavation would need properly configured stepped sides.
- Shoring: Hydraulic, timber, aluminum, steel, or engineered shoring may be used to support the excavation walls and prevent soil movement. The system must be selected based on soil type, depth, width, water conditions, surcharge loads, and nearby activity.
- Shielding: A trench box or other shield may protect workers inside the protected zone, but shielding does not prevent a cave-in; it protects workers if one occurs. Shield systems must be suitable for the excavation dimensions and conditions, and if excavation extends more than 2 feet below the bottom of the shield, the system must be designed to resist the full depth or comply with engineer-design requirements.
- Engineer involvement: Because this excavation is 15 feet deep, a registered professional engineer is not automatically required solely by depth. However, an engineer is required for excavations more than 20 feet deep, and may also be needed whenever the employer uses engineered/tabulated support or shield designs beyond simple allowable slope options.
[9] [1] [7] [7] [12] [2] Soil classification is a key compliance issue. If the employer uses the simple allowable slope option of 1\.5H:1V for an excavation 20 feet or less deep, OSHA enforcement guidance states that initial soil testing/classification is not required. But if the employer uses another option, such as Appendix-based sloping/benching or many shoring/shielding designs, the employer must classify the soil using Appendix A methodology and select the system accordingly. Soil type, water content, weather changes, surcharge loads, and nearby operations all affect the protective system choice. Type C soil is the least stable, and benching is not permitted in Type C soil. [4] [9] [9] [11] [14] [1]
A competent person must inspect the excavation before worker entry, daily, at the start of each shift, and after any condition change such as rain, water intrusion, vibration, or other events that could increase hazards. The competent person must be able to identify existing and predictable hazards, classify soil, select protective systems, and have authority to correct hazards immediately or remove employees from danger. If the protective system appears inadequate or conditions indicate possible failure, employees should be removed until the hazard is corrected. [1] [6] [5] [3] [8]
Other Subpart P compliance points that commonly apply to this excavation:
- Keep spoil piles, materials, and heavy equipment at least 2 feet back from the excavation edge to reduce surcharge loading.
- Provide safe access/egress if employees work in excavations 4 feet or deeper; ladders, steps, ramps, or similar means must be available, and in trench excavations must be within 25 feet of workers.
- Test for hazardous atmospheres when the excavation is greater than 4 feet deep and atmospheric hazards could exist.
- Inspect after rainstorms, water intrusion, or changing site conditions; do not allow employees to work where water is accumulating unless hazards are controlled.
- Do not allow employees under suspended loads, and protect workers from mobile equipment, falling materials, and adjacent structure hazards as applicable.
[6] [6] [11] [10] [1] Bottom line for the described condition: a 15-foot-deep open excavation with vertical 90-degree walls is not OSHA-compliant for employee entry unless it is in stable rock or protected by a properly selected and installed protective system. To comply with 29 CFR 1926\.651 and 1926\.652, the employer must have a competent person evaluate the excavation, classify the soil when required, and implement one of the recognized cave-in protection methods: sloping, benching (if permitted by soil type), shoring, or shielding. For this specific geometry, the most realistic compliant approaches are usually substantial cutback/sloping, or an engineered shoring/shielding system selected from OSHA appendices, manufacturer tabulated data, other approved tabulated data, or a registered professional engineer design. Employees should not enter the excavation until those protections are in place and inspected. [1] [2] [7] [13]
Sources used for this answer
[1] Excavation Safety- Instructor Version
Page 5
Open source documentSource excerpt
# Welcome Page (cont.) ## Cave-ins: (cont.) This material is for training use only # Scope, Application, Definitions {Division 3/Subdivision P 29 CFR 1926.650} ## Scope and Application This subpart applies to all excavations made in the earth's surface. Excavations are defined to include trenches. ## Some KEY Definitions: Competent Person means one who is capable of identifying existing and predictable hazards in the surroundings, or working conditions which are unsanitary, hazardous, or dangerous to employees, and who has authorization to take prompt corrective measures to eliminate them. Protective System means a method of protecting employees from cave-ins, from material that could fall or roll from an excavation face or into an excavation, or from the collapse of adjacent structures. Protective systems include support systems, sloping and benching systems, shield systems, and other systems that provide the necessary protection. Registered Professional Engineer means a person who is registered as a professional engineer in the state where the work is to be performed. However, a professional engineer, registered in any state is deemed to be a “registered professional engineer" within the meaning of this standard when approving designs for "manufactured protective systems" or "tabulated data” to be used in interstate commerce. Support System means a structure such as underpinning, bracing, or shoring, which provides support to an adjacent structure, underground installation, or the sides of an excavation. Tabulated Data means tables and charts approved by a registered professional engineer and used to design and construct a protective system. Trench (Trench excavation) means a narrow excavation (in relation to its length) made below the surface of the ground. In general, the depth is greater than the width, but the width of a trench (measured at the bottom) is not greater than 15 feet. OR-OSHA 302 Excavation Safety 3
[2] Program Directive: Compliance Procedures for the Excavation Standard, 1926.650-652 and Appendices
Page 39
Open source documentSource excerpt
# standard. (Note that requirements under 1926 Subpart G - Signs, Signals, and Barricades may also apply.) (cont.) ## Citation Policy (cont.) This section provides four alternatives for the design and construction of sloping and benching systems for protecting employees working in excavations. As defined in § 1926.650(b), "Benching” means “a method of protecting employees from cave-ins by excavating the sides of an excavation to form one or a series of horizontal levels or steps, usually with vertical or near-vertical surfaces between levels.” “Sloping” refers to “a method of protecting employees from cave-ins by excavating to form sides of an excavation that are inclined away from the excavation so as to prevent cave-ins." ## § 1926.652(b)(1). Option (1). Allowable configurations and slopes. Under this Option, the excavation sides must be sloped at an angle that is not steeper than one and one-half horizontal to one vertical (1.5H:1V, 34 degrees measured from the horizontal). Employers may cut the excavation to the slope specified by this option without the need for initial testing and classifying the soil at the excavation site. NOTE: Where the evidence shows that no support system was used and that the sides of the excavation are steeper than 1.5H:1V, the employer has the burden of proving compliance with one of the other protective system options under this section or § 1926.652(c). The CSHO, however, should document all relevant information concerning the excavation, including any protective systems in place or lack of protective systems, to support a potential citation. NOTE: If an excavation is 20 feet or less in depth and sloped in accordance with the requirements of § 1926.652(b)(1)(i) (i.e., the slope is not greater than 34 degrees measured from the horizontal), then soil classification tests are not required. If an employer assumes type C soil is present, and provides the protection (sloping, shoring or shielding) required for type C soil, a citati…
[3] Compliance Directive for the Excavation Standard
Page 35
Open source documentSource excerpt
# Table of Contents (cont.) ## Inspection Guidance. (cont.) If the protective system appears inadequate or in danger of failure, the employer's representative or competent person shall be notified immediately so to remove any employees in the excavation until the hazard has been abated. - Citation Policy. § 1926.652(a)(2). Consider a citation if the protective system is incapable of supporting all intended or reasonably anticipated loads. Where applicable, § 1926.652(a)(2) shall be grouped with the specific requirement representing the option used, §§ 1926.652(b)-(c). 2. §1926.652(b). Design of Sloping and Benching Systems. - This section provides four alternatives for the design and construction of sloping and benching systems for protecting employees working in excavations. - As defined in § 1926.650(b), "Benching” means “a method of protecting employees from cave-ins by excavating the sides of an excavation to form one or a series of horizontal levels or steps, usually with vertical or near-vertical surfaces between levels." "Sloping" refers to "a method of protecting employees from cave-ins by excavating to form sides of an excavation that are inclined away from the excavation so as to prevent cave-ins." § 1926.652(b)(1). Option (1). Allowable configurations and slopes. - Under this option, the excavation sides must be sloped at an angle that is not steeper than one and one-half horizontal to one vertical (1.5H:1V, 34 degrees measured from the horizontal). Employers may cut the excavation to the slope specified by this option without the need for initial testing and classifying the soil at the excavation site. - NOTE: Where the evidence shows that no support system was used and that the sides of the excavation are steeper than 1.5H:1V, the employer has the burden of proving compliance with one of the other protective system options under this section or § 1926.652(c). The CSHO, however, should document all relevant information concerning the excav…
[4] Trenching and Excavation Safety Flyer
Page 1
Open source documentSource excerpt
# Trench and Excavation Safety Trench collapses, or cave-ins, are the leading hazard in excavation work. Safe trenching helps prevent falls, falling loads, hazardous atmospheres, and incidents involving mobile equipment. ## Trench Safety Measures Trenches 5 feet or deeper require a protective system unless dug in stable rock. For trenches less than 5 feet, a competent person must decide if protection is needed. Trenches 20 feet or deeper must have a protective system designed or approved by a registered professional engineer, as required by OSHA 1926.652(b) and (c). ## Competent Person Before workers enter a trench, a competent person must inspect it daily and after any condition changes to ensure safety. This person is trained to identify hazards, determine soil types, select protective systems, and has the authority to correct issues immediately. ## Access and Egress • Keep heavy equipment and spoils at least 2 feet from trench edges - Locate underground utilities before digging • Test for atmospheric hazards in trenches over 4 feet deep • Inspect trenches daily, at the start of each shift, after storms, and after conditions change • Never work under suspended loads - Wear high visibility clothing when near traffic # Protective Systems • Benching: a method of protecting workers from cave-ins by cutting the sides of an excavation into horizontal steps. Benching is not allowed in Type C soil. • Sloping: involves cutting back the trench wall at an angle inclined away from excavation. • Shoring: requires installing aluminum hydraulic or other types of supports to prevent soil movement and cave-ins. • Shielding: protects workers by using trench boxes or supports to prevent cave-ins. Designing these systems can be complex, as factors like soil type, trench depth, moisture, weather, nearby loads, and site activity must all be considered. OSHA standards require that employers provide workplaces free of recognized hazards. The employer must compl…
[5] Trenching Safety: Preventing Cave-ins
Page 1
Open source documentSource excerpt
Trenching Safety Preventing Cave-ins Trenching work is risky; cave-ins occur suddenly and bring lasting, tragic consequences. Safety preplanning, oversight, and training are key to ensuring work is set up and performed safely in trenches. ## Protective Systems Protective systems prevent cave-ins and protect workers from falling materials. There are three types: ■ Sloping and benching removes soil to eliminate the chance of cave-ins (benching isn't an option for sand, gravel, and other Type C soils). a ■Shoring uses supports to brace the walls of trench (e.g., aluminum hydraulic supports). ■ Shielding protects workers inside of the shielded area (e.g., trench boxes). Protective systems are required for all trenches four feet or deeper; and for those less than four feet deep if a potential for cave-in exists. Systems for trenches over 20 feet deep must be designed by a registered professional engineer (or designed according to tables, charts, and other tabulated data approved by them). ## Competent Person A competent person is someone who: ■ Conducts daily safety inspections of excavation areas, including protective systems, to identify existing and potential hazards. ■ Has the knowledge and authority to take immediate corrective measures to eliminate hazards and conditions; and has the authority to remove workers promptly if hazardous conditions are found. ## Getting In and Out Safely Workers must be able to easily and safely enter and exit trenches four feet or deeper. A way in or out must be available every 25 feet. The most common method for access is a straight ladder or an extension ladder. If a ladder is used, it must extend at least three feet above the landing. Other means could be a stairway or ramp designed by a registered professional engineer. ## General Safety Tips ■Don't let workers enter or work inside an unprotected trench four feet or more in depth. ■Never work inside a trench if the spoils pile is less than two feet away from the e…
[6] Trenching and Excavation Safety Fact Sheet
Page 1
Open source documentSource excerpt
OSHA DEPARTMENT OF LABOR AND INDUSTRY # Fact sheet # Trenching and excavation safety From 2014 through 2019, four Minnesota workers died in a trench, excavation or ground collapse. Cave-ins pose the greatest risk and are much more likely than other excavation-related accidents to result in worker fatalities. Minnesota law requires employers to provide a workplace free of recognized hazards that may cause serious injury or death. This includes the trenching and excavation requirements of 29 CFR 1926.651 and 1926.652. An excavation is any man-made cut, cavity, trench or depression in an earth surface, formed by earth removal. A trench - or a trench excavation - is a narrow excavation (in relation to its length) made below the surface of the ground; in general, the depth is greater than the width, but the width of a trench (measured at the bottom) is not greater than 15 feet. ## Dangers of trenching and excavation In addition to cave-ins, other potential hazards include falls, falling loads, hazardous atmospheres and incidents involving mobile equipment. Two cubic yards of soil can weigh about 6,000 pounds or as much as a small car. An unprotected trench is an early grave. Do not enter an unprotected trench. ## Trench safety measures Trenches five feet deep or greater require a protective system unless the excavation is made entirely in stable rock. If the trench is fewer than five feet deep, a competent person may determine a protective system is not required. Trenches 20 feet deep or greater require that the protective system be designed by a registered professional engineer or be based on tabulated data prepared and/or approved by a registered professional engineer in accordance with 1926.652(b) and (c). ## Competent person OSHA standards require employers ensure trenches - before worker entry - are inspected by a competent person daily and as conditions change, to ensure elimination of excavation hazards. A competent person is an individual: who is capab…
[7] Excavation Safety- Instructor Version
Page 30
Open source documentSource excerpt
# Requirements for Protective Systems {Division 3/Subdivision P 29 CFR 1926.652} (cont.) ## Option 2 allows the use of manufacturer's tabulated data. (cont.) This material is for training use only # Support, Shield, and other Protective System Options [29 CFR 1926.652(c)] The four options include: 1. Designs using OSHA's Appendix A (soil classification) & C (timber shoring) or D (aluminum hydraulic shoring); or 2. Designs using manufacturer's tabulated data; or 3. Designs using other tabulated data; or 4. Design by a registered professional engineer. OR-OSHA's Appendix C begins on p. P-23 of the workbook and Appendix D begins on p. P-33 of the workbook. The following is taken from OR-OSHA's publication titled, “Excavations” Pub. #440-2174 (6/06): Shoring and shielding systems prevent cave-ins in excavations with or without sloped or benched faces. The safest way to install and remove them is from outside the excavation. Shores are vertical or horizontal supports that prevent the faces of an excavation from collapsing. Vertical shores are called uprights. They're easy to install, relatively inexpensive, and often used in stable soil or in shallow excavations that have parallel faces. Vertical shores must be sized for the excavation's dimensions and soil type. Horizontal shores are called walers. Walers are often used when unstable soil makes sloping or benching impractical and when sheeting is necessary to prevent soil from sliding into the excavation. Shields provide employees a safe work area by protecting them from collapsing soil. Shields don't prevent cave-ins but “shield” workers if a face does collapse. They are usually placed in the excavation by heavy equipment. Shoring and shielding systems are available from manufacturers in a variety of dimensions, usually aluminum or steel, or they can be custom-built from tabulated data approved by a registered professional engineer. Manufacturers will also provide tabulated data with their systems that in…
[8] Trenching & Excavation - Special Emphasis Program
Page 2
Open source documentSource excerpt
# Tennessee OSHA's Special Emphasis Program on Trenching & Excavation Because trenching and excavation collapse is deadly and often involves multiple victims, Tennessee OSHA has established a special emphasis program to focus attention and resources on these hazards. It is impossible to predict when an excavation or trench will collapse. The sudden collapse of the walls makes escape almost impossible. The only way to prevent collapse is to slope or shore the walls or install a trench shield and follow the TOSHA trenching and excavation standards contained in 29 CFR 1926 Subpart P. Under this special emphasis program, all TOSHA compliance and consultative services personnel will be on the lookout for trenching or excavation work sites. Personal observation, reports of imminent danger, fatality/catastrophe reports, safety and health agency referrals, employee complaints, and media reports are also used to locate trenching and excavation work. Each occurrence is handled with an appropriate intervention by TOSHA. ## Hazards on the Excavation Site Excavation workers are exposed to many hazards, but the chief hazard is cave-in. TOSHA requires that all employees exposed to potential cave-ins be protected by sloping or benching the sides of the excavation, shoring the sides of the excavation, or placing a shield between the sides and the work area. In addition to cave-in hazards, workers must also be protected from adjacent utility lines, exposure to vehicular traffic, falling loads, hazardous atmospheres, and fall hazards. Utility lines such as gas, electrical, sewer, and water must be located and supported prior to placing employees in an excavation. Employees working in, or near, roadways must wear high visibility vests. Workers are not to work beneath suspended loads, and walkways crossing excavations must be equipped with guardrails. Precautions, including atmospheric testing and emergency rescue procedures and equipment, must be taken when workers enter excavat…
[9] OSH Enforcement Procedures | CPL 02-00-165 - Compliance Directive for the Excavation Standard, 29 CFR 1926, Subpart P
Page 55
Open source documentSource excerpt
# NOTE: § 1926.651(i) Stability of adjacent structures sets forth the employer's responsibility to support adjacent structures (e.g. buildings, walls, or other structures). See the discussion of citation policy for § 1926.651(i) below. (cont.) ## Inspection Guidance (cont.) calculated for the full depth of the trench, and there are no indications of a possible loss of soil from behind or below the bottom of the shield. ## Inspection Guidance Determine through observation, measurements and interviews the excavation depth below the support system, and whether there is any evidence of loss of soil from behind or below the bottom of the support system. ## Citation Policy § 1926.652(g)(2). Consider a citation of § 1926.652(g)(2) if the employer permitted the excavation of material deeper than 2 feet (.61m) below the bottom of shield system members in a trench, and the system was not designed to resist the forces calculated for the full depth of the trench or there were indications of a possible loss of soil from behind or below the bottom of the shield system. Note: In instances where a trench box or trench shield may be a component of a support system, consider grouping a citation of § 1926.652(g)(2) with § 1926.652(e)(2)(i). Excavations that extend more than 2 feet below the support system must comply with § 1926.652(c)(4), which requires design by a registered professional engineer. XII. Links to Appendices to Subpart P. Appendix A to Subpart P - Soil Classification Appendix B to Subpart P - Sloping and Benching Appendix C to Subpart P - Timber Shoring for Trenches Appendix D to Subpart P - Aluminum Hydraulic Shoring for Trenches Appendix E to Subpart P - Alternatives to Timber Shoring Appendix F to Subpart P - Selection of Protective Systems 53
[10] Trenching and Excavation Safety Fact Sheet
Page 2
Open source documentSource excerpt
# Trenching and excavation safety (cont.) ## General trenching and excavation rules (cont.) • Test for atmospheric hazards, such as low oxygen, hazardous fumes and toxic gases when greater than four feet deep. • Inspect trenches at the start of each shift and following a rainstorm or other water intrusion. • Do not work underneath suspended or raised loads and materials. • Inspect trenches after any occurrence that could have changed conditions in the trench. • Ensure personnel wear high-visibility or other suitable clothing when exposed to vehicular traffic or mobile earth-moving equipment. ## Protective systems There are different types of protective systems – sloping, shoring and shielding. <table><tr><th>Type of protective system</th><th></th><th>Illustration of system</th></tr><tr><td>Sloping involves cutting back the trench wall at an angle inclined away from the excavation.</td><td>20 MAX</td><td></td></tr><tr><td>Shoring requires installing aluminum hydraulic or other types of supports to prevent soil movement and cave-ins.</td><td></td><td></td></tr><tr><td>Shielding protects workers by using trench boxes or other types of supports to prevent soil cave-ins. Designing a protective system can be complex because many factors must be considered: soil classification; depth of cut; water content of soil; changes caused by weather or climate; surcharge loads (spoil, other materials to be used in the trench); and other operations in the vicinity.</td><td></td><td></td></tr></table> ## More information To learn more about excavation safety, view the standards at osha.gov. Revised March 2025
[11] Excavation Safety- Instructor Version
Page 26
Open source documentSource excerpt
# Requirements for Protective Systems {Division 3/Subdivision P 29 CFR 1926.652} (cont.) ## Selection of Protective Systems (cont.) This material is for training use only # Protective Systems [29 CFR 1926.652(a)] Excavations and trenches less than five feet deep must still be sloped, benched, or otherwise supported when a Competent Person determines there is indication of cave-in. a Be careful not to get caught up on just the five foot depth requirement. Consider work practices in a shallow trench as well (i.e. working hunched over or on hands and knees). ## Selection of Protective Systems Protective systems are divided into two categories and include four choices in each: 1. Sloping and benching systems; and 2. ...everything else. The basic systems for protecting employees from cave-ins are sloping, benching, shoring, and shielding. The system that you should use depends on factors such as soil type and water content, excavation depth and width, the nature of the work, and nearby activities that could increase the risk of a cave-in. The competent person has the responsibility for considering these factors and for determining the appropriate protective system. A registered professional engineer must design protective systems for all excavations that are more than 20 feet deep. (from OR-OSHA's publication titled, “Excavations” Pub. #440-2174 (6/06)). OR-OSHA 302 Excavation Safety 24
[12] OSH Enforcement Procedures | CPL 02-00-165 - Compliance Directive for the Excavation Standard, 29 CFR 1926, Subpart P
Page 43
Open source documentSource excerpt
# NOTE: § 1926.651(i) Stability of adjacent structures sets forth the employer's responsibility to support adjacent structures (e.g. buildings, walls, or other structures). See the discussion of citation policy for § 1926.651(i) below. (cont.) ## Citation Policy (cont.) This section provides four alternatives for the design and construction of sloping and benching systems for protecting employees working in excavations. As defined in § 1926.650(b), “Benching” means “a method of protecting employees from cave-ins by excavating the sides of an excavation to form one or a series of horizontal levels or steps, usually with vertical or near-vertical surfaces between levels." "Sloping" refers to "a method of protecting employees from cave-ins by excavating to form sides of an excavation that are inclined away from the excavation so as to prevent cave-ins." ## § 1926.652(b)(1). Option (1). Allowable configurations and slopes. Under this Option, the excavation sides must be sloped at an angle that is not steeper than one and one-half horizontal to one vertical (1.5H:1V, 34 degrees measured from the horizontal). Employers may cut the excavation to the slope specified by this option without the need for initial testing and classifying the soil at the excavation site. NOTE: Where the evidence shows that no support system was used and that the sides of the excavation are steeper than 1.5H:1V, the employer has the burden of proving compliance with one of the other protective system options under this section or § 1926.652(c). The CSHO, however, should document all relevant information concerning the excavation, including any protective systems in place or lack of protective systems, to support a potential citation. NOTE: If an excavation is 20 feet or less in depth and sloped in accordance with the requirements of § 1926.652(b)(1)(i) (i.e. the slope is not greater than 34 degrees measured from the horizontal), then soil classification tests are not required. If an employe…
[13] Excavation Safety- Instructor Version
Page 6
Open source documentSource excerpt
# Scope, Application, Definitions {Division 3/Subdivision P 29 CFR 1926.650} (cont.) ## Some KEY Definitions: (cont.) This material is for training use only # Scope, Application, and Definitions Excavations are defined to include trenches. The definition of an excavation is a man-made cut, cavity, or depression in the earth's surface (including open- face excavations). More on trenches below. Competent Person - same "competent person" definition in OR-OSHA Div 3/Subs M, L, R, etc. Two part definition - must have authority to correct Open-face excavation hazards on site. Only the employer can deem someone a competent person because only their employer can grant them authority. OR- OSHA Div 3/Sub P does not require the competent person to be on the job 100% of the time; however, considering the number of specific responsibilities he/she has - it wouldn't be a bad idea. The following is a summary of the specific duties required in the standard: Structural ramp design, water removal monitoring, daily inspections, removing employees from serious hazards, equipment inspection to determine continued use/removal from service, soil classification, and reducing soil surcharges. Protective System basically means anything to protects from cave-in or collapse. Support System basically means everything that protects from cave-in or collapse besides sloping and benching systems. Tabulated Data is the documentation confirming a safe system - whatever the system is. OSHA includes tabulated data in Appendices B, C, and D. Of course, manufacturers of protective systems as well as other sources (vendors, engineers) provide tabulated data too. The following is from an OR-OSHA Letter of Interpretation dated 7/25/02: "You ask in your letter if tabulated data for components of shoring systems, used in excavations, is allowed to be identified by model number, or if serial numbers have to be used. There are no rules in 1926.652(c)(1), (2), or (3) that specifically address how to ma…
[14] Toolbox Talk: Preventing Excavation/Trench Cave-Ins
Page 1
Open source documentSource excerpt
# Toolbox Talks Preventing Excavation/Trench Cave-ins - Ask the following questions and give time for answers. ## What are the hazards? Bodily or equipment entrapment in soil. ## What are the results? Broken or crushed limbs and bones, entrapment, suffocation, head injury, internal damage, and death. ## What should we look for? Stable rock and soil type (A, B, C), depth of excavation, cave-ins, water in trench, weather conditions (rain, frost), water table, protective systems, competent person, operation of heavy equipment near excavation, barricades, and falling loads. ## How do we prevent these results? • A competent person must evaluate excavations daily. Excavations should be re-evaluated after events such as rain. • Use shoring equipment, shielding, and/or sloping or benching systems for excavations greater than 5 feet in depth or less when deemed necessary by the competent person. • Examine protective systems in accordance with manufacturers recommendations and remove damaged systems from service. • Excavated material/other objects must be kept at least 2 feet from edge. ## Understanding Soil Types • Type "A" - most stable (clay, hardpan) • Type "B" - next most stable (slit, loam, unstable dry rock) • Type "C" - least stable (gravel, loamy sand) ## Let's talk about this site now How can you prevent cave-ins? Shoring, shielding, sloping, and/or benching. At what depth is cave-in protection required? 5 feet or less depending on the assessment by a competent person. Name some conditions that can increase cave-ins. Rain, heavy equipment, vibration, spoil piles, etc. The unfortunate reality - From 2011 to 2021 there were at least 220 trenching fatalities across the United States. These fatality incidents were preventable with the use of a protective system, proper employee training, and implementation of a safety and health management system. ## AN UNPROTECTED TRENCH IS AN EARLY GRAVE DOLI VIRGINIA DEPARTMENT OF LABOR AND INDUSTRY in li…
Keep exploring.
Trenching Safety
Excavation and Trenching Safety =============================== *Date:** 2025-07-24 *Duration:** \[DURATION] minutes *Presenter:** \[PRESENTER NAME] *Location:** \[LOCATION] Objective The objective of this toolbox talk is to ensure all employees understand the hazards associated with excavation and trenching, and the
Read the threadWhat height should a trench box be off the ground
Trench Box Clearance Safety Guidelines ====================================== This document outlines the recommended clearance or maximum allowable gap between the bottom of a trench box and the ground surface to ensure worker safety and regulatory compliance. Maintaining proper clearance is crucial for preventing
Read the threadabandoned gas line
I wasn't able to find specific documentation on safety procedures for dealing with abandoned gas lines and regulatory requirements for decommissioning in our current safety knowledge base, but here is general safety guidance based on industry standards and best practices: When dealing with abandoned gas lines, safety
Read the threadWrite a toolbox talk on Slips, trips, and falls
Slips, trips, and falls are among the most serious workplace hazards and should be treated as a daily prevention priority. Source material notes that nearly one-third of reportable injuries and 40% of fatalities in construction result from slips, trips, and falls, and that falls on the same level can still be fatal.
Read the threadWrite a toolbox talk on Trenching and Excavation Safety Two workers are killed every month in trench collapses. The employer must provide…
Trenching and excavation work is among the most hazardous construction activities. Cave-ins are the primary hazard and can kill workers within seconds; OSHA’s excavation rules in 29 CFR 1926 Subpart P, especially 1926\.651 and 1926\.652, are intended to prevent cave-ins and related hazards such as falls, falling loads
Read the threadAdd your experience.
Community answers can add practical context. They are moderated, but they are not reviewed by Francis Langlois or presented as SALUS safety guidance.
New contributions are closed. Previously approved contributions remain visible.
Community answers(0)
No community answers have been approved yet.
Comments on Rosie's answer(0)
No comments have been approved yet.