Risk assessment for a fresh air handling unit (FAHU) replacement (US)
Reviewed by Julie Gunn, Head of Services, SALUS Safety
The question, as asked: Write a risk assessment for FAHU replacement
A person submitted this question to Rosie's free generator. The asker's identity is neither imported nor published.
Rosie's answer
Published by SALUSA suitable safe system of work for replacing a Fresh Air Handling Unit (FAHU) should begin with a task-specific risk assessment, coordination with the client/site operator, and a permit-to-work package covering isolation, lifting, work at height, electrical work, hot work if applicable, and any confined-space elements. The work area should be defined, access restricted, and the sequence planned so the unit is shut down, isolated, proved dead, mechanically secured, disconnected, removed, and replaced in a controlled order by competent persons. [1] [3] [5]
Key hazards to assess
- Electrical shock, arc/flash, unexpected energization, and induced or back-fed power
- Mechanical hazards from fans, belts, dampers, actuators, rotating parts, stored spring force, and moving sections
- Release of stored energy from pressurized pipework, steam/hot water/chilled water, pneumatics, hydraulics, and gravity
- Dropped objects, suspended loads, crane or hoist failure, and struck-by/crush hazards during lifting
- Falls from roofs, platforms, ladders, scaffolds, or aerial lifts, plus fragile surfaces and openings
- Manual handling injuries from ductwork, panels, motors, filters, coils, and awkward access
- Exposure to asbestos-containing materials in older insulation, boards, gaskets, coatings, or surrounding building fabric
- Refrigerant exposure, oxygen displacement, cold burns, toxic decomposition products, and environmental release if coils or connected systems contain refrigerant
- Hot work hazards if cutting, grinding, brazing, or welding is required
- Slip, trip, housekeeping, noise, sharp edges, weather, and restricted-access hazards
[7] [12] [13] For HVAC isolation and lockout/tagout, identify all energy sources before work starts: electrical supplies, local isolators, BMS/controls, interlocks, VFD feeds, standby supplies, actuators, dampers, fan rotation, and any connected water, steam, condensate, gas, compressed air, or refrigerant services. Shut down the FAHU, isolate each source with an energy-isolating device, apply personal locks and tags, release stored energy, block moving parts, and verify zero energy by test/try-out before touching conductors or mechanical components. Control-circuit buttons and selectors are not acceptable isolation points on their own. [9] [9] [14]
Where ducts, coils, or connected services could introduce hazardous energy or material, use positive isolation appropriate to the risk. For pipework or ducts carrying hazardous substances or pressure, do not rely on a single valve where complete isolation is required; use methods such as blanking/blinding, removing sections, or double block and bleed where necessary. Drain, vent, purge, and prove isolation before breaking connections. Secure dampers, fan impellers, and access doors against movement. [9] [9] [8]
Recommended work sequence
- Survey the FAHU location and access route; confirm structural capacity, dimensions, lifting path, weather exposure, and whether roof work, confined space entry, or hot work permits are needed.
- Review asbestos information, O\&M manuals, drawings, electrical schematics, and refrigerant/system details before intrusive work.
- Issue permits to work and brief all workers and contractors on hazards, controls, emergency arrangements, and stop-work criteria.
- Shut down the system in a controlled manner and notify affected occupants/users.
- Isolate and lock out all electrical and mechanical energy sources; drain, vent, and isolate connected services; verify zero energy.
- Establish exclusion zones below and around the work and lifting area with barricades and signage.
- Remove panels, filters, belts, motors, coils, duct connections, and fixings in a planned sequence to reduce weight and instability.
- Use suitable lifting equipment and a lifting plan to remove the old FAHU or modules; never allow anyone under suspended loads.
- Install the replacement unit, reconnect services, inspect supports/anchors, and verify guards, access panels, and drainage.
- Before re-energization, remove tools and temporary restraints, confirm all persons are clear, remove locks under procedure, test run, check rotation/airflow/vibration, and hand back the system.
[1] [13] [15] Electrical safety controls should include competent electrical persons, identification of all supplies, proving dead with an approved test instrument, insulated tools where appropriate, protection from exposed live parts nearby, and control of temporary power. If testing or commissioning requires energization, this should be separately planned, authorized, and minimized. Faulty electrical equipment must be removed from service, and equipment used in hazardous atmospheres or restricted spaces should be suitable, grounded, and, where needed, explosion-proof or low-voltage. [5] [14] [15]
Mechanical hazards during FAHU replacement include rotating fans, belts, pulleys, dampers, actuators, spring-loaded components, sharp sheet-metal edges, hot surfaces, and stored pressure. Controls should include full shutdown, LOTO, blocking against motion, securing moving parts, allowing hot components to cool, draining coils and pipework, and using cut-resistant gloves where appropriate. Good housekeeping is essential to prevent slips, trips, and falls during dismantling and installation. [12] [8] [11]
Lifting operations for the FAHU should be planned by a competent person and executed by trained operators/riggers using equipment with adequate capacity and inspection status. Confirm the weight and center of gravity of the unit or modules, lifting points, sling angles, route, landing area, and structural capacity of roofs or floors. Establish a no-go zone, use tag lines where appropriate, protect against falling objects, and never work under suspended loads. Inspect cranes, hoists, hooks, chains, wire rope, and synthetic slings before use, and do not exceed rated capacities. [13] [13] [17]
For work at height, use the safest practicable access method: fixed platforms, scaffold towers, MEWPs/aerial lifts, or ladders only for short-duration low-risk tasks where justified. A site-specific fall protection plan should identify all fall hazards, protection methods, overhead hazard controls, tool/material securing methods, and rescue arrangements. Workers in aerial lifts should use the required harness/lanyard arrangement, keep gates closed, stand on the platform floor, avoid overreaching, and not use ladders or planks in the basket. Stop work in high winds or adverse weather, and protect people below from dropped objects with barricades, toe boards, nets, or overhead protection. [16] [15] [13]
Manual handling risks are significant during FAHU replacement because components are often bulky, sharp-edged, and awkward in posture-constrained plant rooms or roofs. Reduce risk by breaking the unit into smaller modules where possible, using mechanical aids, team lifts, dollies/skates, and planned routes free of trip hazards. Avoid twisting while carrying, keep loads close to the body, and set realistic weight limits based on access and posture rather than weight alone. [7] [11]
Asbestos must be considered before disturbing any older insulation, gaskets, boards, fireproofing, duct insulation, floor tiles, or surrounding building materials. If asbestos-containing material is suspected, stop work until the material is identified. Sampling and assessment should be arranged by competent persons, and any removal or disturbance should follow the applicable asbestos control plan and legal requirements. Controls include restricting access, warning signage, wet methods, HEPA-filtered respiratory protection where required, suitable disposable protective clothing, approved tools/extraction, and compliant waste packaging and disposal. Dry sweeping and compressed air should not be used. [6] [6] [6]
Refrigerant considerations depend on whether the FAHU includes or is connected to refrigerant-containing coils or DX equipment. Before disconnection, identify the refrigerant type and quantity, isolate the system, and arrange recovery by trained and authorized personnel using suitable recovery equipment. Main hazards include pressure release, cold burns/frostbite, oxygen displacement in enclosed areas, and toxic decomposition products if refrigerant contacts flames or hot work. Ventilation should be maintained, ignition sources controlled, and cylinders secured and handled upright. If refrigerant release is suspected in an enclosed plant area, evacuate, ventilate, and prevent re-entry until the atmosphere is confirmed safe.
Permit-to-work controls should normally include, as applicable: LOTO/energy isolation permit, electrical permit, hot work permit, lifting plan/permit, roof or work-at-height permit, and confined-space permit if entry criteria are met. Permits should define the task, location, authorized persons, hazards, isolations, PPE, equipment, validity period, emergency contacts, and hand-back arrangements. Where contractors are involved, host employer and contractor coordination is essential. [1] [3] [5]
If any part of the FAHU replacement involves entry into a space meeting confined-space criteria, comply with permit-required confined-space controls: complete the permit, isolate all energy and connected lines, test the atmosphere before entry and as needed during occupancy, provide ventilation, maintain communication, station an attendant/safety standby outside, and ensure rescue arrangements are in place. Typical acceptable entry conditions include oxygen between 19\.5% and 23\.5% and flammable gas below 10% LEL. [14] [10] [2]
PPE typically required
- Hard hat
- Safety glasses or goggles; face shield for cutting/grinding or splash risk
- Cut-resistant and task-appropriate gloves; chemical-resistant gloves where needed
- Safety footwear with toe protection and slip-resistant soles
- Hearing protection where noise levels require it
- Hi-vis clothing where vehicle or lifting plant movement exists
- Fall-arrest harness/lanyard for MEWP or other specified fall-protection systems
- Respiratory protection selected to the hazard, such as dust/asbestos or refrigerant-related exposure, with fit testing and training where required
- Protective clothing/disposable coveralls where contamination, asbestos, or sharp/dirty work is present
[1] [5] [4] Emergency procedures should be briefed before work starts and matched to the hazards present. They should cover electrical shock, falls from height, dropped loads, fire, refrigerant release, asbestos disturbance, medical emergencies, and any confined-space rescue needs. Emergency contacts, first-aid arrangements, rescue equipment, communication methods, and access for emergency services should be confirmed. For confined spaces, rescue must not rely on improvised entry by unprotected coworkers; standby/rescue arrangements, retrieval equipment where needed, and trained responders should be in place before entry. [3] [8] [16]
From a compliance standpoint, the FAHU replacement should satisfy the core principles of both HSE-style and OSHA requirements: suitable and sufficient risk assessment; competent supervision and trained workers; safe isolation/LOTO; permit-to-work where required; safe access and fall protection; planned lifting operations; PPE based on hazard assessment; control of hazardous substances including asbestos and refrigerants; emergency preparedness; inspection of equipment; and coordination between host employer and contractors. In OSHA terms, this aligns particularly with hazardous energy control, permit-required confined spaces where applicable, fall protection, aerial lift safety, PPE hazard assessment, and safe lifting/struck-by prevention. In HSE terms, it aligns with risk assessment, safe systems of work, work at height, lifting operations, asbestos management, COSHH-style substance control, and contractor management. [4] [9] [16]
Sources used for this answer
[1] Confined Space Entry
Page 1
Open source documentSource excerpt
WORK SAFE KENTUCKY Free safety resources provided by KEMI HOME SAFETY RESOURCES SAFETY TRAINING SAFETY BLOG ABOUT KEMI CONTACT US O # Confined Space Entry ## Print a Sign-In Sheet | Spanish Version Coming Soon ## What is a Confined Space? The Occupational Safety and Health Administration (OSHA) permit- required confined space standard defines a confined space as a space that is large enough for an employee to enter, has restricted means of entry or exit, and is not designed for continuous employee occupancy. A permit-required confined space (permit space) is a confined space that presents or has the potential for hazards related to atmospheric conditions (toxic, flammable, asphyxiating), engulfment, conflagration, or any other recognized serious hazard. Regulations governing entry into confined spaces are specified by OSHA. You can find these regulations at 29 CFR 1910.146. Examples of confined spaces include ship compartments, missile fuel tanks, vats, silos, sewers, tunnels, and vaults. ## Hazards Confined Space Hazards Dangerous vapors and gases can accumulate in confined spaces. Fires, explosions, and physical hazards can also injure or kill an unprotected worker. Physical Hazards Physical hazards may result from mechanical equipment or moving parts, like agitators, blenders, and stirrers. Other physical hazards include heat and sound. Temperatures can build up quickly in a permit space and cause exhaustion or dizziness. Sounds may reverberate and make it hard to hear important directions or warnings. ## Oxygen Deficiency The primary hazard associated with confined spaces is oxygen deficiency. Oxygen may be reduced in a space either by displacement or consumption. Oxygen is displaced by other gases such as argon, nitrogen, r methane. Consumption may be caused by chemical reactions such as rusting, rotting, fermentation, or burning of flammable substances. ## Combustibility Fire and explosion are serious dangers in permit spaces because fumes and…
[2] Toolbox Talk: Aerial Lift Safety
Page 1
Open source documentSource excerpt
# AERIAL LIFT SAFETY ## WHAT IS AN AERIAL LIFT? According to OSHA, an aerial lift is any vehicle-mounted device used to elevate personnel, including: • Extendable boom platforms • Aerial ladders • Articulating (jointed) boom platforms . Vertical towers • Any combination of the above. Work from or around aerial lifts presents many significant hazards. These include Power line contact or contact with other overhead obstructions, falls from elevation, tip-overs, being ejected from the lift basket, structural failure of the lift, objects falling from the and striking persons below, causing injury. Injuries from aerial lift accidents can be devastating and life-threatening, life-altering, or fatal. When broken down by trade, electricians had the most deaths (25%), followed construction laborers (15% ), electrical power installers and repairers (13%), painters (8%), and carpenters (5%). lift Additionally, most falls/collapses/tip-overs were within the height category of 10-29 feet. Tip-overs comprised 44-46% of boom-lift falls and 56-59% of scissor-lift falls. Constructing and repairing activities were associated with fall/collapse/tip-over incidents. ## HAZARDS AND HAZARD PREVENTION TIPS WHEN OPERATING AERIAL LIFTS Falls: This is the most common cause f aerial lift fatalities. Severe injuries or deaths can result from falls. Falls from aerial lifts often occur from improper lift operation and/or not using adequate fall protection equipment. To prevent falls from aerial lifts: • Ensure that access gates or openings are closed • Stand firmly on the floor of the lift platform or bucket • Do not climb on or lean over guardrails • Do not use planks, ladders, other devices to extend the working position • Use a body harness with a tether or lanyard attached to the boom bucket If Tip-overs can occur if proper safety precautions are not followed when using aerial lifts. Ensure the ground a lift is traveling or positioned on is free from bumps, holes, depres…
[3] Lockout/Tagout Sample Forms: Evaluation, Procedures, and Permit
Page 9
Open source documentSource excerpt
# Equipment-Specific Hazardous Energy Control Evaluation and Certification (cont.) Enter name of your company here # Safety Permit for Hazardous Energy Control (Lockout/Tagout) Work Operations Date of work activity: <empty> Permit issued to: Authorized employee name: <empty> Title: <empty> Company name (if outside contractor): <empty> Contact number: <empty> Date/Time issued: <empty> Date/Time permit expires: <empty> Work activity: <empty> Machine/equipment description: <empty> Work location: <empty> Personal protective equipment (PPE), as required: (also circle specific types within the parentheses) [ ] Face shield [ ] Ear plugs [ ] Hard hat [ ] Safety glasses [ ] Ear muffs [ ] Hood (chemical, thermal) [ ] Safety goggles [ ] Suit (rubber, thermal, Tyvek) [ ] Safety harness & line [ ] Filtering facepiece/N95 [ ] Respirator (dust, vapor, combination, full-face, half-face) [ ] Gloves (thermal) [ ] Gloves (latex, neoprene, nitrile, PVC, rubber) [ ] Rubber boots [ ] Shoes (steel-toed, electrical safety, slip-resistant) [ ] Additional PPE required: <empty> Energy control devices, as required: (also circle applicable activities within the parentheses) [ ] Disconnect [ ] Blocks [ ] Accident prevention tags [ ] Valves (close, block, blind) [ ] Lock devices (individual, group) [ ] Grounding means [ ] Lines (bleeding, blanking/blinding) [ ] Other: <empty> Other safety considerations, as required: (also circle applicable items within the parentheses) [ ] Confined space (requires additional permit) [ ] Fire hazards (fire extinguisher, area free of combustibles) [ ] Restrict area (barricade, safety tape) [ ] Welding (sparks, shield arcs) [ ] Safe access (ladder, aerial device, scissor lift) [ ] Other: <empty> Approval: Signature: <empty> Print name/title (i.e., Safety Manager, Supervisor): <empty> Date: <empty> [ ] Job complete [ ] Job incomplete Notes: <empty> The authorized worker holds this permit during the work activity and returns it to the approver after wo…
[4] Occupational Safety and Health Standards (OSHA 29 CFR 1910) - 1910.146 App C - Examples of Permit-required Confined Space Programs
Page 5
Open source documentSource excerpt
# Occupational Safety and Health Administration (cont.) ## B. Entry Permit Required (cont.) Potential Hazards. The recognized hazards associated with cookers and dryers are the risk that employees could be: 1. Struck or caught by rotating agitator; 2. Engulfed in raw material or hot, recycled fat; 3. Burned by steam from leaks into the cooker/dryer steam jacket or the condenser duct system if steam valves are not properly closed and locked out; 4. Burned by contact with hot metal surfaces, such as the agitator shaft assembly, or inner shell of the cooker/dryer; 5. Heat stress caused by warm atmosphere inside cooker/dryer; 6. Slipping and falling on grease in the cooker/dryer; 7. Electrically shocked by faulty equipment taken into the cooker/dryer; 8. Burned or overcome by fire or products of combustion; or 9. Overcome by fumes generated by welding or cutting done on grease covered surfaces. Permits. The supervisor in this case is always present at the cooker/dryer or other permit entry confined space when entry is made. The supervisor must follow the pre-entry isolation procedures described in the entry permit in preparing for entry, and ensure that the protective clothing, ventilating equipment and any other equipment required by the permit are at the entry site. - Control of hazards. Mechanical. Lock out main power switch to agitator motor at main power panel. Affix tag to the lock to inform others that a permit entry confined space entry is in progress. Engulfment. Close all valves in the raw material blow line. Secure each valve in its closed position using chain and lock. Attach a tag to the valve and chain warning that a permit entry confined space entry is in progress. The same procedure shall be used for securing the fat recycle valve. Burns and heat stress. Close steam supply valves to jacket and secure with chains and tags. Insert solid blank at flange in cooker vent line to condenser manifold duct system. Vent cooker/dryer by opening access do…
[5] Confined Space Guide for General Industry
Page 59
Open source documentSource excerpt
# ATTACHMENT C # Confined Space Entry Permit Sample (Enhanced Title 8 Version) Permit valid for 8 hours only. All copies of permit will remain at job site until job is completed. Date: Time: Site location and description: Purpose of entry: NATURE OF CONFINED SPACE HAZARD Oxygen deficiency (less than 19.5%) Flammable gases/vapors above 10% of lower explosive limit (LEL) Mechanical hazards Oxygen over 23.5% Toxic gases or vapors greater than permissible exposure limit (PEL) Electrical shock Materials harmful to skin Electrical lockout Engulfment Valve out/isolation Other(s) BOLD DENOTES MINIMUM REQUIREMENTS TO BE COMPLETED AND REVIEWED PRIOR TO ENTRY PREPARATION COMPLETED DATE TIME Lock out/de-energize/try-out Line(s) broken/capped/blanked Secure area (post and flag) Breathing apparatus Resuscitator/inhalator Cleaned, drained, washed, & purged Ventilation for fresh air Emergency response team available Employees informed of specific hazards Procedures reviewed with each employee_ Atmospheric test in compliance Hot work permit attached (if required) Continuous monitoring required Other(s) REQUIREMENTS COMPLETED DATE TIME Full body harness w/ "D" ring Emergency escape retrieval equip. Lifelines Lighting (explosion-proof) Protective clothing (PPE) Respiratory equipment Specify Communication equipment Specify Rescue equipment Specify Rescue Service Phone# <table><tr><th>CONTINUOUS MONITORING</th><th>PERMISSIBLE</th><th>RECORD MONITORING RESULTS/TIME</th></tr><tr><td>TEST(S) TO BE TAKEN</td><td>ENTRY LEVEL</td><td></td></tr><tr><td>Percent of Oxygen</td><td>19.5% to 23.5%</td><td></td></tr><tr><td>Lower flammable limit</td><td>Under 10%</td><td></td></tr><tr><td>Carbon Monoxide</td><td>25 ppm</td><td></td></tr><tr><td>Aromatic Hydrocarbon</td><td>1 ppm - 5 ppm</td><td></td></tr><tr><td>Hydrogen Cyanide</td><td>4.7 ppm (S)</td><td></td></tr><tr><td>Hydrogen Sulphide</td><td>10 ppm* 15 ppm**</td><td></td></tr><tr><td>Sulphur Dioxide</td><td>2 ppm* 5 ppm**</td>…
[6] Confined Space Guide for General Industry
Page 55
Open source documentSource excerpt
# ATTACHMENT A # Hot Work Permit Sample (attach to Entry Permit) XYZ Company Date: <empty> Issue time: <empty> Expiration time: <empty> Location of permit space: <empty> Work tasks: <empty> Potential Hazards Authorized Workers O Toxic O Electrical Entrants: O Corrosive O Mechanical O Flammable/Explosive O Fire/heat Attendant(s): O Radioactive O Spills Fire/safety watch: O Energy release O Oxygen Enrichment - O Stored energy Procedures/Precautions: O Procedures O Communications O Entry permit O Ventilation O Training O CPR/first aid O Rescue plan O Sprinkler system in service O Charged fire hose O Surfaces wetted down O Shower/eyewash located Safety Equipment: O Hard hat O Eye protection O Hearing protection O Foot/hand protection O Protective clothing O SCBA O Respirator: <empty> O Tripod O Barricade/cones O Communication devices O First aid kit O Fire extinguisher O: <empty> Vessel Prep/Isolation: O Cleaning/purging O Ventilation O Signs/barriers O Lagging cloths/tarps O Lockout/tagout O Blanking/bleeding O Disconnect mechanical linkages O Secure moving parts O: <empty> O: <empty> O: <empty> Special Tools - O Low voltage - O Non-sparking - O Tools inspected for frayed/broken wires - O Lighting intrinsically safe Special Work Procedures - O Never bring gas cylinders or other large equipment into space - O Never block entry/exit with equipment - O Shut down during breaks or overnight - O Fire watch to remain 30 minutes after completion of hot work O Entry authorizer (name, title, date): <empty> Emergency contact: <empty> 52 2
[7] Confined Space - Program
Page 2
Open source documentSource excerpt
# Confined Space - Program (cont.) ## What is a Confined Space Hazard Assessment and Control Program? (cont.) - Development of an emergency plan complete with training and equipment in case an unforeseen situation occurs. - An emergency response system. - Reporting and investigating incidents related to work in confined spaces. - Record and documentation control. - Program review whenever there is a change in circumstances or at least annually, to identify program weaknesses and make any necessary changes to the program. More information about confined spaces is located in the OSH Answers documents Confined Spaces - Introduction and Confined Space - Atmospheric Testing. ## What is an Entry Permit System? An entry permit is an administrative tool used to document the completion of a hazard and risk assessment for each confined space entry. Someone fully trained and experienced in confined space work should complete the entry permit. Some jurisdictions require a permit for all confined space entries. An entry permit is required for confined spaces where the hazard and risk assessment determined that the measures to control the risk involve the following: - atmospheric monitoring, - isolation, - lockout, - ventilation, - safeguarding devices, - respiratory protection, or - any other control that needs to be verified and documented in the permit as required by the assessment. Before entering a confined space, an entry permit should be completed. It should contain at least the following information: - The length of time the permit is valid for. - The name(s) of the worker(s) that are authorized to enter the confined space. - The name(s) of the attendant(s) (safety watch). - The name of the supervisor responsible for the work. - The location and description of the confined space. Confined Space - Program CCOHS
[8] Toolbox Talk: Falling Objects
Page 1
Open source documentSource excerpt
# FALLING OBJECTS Date Posted: 01/30/2024 Each day, countless workplaces are subjected to the risk of falling objects. According to a recent survey conducted by the Center for Construction and Research and Training (CPWR), in 2022, falling/flying objects accounted for approximately 30% of injuries on construction sites. Falling objects from above cause severe injuries and account for fatalities every year. Falling object occur due to: incidents • A lack of hazard communication. • Improper storage of materials. • Improper protection of elevated storage areas. • Not moving or securing loads properly when protective headgear is not worn. • Improper housekeeping. Workers' most common injuries from falling objects are bruises, fractures, strains, and sprains. The objects that commonly fall range from large items such as roof trusses and steel beams to items such as fasteners and small hand tools. Understanding these hazards and implementing effective control measures is crucial in maintaining the safety of workers and bystanders alike. small ## COMMON FALLING OBJECT HAZARDS Tools, materials, and other objects can fall from roofs, cranes, and scaffolds, and even objects falling from lower levels, such as a truck bed or dolly, can lead to injuries. Several factors increase the risk of more severe injuries, including the object's shape and where on the body the person is struck. The height at which the object falls and the weight of the object are also extremely important, with injury severity increasing as the height and weight of the falling object increase. - of Objects during Work at Height: As workers perform tasks at elevated positions, items such • Dislodgement as tiles can be dislodged from a rooftop, causing hazards to those • Falling Objects due to Environmental Factors or Deterioration: Harsh weather conditions can lead to objects like scaffold planks cast off scaffolds in robust winds. Similarly, fixtures ductwork might fall from a ceiling due t…
[9] Construction Tool Box Reviews
Page 2
Open source documentSource excerpt
# Table of Contents # Aerial Lifts # Asbestos Aerial Lifts Asbestos Back Injuries Compressed Gases Concrete and Masonry Confined Spaces Cranes and Rigging Electrical Fall Protection Fire Prevention First Aid/Bloodborne Pathogens Flammable and Combustible Materials Fueling Hand and Portable Tools Hazard Communication Heat Illnesses Hexavalent Chromium Housekeeping Industrial Trucks (Forklifts) Ladders Lead Lightning Lockout/Tagout Material Handling Overhead Power Lines Personal Protective Equipment Recording and Reporting Scaffolding Silica Stairways Trenching Vehicles Welding, Cutting and Brazing Workplace Violence Work Zones Hazards: Falls that can result in broken bones or death. Aerial lifts: Vehicle-mounted aerial devices used to elevate personnel to job-sites above ground. Examples include extensible boom platforms, aerial ladders, articulating boom platforms, vertical towers and a combination of any such devices. Aerial equipment may be powered or manually operated and may or may not be capable of rotating about a vertical axis. ## Safe Practices: ➤ Test lift controls each day before use. ➤ Only authorized persons can operate the lift. ➤ Do not tie off to an adjacent pole, structure or equipment while working from an aerial lift. ➤ Stand firmly on the floor; do not sit or climb on the edge of the basket or use planks, ladders or other items for a work position. ➤ Wear a body harness (or restraining belt) and lanyard attached to the boom or basket. ➤ Do not exceed specified load limits. ➤ Set the brakes during use. ➤ Position outriggers on pads or solid surface. ➤ Use wheel chocks when on an incline. ➤ Do not move when boom is elevated in a working position with anyone in the basket, except for equipment that is specifically designed for this type of operation. ➤ Ensure boom platforms, primarily designed as personnel carriers, have both platform (upper) and lower controls. ➤ Ensure upper controls are within easy reach of the operator. ➤ Lo…
[10] Confined Space Permit Form
Page 3
Open source documentSource excerpt
# Confined Space Entry Assessment Form/Permit <table><tr><th colspan="6">Preparation</th></tr><tr><td>Yes</td><td>N/A</td><td></td><td>Yes</td><td>N/A</td><td></td></tr><tr><td></td><td></td><td>Entry area free of debris and objects</td><td></td><td></td><td>No compressed cylinders in space</td></tr><tr><td></td><td></td><td>Warning barriers and signs in place</td><td></td><td></td><td>Host employer and/ or contractor notified</td></tr><tr><td></td><td></td><td>Atmospheric monitoring conducted</td><td></td><td></td><td>Entry and emergency procedures reviewed</td></tr><tr><td></td><td></td><td>Other hazards identified and isolated</td><td></td><td></td><td>Personnel have been trained</td></tr><tr><td></td><td></td><td>Hot work permitted</td><td></td><td></td><td>Personnel informed of potential hazards</td></tr><tr><td></td><td></td><td>Energy sources isolated/locked out</td><td></td><td></td><td>Electrical equipment is grounded</td></tr><tr><td></td><td></td><td>Confined space drained and flushed</td><td></td><td></td><td></td></tr></table> <table><tr><th></th><th></th><th colspan="4">Equipment Required</th></tr><tr><td colspan="3">Yes N/A</td><td>Yes</td><td>N/A</td><td></td></tr><tr><td></td><td></td><td>Forced air or exhaust ventilation</td><td></td><td></td><td>Non-sparking tools used</td></tr><tr><td></td><td></td><td>Ground fault interrupters (GFCI)</td><td></td><td></td><td>Low voltage lighting used</td></tr><tr><td></td><td></td><td>Retrieval Equipment</td><td></td><td></td><td>Equipment rated for explosive atmospheres</td></tr><tr><td></td><td></td><td>Fire Extinguishers</td><td></td><td></td><td>Communication Equipment</td></tr></table> <table><tr><th colspan="6">Personal Protective Equipment Required</th></tr><tr><td>Yes</td><td>N/A</td><td></td><td>Yes</td><td>N/A</td><td></td></tr><tr><td></td><td></td><td>Hard Hat</td><td></td><td></td><td>Protective Clothing</td></tr><tr><td></td><td></td><td>Eye/Face Protection</td><td></td><td></td><td>Hearing Pro…
[11] Fall Protection Work Plan
Page 1
Open source documentSource excerpt
Washington State Department of Labor & Industries Division of Occupational Safety and Health # Fall Protection Work Plan WAC 296-880-[redacted postal code]: You must develop and implement a written fall protection work plan including each area of the work place where the employees are assigned and where fall hazards of 10 feet or more exist and be available on the job site for inspection by the department. Company Name Date Company Name:<empty> Date:<empty> Site Address:<empty> (If additional space is needed, use the back of the sheet.) Identify all fall hazards 10 feet or more above the ground or lower level. Check all that apply. [ ] Open-sided floors [ ] Openings [ ] Leading edge work [ ] Decks/Balconies [ ] Roof [ ] Mobile lift work [ ] Hole [ ] Skylights Methods of fall protection to be used: (LSO = Low Slopes Only. Low Slope = 4 x 12 or less) [ ] Personal fall arrest system [ ] Safety watch system (LSO) [ ] Warning line system (LSO) [ ] Catch platform [ ] Positioning device system [ ] Safety net [ ] Covers [ ] Horizontal life lines [ ] Vertical life lines & rope grab [ ] Personal fall restraint system [ ] Warning line with safety monitor (LSO) Name of safety watch or monitor (if used):<empty> Overhead Hazard Protection Methods [ ] Hard Hats [ ] Toe boards on guardrails [ ] Other:<empty> [ ] Overhead Hazard Signs [ ] Screens on guardrails [ ] Other:<empty> [ ] Debris Nets [ ] Barricade to control access to area Describe procedures for assembly, maintenance, inspection, disassembly of fall protection system to be used.:<empty> Describe procedures for handling, storage, and securing tools, equipment, and materials.:<empty> Describe methods of overhead protection for workers who may be in, or pass through work area.:<empty> Describe method for prompt rescue of employees in the event of a fall.:<empty> Employees who received fall protection training on the above site specific fall protection work plan. Name(s):<empty> Date:<empty> <empty> <empty> <e…
[12] Worker falls 28 feet from a rough terrain work platform.
Page 4
Open source documentSource excerpt
# SCAFFOLDS AND SCAFFOLD PLATFORMS, PART (cont.) - Rule 1243(9): - If an employee is elevated in a platform on a variable reach lift truck, a personal fall arrest system, including the anchorage required in Part 45. Fall Protection, being R 408.[redacted postal code] et seq., of the Michigan Administrative Code and Part 6. Personal Protective Equipment, being R408.[redacted postal code] et seq., of the Michigan Administrative Code, is required and shall be worn when an employee is elevated. - No fall protection provided or used while employee with material was located upon a scaffold platform 28 ft. above grade. Employee with unsecured window (56 ft. X 106 ft.) fell from scaffold platform. Fall resulted in a fatality. - Rule 1243(24): - The only tools that are permitted on the work platform are hand tools and portable powered tools. Materials and tools shall be secured to prevent displacement. The total weight of compressed gas cylinders shall not be more than 20 pounds. - Material (window) not properly secured to the scaffold platform. Employee exposed to the inadvertent movement of material (window 56" X 106"). Unsecured window and employee fell from the scaffold approximately 28 ft. Fall resulted in fatality. - Rule 1243(25): - A work platform shall not be used during high winds, electrical storms, snow, ice, sleet, or other adverse weather conditions that could affect the safety of the employees on the work platform or the operator of the truck. - Scaffold platform mounted upon the forks of a Skytrak 6036 extendible boom forklift. Scaffold in use during high wind conditions. Employee and unsecured window (56" X 106") fell from scaffold 28 ft. resulting in a fatality. ## SERIOUS: PERSONAL PROTECTIVE EQUIPMENT, PART 6, Rule 622(1): A helmet, as prescribed in R408.[redacted postal code], was not used to protect the employee where a hazard or risk of injury exists from falling or flying objects or particles or from other harmful contacts or exposures. No…
[13] Confined Space Entry Permit
Page 1
Open source documentSource excerpt
# Confined space entry permit Permit date: <empty> Work shift: [ ] 1st [ ] 2nd [ ] 3rd Expires: <empty> Time started: <empty> Permit space to be entered (name and location of space): <empty> Purpose of entry: <empty> ## Names of trained, authorized individuals Emergency contact information Entry supervisor: Emergency responder: Entry attendant: Contact person: Authorized entrants: Phone number: Authorized entrants: Time: ## Pre-entry checklist Do not enter this permit space until the following "needs action" conditions are corrected: <table><tr><th>OK</th><th>Needs action</th><th></th></tr><tr><td></td><td></td><td>Before entering the permit space, the supervisor or designee must notify the rescue team. IDLH conditions require at least one rescue team member located outside the space.</td></tr><tr><td></td><td></td><td>A minimum of two employees must be assigned to work involving permit space entry. One employee must remain outside the permit space at all times</td></tr><tr><td></td><td></td><td>The surrounding area must be surveyed to show that it is free of hazards such as drifting vapors from tanks, piping, sewers, or vehicle exhaust.</td></tr><tr><td></td><td></td><td>Those responsible for operation of the gas monitor have been trained.</td></tr><tr><td></td><td></td><td>Gas monitor calibration tests and functional test (fresh air calibration) have been performed this shift on the gas monitor. If so, by whom?</td></tr><tr><td></td><td></td><td>The atmosphere will be continuously monitored while the space is occupied, if required by entry procedure.</td></tr></table> <table><tr><th colspan="8">Pre-entry requirements</th></tr><tr><td>Requirements</td><td>Yes</td><td>No</td><td>N/A</td><td>Requirements</td><td>Yes</td><td>No</td><td>N/A</td></tr><tr><td>Lockout-tagout/de-energize</td><td></td><td></td><td></td><td>Hot work permit</td><td></td><td></td><td></td></tr><tr><td>Pipes(s) broken or capped or blanked</td><td></td><td></td><td></td><td>Fall …
[14] Confined Space Guide for General Industry
Page 43
Open source documentSource excerpt
# Hazard Controls (cont.) IS IT SAFE TO ENTER A CONFINED SPACE? # Hazard Controls <table><tr><th>96. What steps are necessary in order to safeguard workers against engulfment hazards?</th><th>In order to avoid engulfment hazards: Remove material prior to entry. • Institute isolation procedures to keep out any potential haz- ardous substances. • Wear full body harnesses and retrieval lines. • Allow entry only if entrant can be rapidly pulled out.</th></tr><tr><td>97. How can slips, trips,</td><td>In order to prevent slips, trips, and falls:</td></tr><tr><td>and falls be prevented?</td><td>• Practice good housekeeping. Residues, unnecessary scraps, debris, and water should be removed from the floor and work areas.</td></tr><tr><td></td><td>Keep ladders in good working order and ensure that proper ladder safety practices are followed.</td></tr><tr><td></td><td>Ensure that guardrails protect all open sides of elevated work areas.</td></tr><tr><td></td><td>Ensure that appropriate fall arrest equipment is provided and properly used where required.</td></tr><tr><td>98. What can be done to make the space safe from explosive hazards?</td><td>Aside from ventilating or taking other precautions to control hazardous atmospheres, remove all potential sources of ignition from the space. Institute a no-smoking rule and use only approved electrical equipment. Personal Protective Equipment and Tools</td></tr><tr><td>99. Who is responsible for pro- viding and using personal protective equipment (PPE)?</td><td>Employers are responsible for providing the proper PPE to their workers and for replacement and repairs as necessary. Employ- ers are also responsible for providing adequate training on the proper use of the equipment, and for enforcing its use and wear. Consult qualified persons, such as:</td></tr><tr><td>100. Who can provide assistance in the selection of PPE and equipment?</td><td>Industrial hygienists. Safety engineers. . Safety and health professionals. . Other trained …
[15] OSHA Letter of Interpretation | Permit Required Confined Space Isolation
Page 1
Open source documentSource excerpt
U.S. DEPARTMENT OF LABOR # Occupational Safety and Health Administration • Standard Number: 1910.146(b), 1926.1202 OSHA requirements are set by statute, standards and regulations. Our interpretation letters explain these requirements and how they apply to particular circumstances, but they cannot create additional employer obligations. This letter constitutes OSHA's interpretation of the requirements discussed. Note that our enforcement guidance may be affected by changes to OSHA rules. Also, from time to time we update our guidance in response to new information. To keep apprised of such developments, you can consult OSHA's website at https://www.osha.gov. November 12, 2021 Brian Monistere, P.E., CSP Professional Safety Services [redacted street address] #301 Flowood, MS [redacted postal code] Dear Mr. Monistere: Thank you for your letter to the Occupational Safety and Health Administration (OSHA), regarding permit required confined space (PRCS) entry requirements. In your letter, you seek clarification from OSHA on PRCS isolation methods. This letter constitutes OSHA's interpretation only of the requirements herein, and may not be applicable to any questions not delineated in your original correspondence. Your paraphrased questions, and our responses, follow. Background: An employer has installed a single knife gate valve equipped with a bleed valve at the bottom of the assembly. Sleeves or gaskets within the knife gate valve form a tight seal when the valve is closed. Two relevant definitions include: "Isolation" (29 C.F.R. § 1910.146(b)) means the process by which a permit space is removed from service and completely protected against the release of energy and material into the space by such means as: blanking or blinding; misaligning or removing sections of lines, pipes, or ducts; a double block and bleed system; lockout or tagout of all sources of energy; or blocking or disconnecting all mechanical linkages. "Energy isolating device" (29 C.F.R § 1…
[16] Healthy Workplaces: Electrical Contractors Industry Focus Group Report
Page 20
Open source documentSource excerpt
# Table 2. Health and safety concerns from focus group participants. <table><tr><th colspan="2">Broad List of Health and Safety Concerns</th><th>Prioritized List</th></tr><tr><td colspan="2">NECA Managers</td><td></td></tr><tr><td>Ladder hazards</td><td>Training (standardized)</td><td>Ladder hazards</td></tr><tr><td>Proper use of tools</td><td>Confined space</td><td>Energized work/LOTO</td></tr><tr><td>Energized work/LOTO</td><td>Hazardous materials</td><td>Back injury</td></tr><tr><td>Fleet safety</td><td>Back injury</td><td></td></tr><tr><td colspan="2">Non-Affiliated Managers (Group 1)</td><td></td></tr><tr><td>Falls</td><td>Trip hazards</td><td>Back injury</td></tr><tr><td>Back injury</td><td>Hand injury</td><td>Eye injury</td></tr><tr><td>Energized work</td><td>Eye injury</td><td>Hand injury</td></tr><tr><td>Punctures</td><td>Dust/fiberglass/PPE use</td><td></td></tr><tr><td colspan="2">Non-Affiliated Managers (Group 2)</td><td></td></tr><tr><td>Ladder hazards</td><td></td><td>Ladder hazards</td></tr><tr><td>Eye injury</td><td></td><td>Back injury</td></tr><tr><td>Back injury</td><td></td><td>Eye injury</td></tr><tr><td>Asbestos</td><td></td><td></td></tr><tr><td>Union Workers</td><td></td><td></td></tr><tr><td>Housekeeping hazards</td><td>Ladder hazards</td><td>Ladder hazards</td></tr><tr><td>Lack of fall protection</td><td>Trip hazards</td><td>Energized work/LOTO</td></tr><tr><td>Lifting</td><td>Illumination</td><td>Housekeeping hazards</td></tr><tr><td>Energized work/LOTO</td><td>PPE</td><td></td></tr><tr><td>Hazard analysis</td><td>Wire pulling</td><td></td></tr><tr><td>Non-Union Workers</td><td></td><td></td></tr><tr><td>Energized work/LOTO</td><td>Housekeeping hazards</td><td>Energized work/LOTO</td></tr><tr><td>Labeling circuits</td><td>Eye protection</td><td>Housekeeping hazards</td></tr><tr><td>Back/shoulder injuries</td><td>Dust Asbestos</td><td>Back injury</td></tr><tr><td>Ladder safety</td><td>Tool maintenance</td><td></td></tr><tr><td>Burns</td><t…
[17] Personal Protective Equipment (PPE) Guide
Page 18
Open source documentSource excerpt
# Hazard Assessment For PPE (cont.) ## Instructions: (cont.) Option 1 # PPE Hazard Assessment Certification Form *Name of work place: <empty> *Work place address: <empty> *Required for certifying the hazard assessment. Work area(s): <empty> *Assessment conducted by: <empty> *Date of assessment: <empty> Job/Task(s): <empty> Use a separate sheet for each job/task or work area *Required for certifying the hazard assessment. Use a separate sheet for each job/task or work area EYES: Work activities, such as: [ ] abrasive blasting [ ] sanding [ ] chopping [ ] sawing [ ] cutting [ ] grinding [ ] drilling [ ] hammering [ ] welding [ ] punch press operations [ ] other: <empty> Work-related exposure to: [ ] airborne dust [ ] flying particles [ ] blood splashes [ ] hazardous liquid chemicals [ ] intense light [ ] other: <empty> Can hazard be eliminated without the use of PPE? Yes [ ] No [ ] If no, use: [ ] Safety glasses [ ] Side shields [ ] Safety goggles [ ] Dust-tight goggles [ ] Shading/Filter (#<empty>) [ ] Welding shield [ ] Other: <empty> FACE: Work activities, such as: [ ] cleaning [ ] foundry work [ ] welding [ ] siphoning [ ] mixing [ ] painting [ ] pouring molten metal [ ] dip tank operations [ ] other: <empty> Work-related exposure to: [ ] hazardous liquid chemicals [ ] extreme heat/cold [ ] potential irritants: <empty> [ ] other: <empty> Can hazard be eliminated without the use of PPE? Yes [ ] No [ ] If no, use: [ ] Face shield [ ] Shading/Filter (#<empty>) [ ] Welding shield [ ] Other: <empty> HEAD: Work activities, such as: [ ] building maintenance [ ] confined space operations [ ] construction [ ] electrical wiring [ ] walking/walking under catwalks [ ] walking/workng under conveyor belts [ ] walking/workng under crane loads [ ] utility work [ ] other: <empty> Work-related exposure to: [ ] beams [ ] pipes [ ] exposed electrical wiring or components [ ] falling objects [ ] machine parts [ ] other: <empty> Can hazard be eliminated without the us…
Keep exploring.
rail construction
Rail Construction and Maintenance Safety ======================================== Document Number: \[SWP-NUMBER] Revision Date: \[DATE] Next Review Date: \[NEXT REVIEW DATE] Department: \[DEPARTMENT NAME] 1\. Scope This safe work procedure (SWP) outlines the safety requirements for all rail construction and maintenance
Read the threadWrite a pre-task plan for Daily safety briefing
A compliant pre-task plan and daily safety briefing should be completed before work starts and updated whenever conditions, scope, personnel, or controls change. The process should be site-specific and should use a documented job hazard analysis (JHA/JSA) to break the work into steps, identify hazards for each step
Read the threadPouring concrete
Critical Safety Procedures for Concrete Pouring Operations ========================================================== Concrete pouring operations present various safety hazards that require strict adherence to safety procedures. This document outlines critical safety measures, including hazard assessments, PPE
Read the threadline break safe work procedure
Safe Work Procedure: Line Breaking Operations ============================================= Document Number: \[SWP-NUMBER] Revision Date: \[DATE] Next Review Date: \[NEXT REVIEW DATE] Department: \[DEPARTMENT NAME] 1\. Scope This safe work procedure (SWP) outlines the necessary steps and safety precautions for safely
Read the threadAdd your experience.
Community answers can add practical context. They are moderated, but they are not reviewed by Francis Langlois or presented as SALUS safety guidance.
New contributions are closed. Previously approved contributions remain visible.
Community answers(0)
No community answers have been approved yet.
Comments on Rosie's answer(0)
No comments have been approved yet.