Published by SALUSNaturally Occurring Radioactive Material (NORM/N.O.R.M.S.) Handling ===================================================================
Document Number: \[SWP-NUMBER]
Revision Date: \[DATE]
Next Review Date: \[NEXT REVIEW DATE]
Department: \[DEPARTMENT NAME]
1\. Scope
This Safe Work Procedure applies to the identification, handling, temporary storage, contamination control, decontamination, monitoring, packaging, transport preparation, and disposal of naturally occurring radioactive material (NORM/N.O.R.M.S.) and NORM-contaminated equipment, dust, residues, and waste generated during industrial activities. It is intended for workplaces where NORM may be encountered, including mineral extraction and processing, metal recycling, waste management, phosphate fertilizer production, forestry products and thermal electricity facilities, tunneling and underground workings, and water treatment facilities using sorptive media or ion-exchange resins. The procedure is limited to routine NORM handling and contamination-control activities performed by trained personnel; higher-risk tasks such as major decontamination, source recovery, unusual contamination events, or work involving elevated radiation levels must only be performed by personnel with appropriate radiation safety training and authorization. This procedure does not replace site-specific radiation protection programs, regulatory requirements, or emergency response plans, and it must be used together with applicable permits, monitoring programs, and waste-disposal requirements.
2\. Definitions
Naturally Occurring Radioactive Material (NORM) Radioactive material containing naturally occurring radionuclides such as uranium, thorium, potassium, and their decay products. NORM may be present at low levels in the earth’s crust but can become concentrated through industrial processing, increasing exposure potential. [1] [1]
Contamination The presence of radioactive material on surfaces, equipment, clothing, skin, or in the work area where it can be spread by contact, dust generation, or improper handling. Contamination control focuses on preventing spread and removing radioactive residues safely. [3] [6]
Occupational exposure Exposure received by a worker in the course of employment where duties involve radiation or radioactive material, including work in restricted areas or areas where NORM contamination may be present. [2]
Personnel monitoring The assessment of a worker’s radiation dose using wearable monitoring devices, bioassay, or survey data to verify exposure control and compliance with dose limits. [2]
ALARA A radiation protection principle meaning exposures should be kept as low as reasonably achievable by using time, distance, shielding, contamination control, and work planning. [3] [3]
3\. Responsibilities
3\.1 Supervisors
- Ensure a pre-job hazard assessment is completed before NORM work begins, including identification of likely contamination sources, exposure pathways, required controls, and emergency arrangements. Supervisors must verify that the work plan reflects the actual site conditions and that the task is stopped if conditions change or if unexpected contamination is discovered. [14]
- Assign only trained and authorized workers to handle NORM, contaminated equipment, or contaminated waste. Supervisors must ensure workers understand radiation hazards, contamination controls, decontamination methods, and the limits of their authorization. [1]
- Ensure radiation surveys, contamination checks, and personnel monitoring are performed as required, and that calibrated survey instruments and dosimetry are available before work starts. Supervisors must review results and take immediate corrective action if readings indicate elevated exposure or contamination. [6]
- Maintain controlled access to NORM storage and work areas, enforce housekeeping and dust suppression measures, and ensure contaminated materials are packaged, labeled, and transferred to authorized disposal or processing facilities without stockpiling. [1]
- Ensure incidents, abnormal survey results, contamination events, damaged containers, or suspected overexposures are reported immediately and investigated, and that corrective actions are documented and communicated to the workforce. [4]
3\.2 Workers
- Follow all radiation safety instructions, site rules, and permit conditions; attend required training and pre-job briefings; and stop work immediately if controls are missing, damaged, or ineffective. [1]
- Wear the required PPE correctly, keep it clean and serviceable, and do not remove PPE until contamination checks confirm it is safe to do so. Workers must not eat, drink, smoke, chew, or store food in NORM-controlled areas. [1]
- Use dust-minimizing work practices, maintain distance from the source where practical, and minimize time spent in contaminated areas. Workers must avoid cutting, grinding, polishing, or other activities that can generate airborne contamination unless specifically authorized and controlled. [1]
- Report damaged containers, unusual dust, elevated survey readings, contamination on skin or clothing, spills, leaks, or any suspected exposure immediately to the supervisor and follow decontamination and emergency instructions without delay. [6]
- Cooperate with personnel monitoring, contamination surveys, bioassay requirements if assigned, and recordkeeping requirements, including returning dosimeters on schedule and participating in post-job contamination checks. [6]
3\.3 Health and Safety Representative
- Participate in hazard assessments, workplace inspections, and review of control measures to verify that radiation protection practices are effective and practical for the task being performed. [12]
- Review incident trends, near misses, contamination events, and monitoring results to identify recurring weaknesses in work planning, housekeeping, PPE selection, or decontamination practices. [11]
- Support worker consultation, reinforce reporting expectations, and verify that corrective actions are implemented and communicated after incidents or abnormal survey findings. [5]
4\. Potential Hazards and Risks
| Hazard | Risk | Control Measures |
|---|---|---|
| Airborne NORM dust generated during handling, cutting, grinding, cleaning, or transfer of contaminated material [1] [1] [3] | Inhalation of radioactive dust leading to internal exposure, contamination of respiratory tract, and increased long-term cancer risk. | Eliminate or minimize dust-generating activities where possible. Use wet methods, local containment, and controlled handling techniques. Prohibit cutting, grinding, and polishing unless specifically authorized and controlled. Wear appropriate respiratory protection when engineering and administrative controls cannot adequately prevent inhalation exposure. |
| Contaminated surfaces, tools, clothing, and equipment [1] [1] [7] | Spread of radioactive contamination to workers, vehicles, clean areas, and the environment. | Establish designated contaminated zones and controlled access. Inspect and survey equipment before removal from the work area. Decontaminate equipment and surfaces using approved methods, and check all workers for contamination before leaving the work area. Package and label contaminated items for authorized disposal or storage. |
| External radiation exposure from concentrated NORM residues, scale, sludge, or contaminated equipment [3] [3] [9] | Increased occupational dose from prolonged proximity to radioactive material. | Apply ALARA principles by minimizing time near the source, maximizing distance, and using shielding where appropriate. Restrict access to the work area, post warning signs where required, and use calibrated survey instruments to verify dose rates before and during work. |
| Improper storage or unsecured transport of NORM-contaminated material [7] [7] | Loss of control, unauthorized access, accidental release, tampering, or contamination during transport. | Store radioactive material in locked, physically secured containers or designated storage areas. Secure transport packages in vehicles to prevent movement or unauthorized removal. Ensure packages are labeled, marked, and accompanied by appropriate shipping papers when transport is required. |
| Inadequate personnel monitoring or failure to detect contamination before leaving the work area [6] [6] [1] | Undetected exposure or spread of contamination beyond the controlled area. | Issue and require personal dosimetry where applicable, perform routine contamination surveys, and conduct exit contamination checks before workers leave the controlled area. Maintain records of monitoring results and investigate abnormal readings immediately. |
| Waste accumulation and poor disposal practices [1] [1] | Stockpiling of contaminated waste, increased exposure, and environmental release. | Segregate NORM waste, label it clearly, and transfer it promptly to a facility authorized to accept contaminated materials. Maintain waste records and avoid unnecessary accumulation of contaminated materials on site. |
| Damaged sealed source, ruptured container, or unexpected high radiation reading [6] [7] | Potential acute exposure, contamination spread, and need for emergency response. | Stop work, isolate the area, notify the supervisor, and prevent entry. Use trained radiation safety personnel to assess the scene, determine contamination boundaries, and implement decontamination and protective measures. Do not attempt unauthorized repairs or source manipulation. |
5\. Personal Protective Equipment (PPE)
Personal protective equipment is the last line of defense and must be selected to match the contamination, inhalation, and splash hazards identified in the job hazard analysis. PPE does not replace engineering controls, contamination control, or good work practices; it must be used together with exposure minimization, controlled access, and monitoring.
- Impermeable Coveralls or Disposable Protective Clothing: Wear impermeable or disposable coveralls that provide full-body coverage and reduce the transfer of radioactive dust or residues to personal clothing and skin. Clothing should fit properly, allow safe movement, and be removed as contaminated waste or decontaminated according to site procedures after use. [1]
- Use disposable garments when contamination is expected to be difficult to remove.
- Inspect seams, closures, and cuffs before use.
- Remove clothing carefully to avoid spreading contamination.
- Chemical-Resistant Boots or Boot Covers: Use boots or boot covers that are resistant to contamination and easy to decontaminate or dispose of. Footwear must prevent tracking radioactive material out of the controlled area and should be dedicated to the work zone when practical. [1]
- Select slip-resistant soles suitable for the work surface.
- Inspect for tears, cracks, or contamination before entry and before exit.
- Decontaminate or dispose of footwear in accordance with site rules.
- Protective Gloves: Wear gloves appropriate to the contamination and chemical conditions present. Gloves should provide a secure wrist seal, maintain dexterity for handling tools and samples, and be changed immediately if torn, heavily contaminated, or compromised. [1]
- Use double-gloving where contamination potential is elevated.
- Avoid touching clean surfaces with contaminated gloves.
- Remove gloves before touching personal items or controls outside the work zone.
- Protective Eyewear or Face Protection: Use protective eyewear or face protection to prevent contamination of the eyes and face during dusty work, decontamination, or transfer operations. Eye protection should fit securely and be compatible with respirators and other PPE. [1]
- Select sealed goggles where splash or dust exposure is likely.
- Use face shields when there is a risk of splatter during decontamination.
- Clean or dispose of eye protection after use if contaminated.
- Respiratory Protection: Use respiratory protection when airborne contamination cannot be adequately controlled by engineering or work-practice controls. Respiratory protection must be selected, fitted, and used in accordance with the site respiratory protection program and the contamination hazard present. Negative-pressure, positive-pressure, or supplied-air devices may be required depending on the exposure scenario and regulatory requirements. [1]
- Perform fit testing and user seal checks before use.
- Do not use a respirator with facial hair or damaged seals.
- Remove and replace filters or cartridges according to the program and contamination conditions.
- Personal Dosimeter: Wear assigned personnel monitoring equipment whenever required by the radiation protection program. Dosimeters must be worn by one person only, kept in the correct location on the body, and returned for processing on schedule so that occupational exposure can be tracked accurately. [6]
- Do not share dosimeters.
- Store dosimeters away from heat, contamination, and radiation sources when not in use.
- Report lost, damaged, or unreadable dosimeters immediately.
Inspect PPE before each use for tears, punctures, degraded seals, contamination, missing components, and fit issues. Replace disposable PPE when contaminated or damaged, and clean reusable PPE only using approved decontamination methods. Maintain PPE in a sanitary and reliable condition, and remove from service any item that cannot be effectively decontaminated or repaired. [13] [1]
6\. Equipment and Tools
Equipment and monitoring devices used for NORM work must be suitable for the contamination level, calibrated where required, and inspected before use. Defective or uncalibrated equipment must not be used because it can lead to missed contamination, inaccurate dose assessment, or uncontrolled exposure.
- Calibrated Radiation Survey Meter: Use a calibrated and operable survey meter capable of detecting beta and gamma radiation to assess work areas, containers, tools, and vehicles before, during, and after NORM handling. The instrument must be suitable for the expected dose range and contamination conditions. [7]
- Verify calibration status before use.
- Check battery condition and response with a source check if required by site procedure.
- Remove from service if readings are unstable or the instrument fails a functional check.
- Contamination Survey Supplies: Use wipes, swipe media, sample containers, labels, and documentation forms to perform contamination surveys and record results. Supplies must be clean, compatible with the material being sampled, and handled to prevent cross-contamination. [9]
- Use separate materials for clean and contaminated areas.
- Label samples immediately after collection.
- Follow chain-of-custody or site documentation requirements where applicable.
- Designated Storage Containers or Waste Packages: Use locked, physically secured containers or packages for temporary storage and transfer of NORM-contaminated materials and waste. Containers must be compatible with the waste form, clearly labeled, and maintained to prevent tampering, leakage, or unauthorized access. [7]
- Inspect closures, seals, and labels before use.
- Do not overfill containers.
- Keep incompatible materials segregated.
- Remote Handling Tools: Use remote handling tools where practical to increase distance from contaminated material and reduce direct contact. Tools must be appropriate for the load, inspected for damage, and kept clean to avoid spreading contamination. [6]
- Verify handles, grips, and moving parts before use.
- Do not use improvised tools for radioactive material handling.
- Decontaminate tools after use or segregate them as contaminated equipment.
- Decontamination Equipment and Materials: Provide approved cleaning materials, absorbents, containment supplies, and waste bags or drums for controlled decontamination of surfaces, tools, and PPE. Decontamination materials must be selected to avoid spreading contamination and must be disposed of as radioactive waste when contaminated. [1]
- Use only approved cleaning agents and methods.
- Contain runoff and residues.
- Survey the area after decontamination to confirm effectiveness.
Inspect survey meters, remote handling tools, storage containers, and decontamination equipment before each use and at the frequency required by the radiation protection program. Remove defective equipment from service immediately, document the defect and repair, and do not return the item to use until it is verified safe and functional. Maintain calibration records, inspection logs, and maintenance records for the required retention period. [7] [7]
7\. Pre-Job Requirements
7\.1 Training and Competency
Training and Competency: Only workers who have received radiation safety training appropriate to the task may handle NORM or contaminated materials. Training must cover the difference between radiation and contamination, internal and external exposure, biological effects, ALARA principles, survey instrument use, contamination control, emergency actions, and waste handling. Workers assigned to higher-risk or nonroutine tasks must receive task-specific instruction and demonstrate competence before working independently. [3] [1]
7\.2 Pre-Job Briefing
Pre-Job Briefing: Conduct a documented pre-job briefing before each NORM task to review the scope of work, identified hazards, control measures, PPE, monitoring requirements, contamination boundaries, waste handling, emergency actions, and stop-work authority. The briefing must confirm that workers understand the work sequence, communication methods, and the steps the employer has taken to protect them from exposure. [1] [13]
7\.3 Work Area Preparation
Work Area Preparation: Prepare the work area by establishing controlled access, posting warning signs where required, segregating clean and contaminated zones, and arranging containers for waste and contaminated tools. Verify that ventilation, dust suppression, lighting, and housekeeping arrangements are adequate for the task. Remove unnecessary personnel and materials from the area before work begins. [1] [1] [9]
8\. Safe Work Procedure Steps
- 1\. Confirm Authorization and Review the Job Plan: Verify that the task is authorized, that the crew is trained for NORM work, and that the work plan matches current site conditions. Review the hazard assessment, required controls, PPE, monitoring requirements, waste routes, and emergency actions before starting. If the task involves unusual contamination, elevated readings, or nonroutine work, stop and obtain radiation safety direction before proceeding. [1]
- Confirm scope, boundaries, and stop-work authority.
- Review any permits, access restrictions, and disposal requirements.
- Ensure all required equipment and PPE are available and serviceable.
- 2\. Establish the Controlled Area: Set up the work zone so that contaminated material is isolated from clean areas and unauthorized entry is prevented. Post warning signs where required, define entry and exit points, and place containers, survey instruments, and decontamination supplies at the boundary. Keep food, drink, and smoking materials out of the area at all times. [1]
- Restrict access to essential personnel only.
- Use barriers, tape, cones, or other physical controls as needed.
- Maintain clear housekeeping to reduce spread of dust and residues.
- 3\. Inspect PPE, Tools, and Monitoring Devices: Before entering the work area, inspect all PPE, survey meters, remote handling tools, containers, and decontamination supplies. Confirm that survey instruments are calibrated and operable, dosimeters are assigned correctly, and any damaged or defective equipment has been removed from service. Do not begin work until all required items are ready and verified. [7]
- Check PPE for tears, degraded seals, and fit issues.
- Verify survey meter function and calibration status.
- Confirm dosimeter assignment and wear location.
- 4\. Don Required PPE and Perform Entry Controls: Put on the required PPE before entering the controlled area and ensure all closures, seals, and respirator checks are completed. Use respiratory protection when airborne contamination is possible or when dust cannot be adequately controlled by other means. Enter the work area only after the supervisor confirms that controls are in place and the crew understands the task sequence. [1]
- Perform respirator seal checks or fit checks as required.
- Avoid touching clean surfaces with contaminated gloves or clothing.
- Keep PPE on until exit contamination checks are complete.
- 5\. Handle NORM Using Dust-Control and ALARA Practices: Handle material carefully to avoid generating dust or spreading contamination. Use wet methods, enclosed transfer methods, or remote handling tools where practical. Keep time in the contaminated area as short as possible, maximize distance from the source, and use shielding if appropriate. Do not cut, grind, polish, or otherwise disturb material unless the activity has been specifically assessed and controlled. [1]
- Move slowly and deliberately to avoid spills and airborne release.
- Keep containers closed when not actively transferring material.
- Use shielding only when it is suitable for the material and task.
- 6\. Perform Radiation and Contamination Monitoring: Conduct surveys of the work area, tools, containers, and personnel at the frequency required by the job plan and whenever conditions change. Use calibrated instruments to identify elevated radiation levels and contamination. Record readings, compare them to expected background or site action levels, and stop work if abnormal results are found. [6]
- Survey before work, during work as needed, and after completion.
- Check the exterior of containers and transport packages before movement.
- Monitor workers before they leave the controlled area.
- 7\. Package, Label, and Segregate Contaminated Material: Place contaminated material, disposable PPE, wipes, absorbents, and removed equipment into designated containers or waste packages. Keep containers closed, labeled, and physically secured. Segregate contaminated items from clean materials and prevent overfilling or leakage. Prepare shipping or transfer documentation when material is moved off site. [7]
- Use only approved containers for the waste form.
- Label containers clearly as radioactive or contaminated material as required by site rules.
- Do not mix incompatible waste streams unless authorized.
- 8\. Decontaminate Personnel, Tools, and Work Surfaces: After the task is complete, decontaminate tools, equipment, and work surfaces using approved methods. Remove contamination from personnel in the designated decontamination area and re-survey to confirm effectiveness. If contamination cannot be removed safely, isolate the item, label it, and treat it as contaminated waste or contaminated equipment. [1]
- Use approved cleaning methods that do not spread contamination.
- Collect residues and cleaning materials as radioactive waste.
- Repeat surveys until the area meets release criteria or supervisor direction.
- 9\. Remove PPE and Exit the Controlled Area: Remove PPE in the correct sequence to avoid self-contamination and spread of radioactive material. Perform final contamination checks on hands, clothing, footwear, and any reusable equipment before leaving the controlled area. Dispose of single-use PPE as contaminated waste and store reusable items for decontamination or controlled reuse. [1]
- Remove outer gloves and disposable items first, unless site procedure specifies otherwise.
- Avoid touching the face, hair, or personal items during doffing.
- Wash hands and exposed skin after exit if contamination controls require it.
- 10\. Complete Records and Report Findings: Document survey results, contamination checks, waste quantities, equipment defects, dosimeter issues, and any unusual conditions encountered during the job. Report abnormal readings, contamination events, spills, damaged containers, or suspected exposures immediately through the site reporting process. Retain records according to the radiation protection program and regulatory requirements. [6]
- Record date, location, personnel involved, and key readings.
- Note any corrective actions taken during the job.
- Escalate unresolved issues to radiation safety personnel.
9\. Precautions and Safety Measures
- Do not eat, drink, smoke, chew, or store food in NORM-controlled areas. - Provide designated clean areas for breaks and ensure workers wash hands before entering those areas. [1]
- Minimize time in contaminated areas and maximize distance from the source whenever practical. - Plan the work so that tools, containers, and personnel are staged efficiently and unnecessary re-entry is avoided. [1]
- Use shielding where appropriate to reduce dose rates from concentrated material. - Only use shielding that is suitable for the material, geometry, and task, and verify that it does not create additional handling hazards. [1]
- Prevent dust generation and airborne spread of contamination. - Avoid cutting, grinding, polishing, dry sweeping, or compressed-air cleaning unless specifically authorized and controlled by the radiation protection program. [1]
- Keep contaminated materials and waste in a designated, access-controlled area until disposal or transfer. - Use clear labels, secure storage, and routine housekeeping to prevent accumulation and unauthorized access. [1]
10\. Emergency Procedures
10\.1 General Emergency Response
If an emergency occurs, stop work immediately, warn nearby personnel, isolate the area, and notify the supervisor and radiation safety personnel. Do not attempt cleanup or repair unless you are trained and authorized to do so. Use the site emergency plan to determine evacuation, medical response, contamination control, and notification requirements. If contamination may have spread, prevent entry and establish boundaries until trained personnel complete the assessment. [6] [6]
10\.2 Specific Emergency Scenarios
- Suspected overexposure or unexpectedly high radiation reading: Stop the task, withdraw personnel from the immediate area, and prevent re-entry. Notify the supervisor and radiation safety personnel, then perform a controlled survey to confirm the reading and identify the source. Review dosimetry and work conditions, and do not resume work until the hazard is understood and controls are corrected. [1]
- Contamination on skin, clothing, or personal items: Stop work, avoid spreading contamination, and move to the designated decontamination area. Remove contaminated outer clothing and follow approved decontamination steps for skin and equipment. Re-survey the person and items before allowing them to leave the controlled area. [1]
- Spill, leak, or damaged container with visible contamination: Isolate the area, stop movement of material, and prevent dust generation. Notify the supervisor immediately and have trained radiation safety personnel assess the extent of contamination using suitable survey instruments. Collect and package contaminated materials using approved methods and send them to authorized disposal or processing facilities. [1]
- Fire, explosion, or other event affecting stored NORM waste: Evacuate the area if conditions are unsafe, notify emergency responders, and inform them that radioactive material may be involved. Do not disturb damaged containers unless directed by trained radiation safety personnel. After the scene is stabilized, perform contamination surveys and manage residues as radioactive waste. [7]
10\.3 Emergency Contact Information
Emergency contact information, site radiation safety contacts, medical response contacts, and regulatory notification numbers must be inserted by the employer or site administrator in the final controlled document.
Approved by: \[NAME AND POSITION]
Date: \[APPROVAL DATE]
Safety powered by SALUS
Sources used for this answer
[1] OSH Enforcement Procedures | CPL 02-02-073 - Inspection Procedures for 29 CFR 1910.120 and 1926.65, Paragraph (q): Emergency Response to Hazardous Substance Releases
Page 19
Open source documentSource excerpt
# TABLE OF CONTENTS (cont.) ## IX. Significant Changes. (cont.) (2) Any biological agent and other disease-causing agent which after release into the environment and upon exposure, ingestion, inhalation, or assimilation into any person, either directly from the environment or indirectly by ingestion through food chains, will or may reasonably be anticipated to cause death, disease, behavioral abnormalities, cancer, genetic mutation, physiological malfunctions (including malfunctions in reproduction) or physical deformations in such persons or their offspring; (3) Any substance listed by the U.S. DOT as a hazardous material under 49 CFR 172.101 and appendices; and (4) Hazardous waste which means a waste or combination of wastes defined in 40 CFR 261.3, or those substances defined as hazardous wastes in 49 CFR 171.8. 3. First Receiver. (not found in 1910.120(a)(3)). First receivers include hospital-based staff (e.g., triage, decontamination, medical treatment, and security) that receive and treat contaminated victims from mass casualty incidents. These personnel are removed from the site of the emergency and the point of release and do not need to be trained - or equipped - for control, containment, or confinement operations as is required for a HAZMAT team. First receivers are still considered to be part of an emergency response and will be required to wear appropriate PPE and be provided effective training based on the duties and functions to be performed. 4. Hazardous Substance, Radioactive Waste. The term "hazardous substance" as defined by 1910.120 includes radioactive waste in addition to hazardous waste, and should not be confused with the definition of hazardous chemical in 1910.1200, Hazard Communication, which specifically excludes any radioactive chemicals. - The U.S. Nuclear Regulatory Commission (NRC) has jurisdiction "inside the fence" at NRC licensed nuclear facilities for the risks involved with licensed radioactive materials, including emer…
[2] Nevada Administrative Code, Chapter 459 - Hazardous Materials (NAC-459)
Page 55
Open source documentSource excerpt
# GENERAL PROVISIONS (cont.) ## NAC 459.312 Transfer of material. (NRS 459.201) (cont.) 1. At a facility licensed pursuant to 10 C.F.R. Part 61 or equivalent regulations of an agreement state, even though it is not defined as low-level radioactive waste, if it meets the requirements (1) Operating and emergency procedures; - of NAĆ 459.313; or 2. At any disposal facility authorized to dispose of such material in accordance with any federal or state solid or hazardous waste law, including the Solid Waste Disposal Act, authorized pursuant to the Energy Policy Act of 2005, Public Law 109-058. (Added to NAC by Bd. of Health by R185-08, eff. 5-7-2010) as - NAC 459.313 Transfer or shipment of radioactive waste or by-product material for disposal at licensed land disposal facility. (NRS 459.201) 1. Transfers of low-level radioactive waste by any waste generator, waste collector or waste processor who ships low-level radioactive waste either directly or indirectly through a waste collector or waste processor to a licensed low-level radioactive waste land disposal facility are governed by the requirements of this section and NAC 459.8231 and Appendix G. 2. A licensee who ships radioactive waste intended for ultimate disposal at a licensed land disposal facility must document the information required on the Nuclear Regulatory Commission's Uniform Low-Level Radioactive Waste Manifest, and transfer the recorded manifest information to the intended consignee in accordance with the provisions of Appendix G. 3. Each manifest described in subsection 2 must include a certification by the waste generator as provided in section II of Appendix G. 4. Each person involved in the transfer for disposal or the disposal of radioactive waste, including, without limitation, the waste generator, waste collector, waste processor and disposal facility operator, r, shall comply with the requirements of section III of Appendix G. 5. A licensee who ships any by-product material speci…
[3] Nevada Administrative Code, Chapter 459 - Hazardous Materials (NAC-459)
Page 56
Open source documentSource excerpt
# GENERAL PROVISIONS (cont.) ## NAC 459.312 Transfer of material. (NRS 459.201) (cont.) (2) The difference between and requirements related to routine and nonroutine maintenance; and (3) Lockout procedures; (III) Routine maintenance; and (d) On-the-job training under the supervision of a radiation safety officer or a person who is authorized to use and supervise the use of radioactive material that involves the use of a fixed gauge which includes, without limitation, hands-on experience performing: (1) Operating procedures; (2) Practical tests which involve following emergency procedures; (3) Routine maintenance; and (4) Lockout procedures; and (e) An evaluation by a management official concerning whether the proposed radiation safety officer is qualified to work independently with and is knowledgeable of the radiation safety aspects of each type of fixed gauge to be possessed by the applicant for the specific license or possessed by the licensee, as applicable. This evaluation may be accomplished by a written oral examination or by observation or 3. The classroom training required by subsection 2 may be in the form of lecture, videotape or self-study. 4. In addition to the training required by subsection 1, if the proposed radiation safety officer is appointed for a radiation safety program that includes nonroutine operations, the proposed radiation safety officer must have successfully completed a course of training in nonroutine operations related to fixed gauges provided by the manufacturer or distributor. As used in this subsection, "nonroutine operations" include, without limitation: (a) Repairs involving or potentially affecting components related to the radiological safety of the fixed gauge, including, without limitation, the source, source holder, source drive mechanism, shutter, shutter control or shielding; and (b) Any other activities during which personnel may receive doses of radiation exceeding safe limits, including, without limi…
[4] Nevada Administrative Code, Chapter 459 - Hazardous Materials (NAC-459)
Page 16
Open source documentSource excerpt
# GENERAL PROVISIONS (cont.) (Added to NAC by Bd. of Health, eff. 1-18-94) NAC 459.0517 "National Source Tracking System" defined. (NRS 459.201) "National Source Tracking System" means the mandatory tracking system for radiation sources in the United States established and administered by the Nuclear Regulatory Commission pursuant to 42 U.S.C. § 2210h. (Added to NAC by Bd. of Health by R149-07, eff. 1-30-2008) NAC 459.0518 "National Source Tracking Transaction Report" defined. (NRS 459.201) "National Source Tracking Transaction Report" means a report submitted to the National Source Tracking System. (Added to NAC by Bd. of Health by R149-07, eff. 1-30-2008) NAC 459.0519 "Nationally tracked source" defined. (NRS 459.201) "Nationally tracked source" has the meaning ascribed to it in 10 C.F.R. § 20.1003. (Added to NAC by Bd. of Health by R149-07, eff. 1-30-2008) NAC [Bd. 459.052 "Natural radioactivity" defined. (NRS 459.201) "Natural radioactivity" means radioactivity of naturally of Health, Radiation Control Reg. § 1.2.18, eff. 2-28-80] occurring nuclides. NAC 459.0525 "Naturally occurring or accelerator-produced radioactive material" defined. (NRS 459.030) "Naturally occurring or accelerator-produced radioactive material" includes naturally occurring radioactive material, including materials generated by accelerators used in subatomic particle physics research, and accelerator-produced radioactive material. The term does not include by-product, source or special nuclear material. (Added to NAC by Dep't of Human Resources by R137-01, eff. 5-30-2003) NAC 459.0527 "Negative pressure respirator" defined. (NRS 459.201) "Negative pressure respirator" means a respirator which the air pressure inside the facepiece negative during inhalation with respect to the ambient air pressure outside the respirator. (Added to NAC by Bd. of Health by R085-06, eff. 11-13-2006) NAC 459.053 "Nonstochastic effect" defined. (NRS 459.201) "Nonstochastic effect" means the effects on…
[5] Nevada Administrative Code, Chapter 459 - Hazardous Materials (NAC-459)
Page 4
Open source documentSource excerpt
# CHAPTER 459-HAZARDOUS MATERIALS (cont.) 459.3142 Industrial radiography. 459.3143 Radioactive material that involves use of portable gauge. 459.3144 Radioactive material that involves use of fixed gauge. 459.3145 Radioactive material that involves use of category 1 irradiators. 459.3146 Radioactive material that involves use of irradiators other than category 1 irradiators. 459.3147 Use of radioactive materials in academic research or other research and development. 459.3148 Radioactive material that involves use of gas chromatographs. 459.3149 Radioactive material that involves X-ray fluorescence. 459.315 Type A specific license of broad scope. 459.3151 Type B specific license of broad scope. 459.3152 Certain preparation of radioactive drugs in nuclear pharmacy for commercial distribution and redistribution. 459.3153 Use of sealed sources, tracers or field flood studies in well logging. 459.3154 Certain possession and production of radiochemicals using accelerator for transfer or distribution. Radiological Criteria for Termination of License 459.316 Definitions. 459.3164 "Critical group" defined. 459.3166 "Distinguishable from background radiation" defined. 459.3168 "Residual radioactivity" defined. 459.317 Applicability. 459.3172 Explanation of total effective dose equivalent to average member of critical group used. 459.3174 Minimization of contamination required for issuance of any license. 459.3176 Additional cleanup of decommissioned site. 459.3178 Property of decommissioned facility: Eligibility for release for unrestricted use. 459.318 Property decommissioned facility: Eligibility for release for restricted use. 459.3182 Property of decommissioned facility: Alternate criteria for release for restricted or unrestricted use. 459.3184 Notice to public; public comment. Standards for Protection Against Radiation 459.320 Purpose; applicability; reasonable effort required. 459.3205 Adoption by reference of certain provisions of federal regulations. 459.321 Devel…
[6] Nevada Administrative Code, Chapter 459 - Hazardous Materials (NAC-459)
Page 90
Open source documentSource excerpt
# GENERAL PROVISIONS (cont.) ## Radiation Safety Requirements for Well Logging (cont.) (III) The date on which the irretrievable source was abandoned; (IV) The name of the well owner or well operator, as appropriate; (V) The name of the well and the well identification number or other designation; (VI) An identification of the sealed source by radionuclide and quantity; (VII) The depth of the sealed source and depth to the top of the plug; and (VIII) An appropriate warning such as "DO NOT RE-ENTER THIS WELL." (Added 3. 3. A licensee shall retain a copy of the written A licensee to NAC shall by Bd. retain of Health, a copy of eff. the 9-6-88; written A 1-18-94) required by subsection 1 for 3 years after the completion of the well logging operation. - NAC 459.765 Labeling of components and containers; transportation of radioactive material. (NRS 459.201) 1. A licensee may not use a source, a source holder or a logging tool that contains radioactive material unless the smallest component that is transported as a separate piece of equipment with radioactive material inside bears a durable, legible and clearly visible marking or label. The marking or label must contain the radiation caution symbol specified in NAC 459.355 without the conventional color requirements, and the wording "CAUTION (or DANGER) RADIOACTIVE MATERIAL." 2. A licensee may not use a container to store radioactive material unless the container has securely attached to it a durable, legible and clearly visible label. The label must contain the radiation caution symbol specified in NAC 459.355 and the wording "CAUTION. (or DANGER.) RADIOACTIVE MATERIAL. NOTIFY CIVIL AUTHORITIES (or NAME OF COMPANY) IF FOUND." 3. A licensee may not transport radioactive material unless the material is packaged, labeled, marked and accompanied with appropriate shipping papers in accordance with regulations of the United States Department of Transportation. (Added to NAC by Bd. of Health, eff. 9-6-88; A…
[7] Nevada Administrative Code, Chapter 459 - Hazardous Materials (NAC-459)
Page 2
Open source documentSource excerpt
# CHAPTER 459-HAZARDOUS MATERIALS (cont.) 459.051 "Member of the public" defined. 459.0512 "Minor" defined. 459.0515 "Mobile electronic brachytherapy" defined. 459.0516 "Monitoring" defined. 459.0517 "National Source Tracking System" defined. 459.0518 "National Source Tracking Transaction Report" defined. 459.0519 "Nationally tracked source" defined. 459.052 "Natural radioactivity" defined. 459.0525 "Naturally occurring or accelerator-produced radioactive material" defined. 459.0527 "Negative pressure respirator" defined. 459.053 "Nonstochastic effect" defined. 459.054 "Occupational dose" defined. 459.055 "Occupational exposure" defined. 459.0555 "Package" defined. 459.056 "Particle accelerator" defined. 459.058 "Person" defined. 459.059 "Personnel monitoring" defined. 459.060 "Personnel monitoring equipment" defined. 459.062 "Pharmacist" defined. 459.063 "Physical description" defined. 459.064 "Physician" defined. 459.0645 "Planned special exposure" defined. 459.[redacted postal code] "Portable shielding" defined. 459.0646 "Positive pressure respirator" defined. 459.[redacted postal code] "Pressure demand respirator" defined. 459.[redacted postal code] "Principal activities" defined. 459.065 "Public dose" defined. 459.0653 "Qualitative fit test" defined. 459.0655 "Quality factor" defined. 459.0657 “Quantitative fit test" defined. 459.066 "Rad" defined. 459.068 "Radiation" defined. 459.070 "Radiation area" defined. 459.072 "Radiation machine" defined. 459.074 "Radiation safety officer" defined. 459.075 "Radiation symbol" defined. 459.076 "Radioactive material" defined. 459.078 "Radioactivity" defined. 459.0785 "Record of occupational exposure for a monitoring period" defined. 459.079 "Reference man" defined. 459.080 "Registrant" defined. 459.082 "Registration" defined. 459.084 "Regulations of the Department of Transportation" defined. 459.085 "Released for unrestricted use" defined. 459.086 "Rem" defined. 459.088 "Research and development" defined. 459.0885 "Residu…
[8] IHSA Safety Tool Box talks
Page 111
Open source documentSource excerpt
# Naturally occurring radioactive materials ## Explain dangers Naturally occurring radioactive materials or NORMS contain radioactive elements such as uranium, thorium, potassium and their decay products. In the earth's crust, NORMS are present in very low levels. However, when NORMS are processed or refined through some industrial process, the result can be higher concentrations and increased risk of exposure to humans and the environment. Workers should be aware of the presence of NORMS in the following types of workplaces: - Phosphate fertilizer plants • Forestry products and thermal electricity facilities - Mineral extraction and processing plants - Metal recycling plants - Waste management facilities - Tunneling and underground workings (in some areas where small amounts of radioactive minerals or gases may be present) - Water treatment facilities (where sorptive media or ion-exchange resins are being used to remove minerals). NORMs can enter the body when contaminated dust is generated and inhaled or when contaminated materials are ingested. The most significant health effects associated with exposure to NORMS are lung cancer and leukemia. NORM levels can vary depending on your location. If the area readings are above typical background radiation levels, NORMS may be present. ## Identify controls Radiation surveys should be conducted by those who have been trained in radiation safety or by external consultants to determine if the material is a NORM or man-made radioactive material. NORMS should only be handled by those with appropriate radiation safety training and precautions. These are some general precautions that should be taken when dealing with NORMS: • Train employees who may encounter enhanced NORM levels. - Prohibit drinking, eating, and smoking in areas where NORMS may exist. - Store NORMs and any contaminated materials and waste in a designated area and limit access to this area. - Avoid activities that may create dus…
[9] Personal Protective Equipment (PPE) Guide
Page 38
Open source documentSource excerpt
# SAMPLE PPE POLICIES # Procedures ## A. Hazard Assessment for PPE (Safety Person or designated person), in conjunction with Supervisors, will conduct a walk-through survey of each work area to identify sources of work hazards. Each survey will be documented using the Hazard Assessment Certification Form, which identifies the work area surveyed, the person conducting the survey, findings of potential hazards, and date of the survey. (Safety Person or designated person) will keep the forms in the (Specify exact location, e.g., your company's business files). (Safety Person or designated person) will conduct, review, and update the hazard assessment for PPE whenever • a job changes • new equipment or process is installed • there has been an accident - whenever a supervisor or employee requests it • or at least every year Any new PPE requirements that are developed will be added into (Name of your business)'s written accident prevention program. ## B. Selection of PPE Once the hazards of a workplace have been identified, (Safety Person or designated person) will determine if the hazards can first be eliminated or reduced by methods other than PPE, i.e., methods that do not rely on employee behavior, such as engineering controls (refer to Appendix B - Controlling Hazards). If such methods are not adequate or feasible, then (Safety Person or designated person) will determine the suitability of the PPE presently available; and as necessary, will select new or additional equipment which ensures a level of protection greater than the minimum required to protect our employees from the hazards (refer to Appendix C - Selection of PPE). Care will be taken to recognize the possibility of multiple and simultaneous exposure to a variety of hazards. Adequate protection against the highest level of each of the hazards will be recommended for purchase. All personal protective clothing and equipment will be of safe design and construction for the work to be performed an…
[10] Nevada Administrative Code, Chapter 459 - Hazardous Materials (NAC-459)
Page 65
Open source documentSource excerpt
# GENERAL PROVISIONS (cont.) ## NAC 459.333 Dose equivalents to embryos. (NRS 459.030, 459.201) (cont.) 2. A licensee may label sources of radiation, holders for sources of radiation or device components containing sources of radiation that are subjected to high temperatures with conspicuously etched or stamped radiation symbols that do not comply with the requirements for color set forth in subsection 1. 3. In addition to the contents of signs and labels required by NAC 459.010 to 459.950, inclusive, a licensee or registrant shall provide, on or near the required signs and labels, additional information, as appropriate, to make persons aware of potential exposures and to minimize those exposures. 4. A radiation symbol or the labels described in NAC 459.010 to 459.950, inclusive, must only be used when conditions exist that warrant their use. (Added to NAC by Bd. of Health, eff. 1-18-94; A by R084-98, 1-26-99; R149-07, 1-30-2008) - NAC 459.3555 Precautionary procedures: Requirements for posting signs. (NRS 459.201) Except as otherwise provided in NAC 459.3565: 1. A licensee or registrant shall post in each radiation area a conspicuous sign or signs bearing the radiation symbol and the words "CAUTION, RADIATION AREA." 2 A licensee or registrant shall post in each high radiation area a conspicuous sign or signs bearing the radiation symbol and the words "CAUTION, HIGH RADIATION AREA" or "DANGER, HIGH RADIATION AREA." 3. A licensee or registrant shall post in each very high radiation area a conspicuous sign or signs bearing the radiation symbol and the words "GRAVE DANGER, VERY HIGH RADIATION AREA." - 4 A licensee shall post each area of airborne radioactivity a conspicuous sign or signs bearing the radiation symbol and the words "CAUTION, AIRBORNE RADIOACTIVITY AREA" or "DANGER, AIRBORNE RADIOACTIVITY AREA." 5. A licensee shall post in each area or room in which there is used or stored an amount of licensed radioactive material exceeding 10 times the qua…
[11] Personal Protective Equipment Hazard Assessment
Page 3
Open source documentSource excerpt
# Table of contents What is a PPE hazard assessment?.. 2 Why should you do a PPE hazard assessment? .2 What are Oregon OSHA's requirements for PPE hazard assessments?........3 Oregon OSHA's hazard assessment rules .3 How to do a PPE hazard assessment..... Do a baseline survey to identify workplace hazards... Evaluate your employees' exposures to each hazard identified in the baseline survey.... Document your hazard assessment ..5 Do regular workplace inspections .6
[12] Nevada Administrative Code, Chapter 459 - Hazardous Materials (NAC-459)
Page 6
Open source documentSource excerpt
# CHAPTER 459-HAZARDOUS MATERIALS (cont.) <table><tr><th>459.604</th><th>X-ray and electron therapy installations: Selections of radiation type, energy, and stationary or moving beam.</th></tr><tr><td>459.606</td><td>X-ray and electron therapy installations: Focal spot; beam orientation; system checks.</td></tr><tr><td>459.608</td><td>X-ray and electron therapy installations: Shielding requirements.</td></tr><tr><td>459.610</td><td>X-ray and electron therapy installations: Surveys; operating procedure; calibration.</td></tr><tr><td>459.612</td><td>X-ray and electron therapy installations: Spot checks.</td></tr><tr><td>459.614</td><td>Veterinary medicine radiographic installations.</td></tr><tr><td>459.616</td><td>Other radiographic systems: Beam limitation.</td></tr><tr><td>459.618 459.620</td><td>General purpose X-ray systems: Stationary and mobile. Other radiographic systems: Special purpose systems.</td></tr><tr><td>459.622</td><td>Devices to control exposures.</td></tr><tr><td>459.624</td><td>Other radiographic systems: Source to skin distance; exposure reproducibility; standby radiation.</td></tr><tr><td>Radiation</td><td>Safety Requirements for Analytical X-Ray Equipment</td></tr><tr><td>459.640 459.642</td><td>Definitions. "Analytical X-ray equipment" defined.</td></tr><tr><td>459.644</td><td>"Analytical X-ray system" defined.</td></tr><tr><td>459.646</td><td>"Fail-safe characteristics" defined.</td></tr><tr><td>459.648</td><td>"Local components" defined.</td></tr><tr><td>459.650</td><td>"Normal operating procedures" defined.</td></tr><tr><td>459.652</td><td>"Open-beam configuration" defined.</td></tr><tr><td>459.654</td><td>"Primary beam" defined.</td></tr><tr><td>459.656</td><td>Scope.</td></tr><tr><td>459.658 459.660</td><td>Equipment requirements. Area requirements.</td></tr><tr><td>459.662</td><td>Operating requirements.</td></tr><tr><td>459.664</td><td></td></tr><tr><td colspan="2">Personnel requirements. Radiation Safety Requirements for X-Ray Industr…
[13] Nevada Administrative Code, Chapter 459 - Hazardous Materials (NAC-459)
Page 91
Open source documentSource excerpt
# GENERAL PROVISIONS (cont.) ## Radiation Safety Requirements for Well Logging (cont.) NAC 459.7695 Use of radioactive markers and uranium sinker bars. (NRS 459.201) 1. A licensee shall not use radioactive markers in wells if the individual markers contain quantities of radioactive material which exceed the quantities specified in NAC 459.188. 2. The use of radioactive markers is subject to the requirements of NAC 459.7675. 3. A licensee shall not use a uranium sinker bar in well logging if the bar is not legibly impressed with the words "CAUTION - RADIOACTIVE-DEPLETED URANIUM" and "NOTIFY CIVIL AUTHORITIES (or COMPANY NAME) IF FOUND." (Added to NAC by Bd. of Health, eff. 9-6-88) NAC 459.7701 Logging supervisors and assistants: Qualifications; safety reviews; records. (NRS 459.201) 1. A licensee shall not permit a person to act as a logging supervisor until that person: (a) Has completed training in the subjects set forth in NAC (b) Has received copies of, and instruction in: 459.7705. (1) The regulations contained in NAC 459.010 to 459.950, inclusive; (2) The division license under which the logging supervisor will perform well logging; and (3) The licensee's operating and emergency procedures required by NAC 459.7715. (c) - Has completed on-the-job training and demonstrated his or her competence, in a field evaluation, in the use of: (1) Radioactive materials; (2) Remote handling tools; and (3) Radiation survey instruments. (d) Has demonstrated - the person's understanding of the requirements of paragraphs (a) and (b) of subsection 1 by successfully completing a written test. 2. A licensee shall not permit a person to act as a logging assistant until that person: (a) Has received instruction in the regulations contained in NAC 459.010 to 459.950, inclusive; (b) Has received copies of, and instruction in the licensee's operating and emergency procedures required by NAC 459.7715; (c) Has demonstrated his or her understanding of the ma…
[14] Personal Protective Equipment Hazard Assessment
Page 6
Open source documentSource excerpt
# What types of PPE may be necessary? Your hazard assessment should determine if your employees need any of the following types of PPE: - Eye and face protection ◆ Fall protection - Foot protection • Hand/general skin protection - Head protection • Hearing protection • Leg protection ● Personal floatation device • Respiratory protection • Torso/general body protection ## How to do a PPE hazard assessment ## Do a baseline survey to identify workplace hazards A baseline survey is a thorough evaluation of your entire workplace - including work processes, tasks, and equipment - that identifies safety and health hazards. A complete survey will tell you what the hazards are, where they are, and how severe a potential injury could be. ## Suggestions: Use safety data sheets (SDS) to identify chemical hazards. A safety data sheet has detailed information about a hazardous chemical's health effects, its physical and chemical characteristics, and safe handling practices. Review equipment owner and operator manuals to determine the manufacturer's safety warnings and recommended PPE. Conduct a job-hazard analysis (JHA) - a method of identifying, assessing, and controlling hazards associated with specific jobs. A JHA breaks down a job into tasks. You evaluate each task to determine if there is a safer way to do it. A job-hazard analysis works well for jobs with difficult-to-control hazards and jobs with histories of accidents or near misses. JHAS for complex jobs can take a considerable amount of time and expertise to develop. You may want to have a safety professional help you. Have an experienced safety professional survey your workplace with you. 4
Keep exploring.
Generate HS Manual for Construction Project
Construction Project Health and Safety Manual ============================================= This manual outlines the health and safety requirements for the construction project. It details critical safety procedures, risk assessments, emergency response plans, and compliance measures to ensure a safe working
Read the threadWrite a toolbox talk on crushing concrete
Safe Work Practices for Concrete Crushing Operations ==================================================== *Date:** 2026-01-29 *Duration:** \[DURATION] minutes *Presenter:** \[PRESENTER NAME] *Location:** \[LOCATION] Objective To ensure all personnel understand and implement safe work practices during concrete crushing
Read the threadRisk Assessment Reports
Workplace Safety Risk Assessment for General Occupational Activities ==================================================================== *Assessment Date:** \[DATE] *Assessor:** \[ASSESSOR NAME] *Department/Area:** \[DEPARTMENT/AREA] *Review Date:** \[REVIEW DATE] 1\. Assessment Scope This risk assessment covers
Read the threadMake a toolbox talk on Machine Guarding
Machine Guarding Safety ======================= *Date:** 2025-11-20 *Duration:** \[DURATION] minutes *Presenter:** \[PRESENTER NAME] *Location:** \[LOCATION] Objective To understand the importance of machine guarding, identify common hazards, and implement effective control measures to prevent injuries. Introduction
Read the threadppe general industry
General Industry Personal Protective Equipment (PPE) Guidelines =============================================================== Document Number: \[SWP-NUMBER] Revision Date: \[DATE] Next Review Date: \[NEXT REVIEW DATE] Department: \[DEPARTMENT NAME] 1\. Scope This procedure outlines the requirements for personal
Read the threadCreate a safe work procedure for sanding and painting drywall
Safe Work Procedure: Sanding and Painting Drywall Document Number: [SWP-NUMBER] Revision Date: [DATE] Next Review Date: [NEXT REVIEW DATE] Department: [DEPARTMENT NAME] 1. Scope This Safe Work Procedure (SWP) outlines the necessary safety precautions and procedures for sanding and painting drywall in construction and
Read the threadAdd your experience.
Community answers can add practical context. They are moderated, but they are not reviewed by Francis Langlois or presented as SALUS safety guidance.
New contributions are closed. Previously approved contributions remain visible.
Community answers(0)
No community answers have been approved yet.
Comments on Rosie's answer(0)
No comments have been approved yet.