A safe work procedure for hot work should require that the job be avoided if possible, formally authorized, planned, and controlled before work starts. Hot work includes temporary operations involving open flame or producing heat or sparks such as welding, burning, cutting, brazing, grinding, and soldering. A hot work management program should define where and when hot work is permitted, who authorizes it, what must be assessed, how the area is prepared, what tools are required, and how workers, supervisors, fire watch personnel, and contractors are trained. [1] [7] [5]

  1. Determine whether hot work can be eliminated or replaced with a safer method such as mechanical bolting, hydraulic shears, screwed or flanged pipe, or mechanical pipe cutting.
  2. Conduct a documented hazard identification and risk assessment for the exact location, task, equipment, materials, and surrounding exposures before issuing the permit.
  3. Verify the work area is suitable: inspect walls, ceilings, floors, partitions, concealed spaces, ducts, adjacent rooms, and lower levels where sparks, slag, or heat could travel.
  4. Remove combustible and flammable materials from the area. If they cannot be moved, protect them with fire-resistant blankets, shields, or barriers. If adequate protection cannot be achieved, do not permit the work.
  5. Identify and isolate fuel sources and hazardous energy: shut down affected conveyors or suction systems, isolate and vent pressurized vessels, piping, and equipment, and ensure drums, tanks, barrels, and similar containers are cleaned and tested before hot work.
  6. Eliminate explosive atmospheres and continuously monitor where combustible gases, vapors, or dust may accumulate. Do not allow hot work in an explosive atmosphere.
  7. Confirm fire protection is in place: suitable extinguishers immediately available, fixed suppression systems operable, first-aid supplies accessible, and emergency notification procedures understood.
  8. Establish ventilation controls to remove fumes from the breathing zone and prevent buildup of flammable vapors or oxygen-enriched/deficient atmospheres. Use local exhaust where needed; if ventilation is not effective, provide appropriate respiratory protection.
  9. Barricade or restrict the area as needed, post the permit at the job site, and ensure only authorized and trained personnel perform the work.
  10. Assign a dedicated trained fire watch whenever fire could develop, including where combustibles are within the hazard zone, on the opposite side of walls or bulkheads, or below the work area.

[5] [4] [11] [8] [14] The hot work permit should be issued by a designated competent person or supervisor before work begins and posted at the job site. At minimum, the permit should identify the building or area, department, floor or level, description of work, start and completion times, the employee performing the hot work, and the assigned fire watch. The issuer should verify precautions on the checklist, review safety procedures with both the welder and fire watch, and retain completed permit records after the fire watch period and final area inspection. As a best practice aligned with OSHA 29 CFR 1910\.252 and NFPA 51B principles, the permit should also document the hazard assessment, required isolations, atmospheric concerns, PPE, fire protection measures, and authorization period. [2] [2] [3] [3]

Key hazard identification and risk assessment points:

  • Fire and explosion from sparks, slag, hot metal, open flame, and heat transfer through walls, floors, ceilings, cracks, ducts, and openings
  • Combustible loading within at least a 35-foot hazard zone and in concealed or adjacent spaces
  • Flammable liquids, gases, vapors, combustible dusts, oxygen enrichment, and process residues
  • Toxic fumes and gases, especially in enclosed or poorly ventilated spaces
  • Burns, eye injury from radiation and flying particles, electric shock, noise, and pressure buildup in closed piping or vessels
  • Additional confined-space or permit-required hazards where applicable

[6] [6] [1] [9] Isolation and area preparation are critical. Clear combustibles from the hot work area and surrounding exposures, including lower levels and the opposite side of walls or bulkheads. Cover holes, cracks, ducts, floor openings, and other penetrations with fire-resistant materials so sparks cannot travel. Sweep floors clean; if floors are combustible, keep them wet, cover them with wet sand, or use fire-resistant shields. Remove spilled grease, oil, dust, and debris. Protect gas lines and nearby equipment from sparks and hot material. Secure cylinders upright, inspect hoses and equipment for leaks or damage, and keep cylinders away from heat and free of oil or grease. Do not weld or cut on drums, tanks, barrels, or piping that contained flammables until they are properly cleaned, opened or vented as required, and tested safe. [2] [4] [4] [16] [9]

Ventilation must be selected based on the process, materials, and space. Provide sufficient general ventilation for routine work, and use local exhaust ventilation where fumes or gases can accumulate or where contaminants must be captured at the source. Ventilation should remove contaminants from the breathing zone, prevent accumulation of flammable vapors, and prevent oxygen-rich or oxygen-deficient atmospheres. Do not use compressed welding gases for ventilation, cooling, or cleaning. If local exhaust is not effective enough to control exposure, provide respirators under a compliant respiratory protection program. Hazard communication must cover welding consumables and generated contaminants, and workers must have access to labels and safety data sheets. [12] [14] [10] [10] [10]

Minimum PPE and protective clothing should be task-specific and based on the hazard assessment.

  • Welding helmet or hand shield with the correct filter shade for the process; for arc welding, full face protection is required
  • Safety glasses with side shields or goggles under the helmet and during chipping or grinding
  • Face shield over primary eye protection for severe grinding or impact exposure as needed
  • Fire-resistant, oil-free clothing; long sleeves; long pants without cuffs; avoid fabrics that melt
  • Leather gloves, sleeves, apron, and substantial leather safety footwear
  • Fire-resistant cap or head covering; hearing protection when overhead work or hazardous noise is present
  • Respiratory protection when ventilation does not adequately control exposure or when required by the materials and process

[1] [1] [1] [12] [15] Fire watch requirements should be explicit. Assign a dedicated trained fire watch whenever combustibles may be exposed, sparks may travel, work is near walls, bulkheads, concealed spaces, or lower levels, or any fire could develop. The fire watch must not be the person performing the hot work and must not perform other duties. The fire watch must have suitable firefighting equipment immediately available, know how to use it, know alarm and fire notification procedures, stop work if conditions change, and monitor the area continuously during the job and for the required post-work period. Your procedure should meet the most stringent applicable requirement at your site: some documents specify at least 30 minutes after work, while others recommend at least 60 minutes and longer where hazards remain. [1] [1] [2] [2] [8]

Emergency response provisions should include immediate stop-work authority, alarm activation, evacuation, and first response to incipient fires only when it is safe to do so. Before work starts, confirm the location and operability of extinguishers, hoses, sprinklers, alarms, exits, and first-aid supplies. If a fire starts that cannot be controlled immediately with available equipment, evacuate, activate emergency notification, and summon the fire department or site emergency team. For burns, eye injuries, electric shock, suspected toxic inhalation, or confined-space emergencies, obtain prompt medical assistance and follow site rescue procedures. In confined spaces, atmospheric monitoring and a means for quick evacuation are essential. [4] [4] [9]

For OSHA and regulatory compliance, the procedure should align with 29 CFR 1910\.252 for welding, cutting, and brazing; applicable PPE requirements in 29 CFR 1910 Subpart I; respiratory protection in 29 CFR 1910\.134 when respirators are required; hazard communication in 29 CFR 1910\.1200; and any state-specific rules such as Cal/OSHA ventilation requirements. It should also incorporate recognized consensus standards and fire-prevention practices such as NFPA 51B, ANSI Z49\.1, and applicable CSA or local requirements. In practice, compliance means using authorized and trained personnel, maintaining equipment in safe condition, controlling ignition sources and combustibles, providing ventilation and PPE, using permits and fire watch where required, and documenting inspections, authorization, and closeout. [11] [10] [13] [7]

A practical safe work procedure can therefore be summarized as follows: authorize the job through a hot work permit; assess whether hot work can be avoided; inspect the area and adjacent exposures; remove or shield combustibles within the hazard zone; isolate energy sources, vessels, ducts, and processes that could create flammable atmospheres; verify equipment condition; provide ventilation, fire protection, and task-specific PPE; assign a dedicated trained fire watch; perform the work under continuous monitoring; maintain post-work fire watch and final inspection; then close the permit only after the area is confirmed safe. If any required precaution cannot be met, the hot work should not proceed. [3] [11]

16 source record(s)

Sources used for this answer

[1] Toolbox Talk: Cutting & Welding

Page 1

Open source document

Source excerpt

# CUTTING & WELDING AURAZ 6:00 Date Posted: 09/19/2016 Welding and cutting pose several hazards on the jobsite. Following proper guidelines and wearing appropriate attire, you can eliminate the possibility of an accident. ## GENERAL GUIDELINES • Whenever possible, move objects to a safe place before heating, cutting, or welding. • Remove or effectively screen all fire hazards where the welding job is to take place. • Do not cut or weld any steel drum or other vessel that might have contained flammables until it has been steam purged and tested. Flushing with water is not sufficient. • Do not apply heat to the inside surface of any piping or vessel unless it is open to the atmosphere to prevent pressure buildup. • Where it is necessary to catch falling sparks and slag, use fiberglass blankets or fire-retardant welding tarpaulins. • Keep an appropriate type of fire extinguisher available at all times. • Make sure there is sufficient general ventilation. • Where welding fumes and gases can accumulate, use local exhaust ventilation to remove the contaminants. • Proper ventilation is required when using inert gases while welding. ## WORKERS ENGAGED IN WELDING OR BURNING OPERATIONS MUST WEAR Face protectors and safety eyewear to guard against harmful radiation or particles of molten metal, including when chipping and grinding welds ## WORKERS ENGAGED IN WELDING OR BURNING OPERATIONS SHOULD WEAR • Flame-retardant work clothing, preferably made of cotton or wool fibers • Leather gauntlet-type gloves and arm protection • An apron made of leather or other suitable material for heavy work • Substantial safety footwear made of leather or another equally firm material IMPORTANT NOTE: Don't forget the fire watch for at least 30 minutes after work has stopped. ## QUESTIONS FOR DISCUSSION • What damage can a welding arc do to your eyes? • What additional hazards are there when working with stainless steel? ## PRESENTER TIPS • Pre-read the Toolbox Talk. You…

[2] Welding - Hot Work

Page 1

Open source document

Source excerpt

CCOHS CCHST Canadian Centre for Occupational Health and Safety Centre canadien d'hygiène et de sécurité au travail Welding # Welding - Hot Work ## On this page What is hot work? What is a hot work management program? Can hot work be avoided? Before performing hot work, what are some general good practices? ## What is hot work? Working with ignition sources near flammable materials is referred to as "hot work." Welding, soldering, and cutting are examples of hot work. Fires are often the result of the "quick five- minute" job in areas not intended for welding or cutting. Getting a hot work permit before performing hot work is just one of the steps involved in a hot work management program that helps to reduce the risk of starting a fire by hot work in areas where there are flammable or combustible materials. The 2024version of NFPA (National Fire Protection Association) Standard 51B "Fire Prevention During Welding, Cutting and Other Hot Work," serves as the basis for many current fire prevention practices adopted by industry. CSA standard W117.2-12 (R2017) - Safety in welding, cutting, and allied processes and ANSI (American National Standards Institute) standard Z49.1: 2021Safety in Welding, Cutting and Allied Processes were created to protect persons and property from injury, illness, and damage from fire and explosions that may occur from these processes. ## What is a hot work management program? Hot work management programs are put in place to control or eliminate hot work hazards and their risks. Programs include the development of policies, procedures, and the assignment of responsibilities and accountabilities for all aspects of hot work. A program includes: 1. Policies a. Where hot work is permitted b. When hot work is permitted Welding - Hot Work CCOHS

[3] Torch and Welding Hot Work Permit

Page 1

Open source document

Source excerpt

Part 1 of 2 Issue Date Permit # # Welding and Torch Cutting Permit <table><tr><th>Building/Area:</th><th></th><th>Date:</th></tr><tr><td>Department:</td><td></td><td>Floor/Level</td></tr><tr><td>Description of</td><td>Work to be done:</td><td></td></tr></table> Description of Work to be done: <table><tr><th>Time Started:</th><th>Time Complete:</th></tr><tr><td>Employee to be doing "Hot Work":</td><td>Fire Watch Employee:</td></tr></table> ## Cutting and Welding Safety Checklist - Hot Work permit posted on site. (1 Copy) - Equipment and hoses free from damage and leaks. Cylinders supported. - Work area clear of all combustibles within a radius of 35'. Cover holes and openings with fire retardant materials. - Conveyors and suction systems in the area must be shut down. - Area wet down except when arc welding. - Lower areas wet down thoroughly. ## During Cutting and Welding - Fire Watch has fire fighting equipment and is train on its use. - Fire watch knows fire notification procedures. ## After Cutting and Welding - Area wet down thoroughly. - Equipment stored properly. - Fire watch is posted on site for 30 minutes after cutting and welding is done. -1-

[4] Welding - Hot Work

Page 2

Open source document

Source excerpt

# Welding - Hot Work (cont.) ## What is a hot work management program? (cont.) C. Who authorizes, performs, and monitors hot work activities 2. Procedures a. What must be assessed before permitting/performing hot work in an area or on a process piece of equipment or area b. What to do to prepare an area for hot work C. What to do if hot work cannot be avoided in a particularly hazardous area d. What hot work tools are required e. How to obtain a hot work permit, when they are required, and who can administer them 3. Training a. Employees, supervisors, maintenance individuals, fire wardens, trained fire watch individuals, and contractors all have different roles, and must be trained accordingly 4. Communications a. Posting procedures b. Posting policies C. Posting signs in areas that are prohibited from having hot work performed in them ## Can hot work be avoided? You may be able to substitute hot work with other methods. Below are some examples: <table><tr><th>Instead of:</th><th>Use:</th></tr><tr><td>Saw or torch-cutting</td><td>Manual hydraulic shears</td></tr><tr><td>Welding</td><td>Mechanical bolting</td></tr><tr><td>Sweat soldering</td><td>Screwed or flanged pipe</td></tr><tr><td>Torch of radial saw cutting</td><td>Mechanical pipe cutter</td></tr></table> But remember, always assess the substitutes or alternate methods for any risks or hazards. Do not introduce any new risks or hazards. Welding - Hot Work CCOHS

[5] Cal/OSHA Regulations | Chapter 4 | Subchapter 7: General Industry Safety Orders | §5150. Ventilation and Personal Protective Equipment Requirements for Welding, Brazing and Cutting

Page 2

Open source document

Source excerpt

# $5150. Ventilation and Personal Protective Equipment Requirements for Welding, Brazing and Cutting. (cont.) (F) Mercury (G) Zinc (H) Inert-gas metal-arc welding or oxygen cutting of stainless steel (2) The exhaust system shall be vented in a manner such that workers and others are not exposed to hazardous concentrations of toxic substances. (3) When the nature of the work is such that local exhaust ventilation is not an effective means for preventing potentially hazardous exposure levels, as specified by Section 5155, supplied-air respirators shall be worn. (c) Toxic Substances Used in the Open Air. Where toxic substances such as those listed in paragraph (b)(1) are used, respiratory protective equipment, in accordance with Section 5144, shall be provided except as otherwise specified by this subsection. (1) In operations involving beryllium-containing base or filler metals, only supplied-air respirators shall be used. (2) Except for operations involving beryllium, cadmium, lead or mercury, respiratory protective equipment is not required when natural or mechanical ventilation is sufficient to remove welding fumes from the breathing zone of the workers. (d) Improper Use of Welding Gases. Compressed gases used for welding and cutting shall not be used for ventilation purposes, comfort cooling, blowing dust from clothing, or cleaning the work area. (e) Chlorinated Hydrocarbons. Degreasing or other operations involving chlorinated hydrocarbons shall be located or controlled such that vapors from these operations will not enter the atmosphere surrounding any welding or cutting operations to prevent the degradation of such chlorinated hydrocarbon vapors to more highly toxic gases by the action of heat or ultraviolet radiation. (f) Hazard communication. The employer shall include the potentially hazardous materials employed in fluxes, coatings, coverings, and filler metals, all of which are potentially used in welding and cutting, or are released to th…

[6] Toolbox Talk: Welding

Page 2

Open source document

Source excerpt

# WELDING (cont.) ## WHEN DO I NEED TO USE A HOT WORK PERMIT? A Hot Work Permit is required for any temporary operation involving open flames or producing heat and sparks, which could ignite nearby items unless they are protected or the work is completed in a designated area. This includes, but is not limited to, welding, burning, cutting, brazing, grinding, and soldering. The Hot Work Permit is a formal process to ensure that potential safety issues are addressed in the area where you will be doing the work and that someone else agrees it is safe to do it. ## PERSONAL PROTECTIVE EQUIPMENT FOR HOT WORK Welding and cutting can produce hazards such as sparks, spatter, radiation (infrared, ultraviolet, and blue light), slag, heat, hot metal, fumes and gases, and even electric shock. Since these hazards may cause burns, injury, or death, it is essential always to wear proper PPE. ## EYE AND FACE PROTECTION • Wear a helmet with a filter lens and cover plate that complies with ANSI Z87.1 for protection from radiant energy, flying sparks, and spatter. • Helmets and hand shields must protect the face, forehead, neck, and ears to a vertical line in the back of the ears from the direct radiant energy from the arc and direct weld spatter. • Helmets shall be made of material that complies with ANSI Z49.1. • Filter lenses and cover plates must meet the tests prescribed in ANSI Z87.1. • Wear approved safety glasses with side shields (or goggles) under your helmet. • The safety glasses with side shields (or goggles) protect against flying metal, slag chips, grinding fragments, wire wheel bristles, and similar hazards, which can ricochet under the helmet. Choose a filter lens shade according to the Lens Shade Selector Chart in ANSI Z49.1 ## HEAD AND EAR PROTECTION • Wear a fire-resistant welder's cap or head covering under your helmet. It will protect your head from flying sparks, spatter, and burns. • When working overhead, wear approved earplugs or muffs. They preven…

[7] Welding - Personal Protective Equipment and Clothing

Page 4

Open source document

Source excerpt

# Welding - Personal Protective Equipment and Clothing (cont.) ## Why is eye protection important? Eye injury can occur from the intense light and radiation that a welding arc can produce. Eye injury can also occur from hot slag and other metal debris that can fly off from the weld during cooling, chipping or grinding. - Protect your eyes from welding light by wearing a welder's helmet fitted with a filter shade that is suitable for the type of welding you are doing. - ALWAYS wear safety glasses with side shields or goggles when chipping or grinding a work piece if you are not wearing a welding helmet. ## What type of eye and face protection is appropriate for my welding task? The various types of eye protection are broken down into classes in the CSA standard Z94.3- 20 "Eye and face protectors". Each class is designed for a specific use. Eye and face protectors should have distinctive markings to identify the manufacturer and their class. Classifications of common protectors for welding operations are listed below: - Class 2C — direct / non-ventilated goggles with non-ionizing radiation protection - Class 3 - welding helmets - Class 4 - welding hand shields - Class 6 - face shields for non-ionizing radiation protection - Class 7 - respirator facepiece for non-ionizing radiation protection The following operations require full face protection by using either a welding helmet or a hand shield: - arc welding, - plasma arc cutting, gouging or welding, and - air carbon arc cutting. For gas cutting, welding, or brazing, the intensity of the light is much less than from arc welding, cutting or gouging processes. Lighter shade filter lenses can be used with goggles in place of a helmet. More information can be found in the OSH Answers on Eye and Face Protectors. What are the various components of welding hand shields and helmets? Welding - Personal Protective Equipment and Clothing CCOHS

[8] Personal Protective Equipment (PPE) Checklist

Page 2

Open source document

Source excerpt

# Personal Protective Equipment (PPE) Checklist (cont.) <table><tr><th>12. If the employee provides his/her own PPE, is it adequate to protect the worker from hazards in the workplace?</th><th></th><th></th><th></th></tr><tr><td>Eye and Face Protection (N/A )</td><td>Yes</td><td>No</td><td>Comments</td></tr><tr><td>13. Do employees perform hammering, cutting, grinding, sanding and/or masonry work that produces or could produce particles/dust or debris?</td><td>ㅁㅁㅁ</td><td></td><td></td></tr><tr><td>14. Do employees handle chemicals that could splash into their eyes or face?</td><td></td><td></td><td></td></tr><tr><td>15. Do employees work with wet or powdered cement?</td><td></td><td></td><td></td></tr><tr><td>16. Do employees weld?</td><td></td><td></td><td></td></tr><tr><td>17. Do employees work in dusty or windy conditions?</td><td></td><td></td><td></td></tr><tr><td>If "yes" in response to any of the above eye and face protection questions, are the employees using appropriate PPE as applicable (i.e. safety glasses, goggles, welding shields, face shields, etc.)?</td><td></td><td></td><td></td></tr><tr><td>18. Do safety glasses have frames constructed of plastic or metal with impact-resistant lenses?</td><td></td><td></td><td></td></tr><tr><td>19. Do safety glasses have side shields?</td><td></td><td></td><td></td></tr><tr><td>20. Do safety glasses and goggles completely cover the eyes, eye socket and area surrounding the eyes?</td><td></td><td></td><td></td></tr><tr><td>21. Are goggles tight-fitting?</td><td></td><td></td><td></td></tr><tr><td>22. Are welding shields made of fiberglass or vulcanized fiber with a filtered lens?</td><td></td><td></td><td></td></tr><tr><td>23. Do the filter lenses have the appropriate shade number to protect against specific hazards of the welding work being performed?</td><td></td><td></td><td></td></tr><tr><td>24. Is damaged, defective or worn eye/face protection properly discarded and replaced?</td><td></td><td></td><td></td></…

[9] Self-inspection checklist: Welding, cutting and brazing

Page 2

Open source document

Source excerpt

## Welding, cutting and brazing (cont.) - Is work and electrode lead cable frequently inspected for wear and damage and replaced when needed? - Do the means for connecting cable lengths have adequate insulation? - When the object to be welded cannot be moved and fire hazards cannot be removed, are shields used to confine heat, slag, and sparks? - Are fire watchers assigned when welding or cutting is performed in locations where a fire might develop? - When welding is done on metal walls, are precautions taken to protect combustibles on the other side? - Before hot work begins, are drums, barrels, tanks, and other containers thoroughly cleaned and tested so that no substances remain that could explode, ignite, or produce toxic vapors? - Do eye-protection helmets, hand shields, and goggles meet appropriate standards? - Do employees use appropriate PPE when exposed to the hazards of welding, cutting, or brazing operations? - Do you check for adequate ventilation where welding or cutting is performed? - When welders work in confined spaces is the atmosphere monitored and is there a means for their quick evacuation in an emergency? - Are regulator-pressure adjusting screws released when welding or cutting is stopped for an extended period of time? -2-

[10] Welding - Hot Work

Page 4

Open source document

Source excerpt

# Before performing hot work, what are some general good practices? (cont.) - Post a trained fire watcher within the work area, including lower levels if sparks or slag may fall during welding, including during breaks, and for at least 60 minutes after work has stopped. Depending on the work done, the area may need to be monitored for longer (up to 3 or more hours) after the end of the hot work until fire hazards no longer exist. - Eliminate explosive atmospheres (e.g., vapours or combustible dust) or do not allow hot work. Shut down any process that produces combustible atmospheres, and continuously monitor the area for accumulation of combustible gases before, during, and after hot work. - If possible, schedule hot work during shutdown periods. - Comply with the required legislation and standards applicable to your workplace. Fact sheet last revised: 2024-08-12 ## Disclaimer Although every effort is made to ensure the accuracy, currency and completeness of the information, CCOHS does not guarantee, warrant, represent or undertake that the information provided is correct, accurate or current. CCOHS is not liable for any loss, claim, or demand arising directly or indirectly from any use or reliance upon the information. Welding - Hot Work CCOHS

[11] Welding - Ventilation

Page 1

Open source document

Source excerpt

CCOHS CCHST Canadian Centre for Occupational Health and Safety Centre canadien d'hygiène et de sécurité au travail Welding # Welding - Ventilation On this page Where can I find some general guidelines for welding ventilation? What types of ventilation can be used to remove air contaminants from a welder's breathing zone? What are some examples of Local Exhaust Ventilation? ## Where can I find some general guidelines for welding ventilation? Ventilation is used for three general purposes: - Remove air contaminants from a worker's breathing zone and work area, - Prevent the accumulation of flammable or combustible gases or vapours; and, - Prevent oxygen rich or oxygen deficient atmospheres. For processes such as welding, brazing, soldering, and torch cutting, the primary purpose of ventilation is to remove air contaminants from the worker's breathing zone. Different ventilation strategies may be needed in each case to remove air contaminants from the welder's breathing zone. General guidelines have been published in the CSA standard W117.2:19 (R2023) Safety in welding, cutting, and allied processes, and the ANSI (American National Standards Institute) standard Z49.1-2021 Safety in Welding, Cutting and Allied Processes. Whenever ventilation is used as a means of worker protection, the ventilation system should be used and maintained in accordance with acceptable procedures. Where ventilation alone cannot adequately protect the welder, personal protective equipment (respirators) may also be used. Select the appropriate respirator according to the hazards present, any applicable legislation, and/or to the CSA standard Z94.4:18 (R2023) Selection, Use and Care of Respirators. Welding - Ventilation CCOHS

[12] Welding - Hot Work

Page 3

Open source document

Source excerpt

# Before performing hot work, what are some general good practices? Make sure you are following your hot work procedure. Also, consider the following items: - Make sure that all equipment is in good operating order before work starts. - Make sure that all appropriate personal protective devices are available at the site and each worker has been trained on how to use, clean, and store them properly. - Inspect the work area thoroughly before starting. Look for combustible materials in structures (partitions, walls, ceilings). - Move all flammable and combustible materials away from the work area. - If combustibles cannot be moved, cover them with fire-resistant blankets or shields. Protect gas lines and equipment from falling sparks, hot materials, and objects. - Make sure that all available fire suppression systems are in good repair and operable (e.g., sprinklers, hoses, extinguishers, etc.) - Make sure that appropriate fire extinguishers (e.g., ABC fire extinguishers) are available and easily accessible. - Sweep clean any combustible materials on floors around the work zone. Combustible floors must be kept wet with water or covered with fire-resistant blankets or damp sand. Use water ONLY if electrical circuits have been de-energized to prevent electrical shock. - Remove any spilled grease, oil, or other combustible liquid. - Vacuum away combustible debris from inside ventilation or other service duct openings to prevent ignition. Seal any cracks in ducts. Prevent sparks from entering into the duct work. Cover duct openings with a fire resistant barrier and inspect the ducts after work has concluded. - Make sure that the first-aid boxes are available and easily accessible. - Block off cracks between floorboards, along baseboards and walls, and under door openings, with a fire resistant material. Close doors and windows. - Cover wall or ceiling surfaces with a fire resistant and heat insulating material to prevent ignition and accumulation of h…

[13] Self-inspection checklist: Welding, cutting and brazing

Page 1

Open source document

Source excerpt

Self-inspection checklist ## Welding, cutting and brazing - Do you allow only authorized and trained personnel to use welding, cutting, or brazing equipment? - Are compressed gas cylinders regularly examined for signs of defect, deep rusting, or leakage? - Are cylinders kept away from sources of heat? - Are employees prohibited from using cylinders as rollers or supports? - Are empty cylinders appropriately marked, their valves closed, and valve-protection caps placed on them? - Are signs posted that read “DANGER - NO SMOKING, MATCHES, OR OPEN LIGHTS," or the equivalent? - Are cylinders, cylinder valves, couplings, regulators, hoses, and apparatus kept free of oily or greasy substances? - Unless secured on special trucks, are regulators removed and valve-protection caps put in place before moving cylinders? - Do cylinders without fixed hand wheels have keys, handles, or nonadjustable wrenches on stem valves when in service? - Are liquefied gases stored and shipped with the valve end up and with valve covers in place? - Before a regulator is removed, is the valve closed and gas then released from the regulator? - Is open circuit (no load) voltage of arc welding and cutting machines as low as possible and not more than the recommended limit? - Are electrodes removed from holders when not in use? - Are employees required to shut off the electric power to the welder when no one is using it? - Is suitable fire-extinguishing equipment available for immediate use? - Are welders forbidden to coil or loop welding electrode cable around their bodies? - 1 -

[14] Toolbox Talk: Welding

Page 1

Open source document

Source excerpt

# WELDING Date Posted: 05/14/2024 According to the National Fire Protection Agency (NFPA), there are, on average, 4,630 structure fires involving hot work per year. Any time equipment that produces a spark or open flame or a process that generates excessive heat, there is a risk of fire or explosion. Flames and sparks are the leading causes of fire or explosions during welding and cutting. Sparks can travel up to 35 feet in a work area. Sparks can also pass through wall/ceiling/floor openings or be lodged within cracks during the welding and cutting. Combustibles such as wood, paper, rags, dust, and flammable liquids can also increase the risk of fire and explosion. ## YOUR FIRST CONSIDERATIONS Due to the hazardous nature of the work, try to eliminate the need for hot work when feasible. Hot work hazards can be avoided with an alternative job completion method. Some options include the following: • Screwed, flanged, or clamped pipe. . Manual hydraulic shears. • Mechanical bolting or pipe cutting. • Compressed air-actuated fasteners. ## HAZARDS OF HOT WORK Hot work can unite all three parts of the fire triangle: oxygen, fuel, and an ignition source. ## OXYGEN ENRICHMENT Oxygen is present in the ambient air at approximately 21% by volume. Therefore, unsafe practices involving pure oxygen can cause oxygen enrichment (over 22 percent by volume) in the workplace and increase the risk of fire or explosion. ## FUEL SOURCES IN THE WORK AREA Fuel includes anything that can be ignited. Examples of common fuels include the following: • Materials such as wood, plastic, insulation, and roofing materials, including those in concealed spaces. • Flammable and combustible liquids or gases such as fuel, paint, and cleaning solvents. • Simple combustibles include rags, paper, cardboard, lumber, and furnishings. ## IGNITION (HEAT) SOURCES Ignition sources can be as simple as the hot work itself. Ignition results when any heat source sufficient to ignite a fuel does…

[15] Torch and Welding Hot Work Permit

Page 2

Open source document

Source excerpt

# Welding and Torch Cutting Permit (cont.) ## After Cutting and Welding (cont.) File permit with Safety manager. Permit Issued by Date Supervisor to Complete Part 2 of 2 Issue Date Permit # # Welding and Torch Cutting Permit ## Supervisor Responsibility - Verify precautions listed on part 1 of permit. - Complete parts 1 and 2. - Issue Part 1 to employee doing hot work and post on site and retain part 2. - After watch is complete, verify area is safe and retain Part 1 and attach together. <table><tr><th colspan="3">Job Description:</th></tr><tr><td>Safety Procedures reviewed with Welder</td><td>Y</td><td>N</td></tr><tr><td>Safety Procedures reviewed with Fire Watch</td><td>Y</td><td>N</td></tr></table> Comments: Supervisor Sign Off Date Work Completed Date_ Time -2-

[16] Fire Precautions for Welding

Page 1

Open source document

Source excerpt

Fire Precautions for Welding # Safety and health professionals must be familiar with the various types of fire extinguishing equipment and be able to specify the proper selection. by Kris Bancroft As is the case with all hot work tasks, fire prevention is among the foremost safety and health issues for welders. It is the first of the potential hazards listed in the OSHA General Industry standards, cited in 29 CFR 1910.252 paragraph (a), and is subdivided into four parts. ## Basic Precautions Welding and cutting operations produce smoke, spark and slag. Often, the showers of sparks will be punctuated with miniature explosions, causing droplets of molten metal and slag to be hurled considerable distances from their point of origin. This phenomenon is not entirely preventable and is generally caused by one of four factors: 1) There is insufficient oxygen being delivered to the cutting or welding torch and the acetylene is pre-igniting inside the burner tip. 2) The material being welded or cut is contaminated with rust or scale that is being burned off. 3) Two dissimilar metals are being cut simultaneously, and the difference in oxidation rates is causing a reaction. 4) The arc amperage of the welder or cutter is not sufficient for the length of the arc. The basic precautions cited in subparagraph (a)(1) are derived from the Standard for Fire Prevention in Use of Cutting and Welding Processes (NFPA Standard 51B, most recently updated in 1999). The basic precautions are managed by one of four methods, two of which are discussed in the first of three discrete options: 1) Move the object to be welded away from objects that could explode, combust, or ignite when exposed to the heat of the welding process. 2) Move all objects that are prone to explode, combust, or ignite away from the object being welded. 3) Place devices that are designed to shield potentially explosive, combustible, or ignitable materials from open flames, sparks, or hot slag if they cannot be m…

Related Q&A

Keep exploring.

Human questionUS

Write a risk assessment for FAHU replacement

A suitable safe system of work for replacing a Fresh Air Handling Unit (FAHU) should begin with a task-specific risk assessment, coordination with the client/site operator, and a permit-to-work package covering isolation, lifting, work at height, electrical work, hot work if applicable, and any confined-space elements.

Read the thread
Human questionUS

Safe Work Practices for Demolition

Demolition Safety: Safe Work Practices and Regulatory Compliance ================================================================ *Date:** 2025-11-09 *Duration:** \[DURATION] minutes *Presenter:** \[PRESENTER NAME] *Location:** \[LOCATION] Objective To understand and implement safe work practices and comply with

Read the thread
Human questionUS

hot work permit

Safe Work Procedure: Hot Work Permit Document Number: [SWP-NUMBER] Revision Date: [DATE] Next Review Date: [NEXT REVIEW DATE] Department: [DEPARTMENT NAME] 1. Scope This Safe Work Procedure (SWP) outlines the necessary steps and precautions to be taken before, during, and after conducting hot work operations. Hot work

Read the thread
Human questionUS

hot tapping

Safe Work Procedure: Hot Tapping Document Number: [SWP-NUMBER] Revision Date: [DATE] Next Review Date: [NEXT REVIEW DATE] Department: [DEPARTMENT NAME] 1. Scope This Safe Work Procedure (SWP) outlines the necessary safety precautions and procedures for performing hot tapping operations on pressurized pipelines

Read the thread
Discussion thread

Add your experience.

Community answers can add practical context. They are moderated, but they are not reviewed by Francis Langlois or presented as SALUS safety guidance.

New contributions are closed. Previously approved contributions remain visible.

Community answers(0)

No community answers have been approved yet.

Comments on Rosie's answer(0)

No comments have been approved yet.

Ready to put operational safety to work?

Join 400K users across 150K sites already on SALUS.

No commitment · 30-minute personalized walkthrough